FB_MBUS_IST_PulsonicII
FB_MBUS_IST_PulsonicII 1:
This function block is used to read energy meters with pulse output from Ista:
-Pulsonic II
The function block can only be executed together with the function block FB_MBUSKL6781().
FB_MBUS_IST_PulsonicII 2:
The devices are supplied from a battery. The number of read operations is therefore limited. An internal meter prevents communication exceeding 96 times per day on average. The user must make sure that excessive queries are prevented.
Functionality of the function block
usiAddress      : USINT;
stSecAdr        : ST_MBUS_SecAdr;
eBaudrate       : E_MBUS_Baudrate := eMBUS_Baud2400;
bStart          : BOOL;
bSND_NKE        : BOOL := TRUE;
bReadInit       : BOOL := TRUE;
tMinSendTime    : TIME := t#2s;
usiUnit         : USINT;
bDisabled       : BOOL := FALSE;
usiAddress: Primary address of the counter, that shall be readout with this module.
stSecAdr: Secondary address of the counter, that shall be readout with this module.
eBaudrate: 300, 2400 baud.
bStart: Positive edge on this input, the meter is read out once.
bSND_NKE: TRUE to initialize the meter at each reading, and sets the meter on the first telegram (SND_NKE).
bReadInit: After restarting the PLC, the meter is read out once.
tMinSendTime: Standard t#2s. When this time exceeds, the counter is rereadout. At t#0s the counter is not readout and can be readout with bStart manually.
usiUnit: Unit of the energy values. 0=W/J(h) / 1=KW/KJ(h) / 2=MW/MJ(h) / 3=GW/GJ(h).
bDisabled: TRUE = disable the function block.
bBusy           : BOOL;
bReady          : BOOL;
bError          : BOOL;
eError          : E_MBUS_ERROR;
dwIdNumber      : DWORD;
byStatus        : BYTE;
byGEN           : BYTE;
byCounter       : BYTE;
usiRecivedAdr   : USINT;
eMedium         : E_MBUS_Medium;
sMan            : STRING(3);
stValue         : ST_MBus_Info;
stCurrentValue  : ST_MBus_Info;
stDeviceError   : ST_MBus_Info;
bBusy: The bBusy output is TRUE while the meter is being read.
bReady: The bReady output is TRUE for one cycle, once meter reading is completed.
bError: The bError output becomes TRUE as soon as an error occurs. The error is described via the variable eError.
eError: The eError output issues an error code when an error occurs (see E_MBUS_ERROR).
dwIdNumber: Serial number of the meter (secondary address).
byStatus: Status of the meter. Please refer to device description for meanings.
byGEN: Meter software version.
byCounter: Transmission counter (number of transmitted RSP_UD).
usiRecivedAdr: Received primary address (0-250).
eMedium: Medium (see E_MBUS_Medium).
sMan: Manufacturer code.
stValue: Meter reading (see ST_MBus_Info).
stCurrentValue: Current flow / power (see ST_MBus_Info).
stDeviceError: Error message from the device (see ST_MBus_Info).
stCom          : ST_MBUS_Communication;
stCom: About this structure, the block FB_MBUSKL6781() is connected to the meter function blocks (see ST_MBUS_Communication).
Download sample program for PC/CX systems: FB_MBUS_IST_PulsonicII 3:
Download sample program for BX systems: FB_MBUS_IST_PulsonicII 4:
Controller configuration setting: "BCxx50 or BX serial"
Download sample program for BC systems: FB_MBUS_IST_PulsonicII 5:
BCxx00 must be set to "Large Model" in the PLC under "Project/Options/Controller Settings".
Controller configuration setting: "BC serial"