Measuring procedure
A typical measuring procedure for determining the mass of a body consists of three main steps: filtering, scaling and evaluation.

1. Filtering
The signal from the EtherCAT Terminals of the ELM35xx and EL3356 series typically has a level of noise that requires filtering to ensure valid measurement results. The function block FB_WG_ComboFilter offers an effective solution for this by switching a combination of PTn, Moving Average and Notch filters in series. If these filter options are not sufficient, a selection of further filters from the TwinCAT 3 filter library is available.
2. Scaling
The filtered input signal must then be scaled in order to specify the weight in the desired unit (e.g. grams [g]). Scaling is performed by the function block FB_WG_Scaling. Accurate measurement also requires calibration of the PLC function block, which can be carried out using a two-point calibration, for example.
3. Evaluation
In the final step, the scaled signal is analyzed using the function block FB_WG_Weighing. It is necessary to provide the configuration structure ST_WG_Weighing with the appropriate parameters. A key parameter in this structure is ST_WG_Weighing.nWindowLength
, which defines the number of samples used to calculate the moving average - a variable also known as the window size. This parameter determines how many past values are used to calculate the outputs fWeight, fStd, fMin
and fMax
of the function block FB_WG_Weighing. Here, fWeight
represents the average, fStd
the standard deviation and fMin/fMax
the minimum or maximum value of the last nWindowLength
input values. A supplementary figure can illustrate these relationships.

To obtain additional results from the function block, such as bValidMeasurement, bNewResult, tLastResult, fLastWeight
and fLastStd
, it is necessary to configure the substructure ST_WG_Weighing_Validation accordingly.
Within ST_WG_Weighing_Validation, the parameters fThresholdWeight, fMaxWeightDeviation
and fMaxStd
define the criteria for a valid measurement. For a measurement to be considered valid, the following conditions must be met:
FB_WG_Weighing.fWeight
must be greater than or equal tofThresholdWeight
.- The difference
FB_WG_Weighing.fMax - FB_WG_Weighing.fMin
must not exceedfMaxWeightDeviation
. FB_WG_Weighing.fStd
must be less than or equal tofMaxStd
.
These conditions must be met over the number of consecutive samples defined in nValidationSamples
in order to set FB_WG_Weighing.bValidMeasurement
to TRUE
.
The measurement is initiated as soon as FB_WG_Weighing.fWeight
exceeds the value of ST_WG_Weighing_Validation.fThresholdWeight
for the first time. As long as FB_WG_Weighing.bValidMeasurement
has the value TRUE
, the weight (fWeight
) with the smallest standard deviation (fStd
) is searched for and continuously updated in FB_WG_Weighing.fLastWeight
and in FB_WG_Weighing.fLastStd
. If the parameter ST_WG_Weighing_Validation.fRelativeWeightLimit
is defined, the measurement ends as soon as FB_WG_Weighing.fWeight
falls below the value of fThresholdWeight * fRelativeWeightLimit
. If this parameter is not set, the measurement ends when fWeight
falls below fThresholdWeight
.
At the end of the measurement, the timestamp is saved in FB_WG_Weighing.tLastResult
and FB_WG_Weighing.bNewResult
is set to TRUE
for exactly one cycle. If FB_WG_Weighing.fWeight
exceeds the value fThresholdWeight
again, FB_WG_Weighing.fLastWeight
is reset and a new measurement begins.
The following figure illustrates the process described above and shows the relationship between the parameters and the conditions for a valid measurement:

ST_WG_Weighing_AutoTare can be configured in the same way as ST_WG_Weighing_Validation to receive results such as fAutoTareOffset
and bNewAutoTareResult
from the function block. These are essential for automatically taring the function block FB_WG_Scaling, for example by calling AutoTare(fbScaling,E_WG_AutoTareType.eEnd
).
The parameters fThresholdWeight, fMaxWeightDeviation
and fMaxStd
in ST_WG_Weighing_AutoTare define the criteria for the validation of a measurement. A measurement is considered valid if:
FB_WG_Weighing.fWeight
does not exceed the valuefThresholdWeight
.- The difference
FB_WG_Weighing.fMax - FB_WG_Weighing.fMin
does not exceed the specifiedfMaxWeightDeviation
. FB_WG_Weighing.fStd
is less than or equal to the definedfMaxStd
.
The update of fAutoTareOffset
begins as soon as fWeight
falls below fThresholdWeight
for the first time and the stated conditions are met over a series of consecutive samples defined in nValidationSamples
. The system searches for the weight with the lowest standard deviation and updates continuously fAutoTareOffset.
The measurement ends as soon as FB_WG_Weighing.fWeight
exceeds fThresholdWeight
. FB_WG_Weighing.bNewAutoTareResult
is then set once to TRUE
, which signals the end of the measurement. If FB_WG_Weighing.fWeight
falls below the threshold value fThresholdWeight,
, FB_WG_Weighing.fAutoTareOffset
is reset and a new measurement is initiated.
The figure below illustrates the process and clarifies the relationship between the parameters and the criteria for a valid measurement.