FB_MBUS_AMT_CALEC

FB_MBUS_AMT_CALEC 1:

This block is used for reading heat meters from Aquametro:

-CALEC

The block can only be used in conjunction with the block FB_MBUSKL6781().

Functionality of the function block

VAR_INPUT

usiAddress     : USINT;
stSecAdr       : ST_MBUS_SecAdr;
eBaudrate      : E_MBUS_Baudrate := eMBUS_Baud2400;
bStart         : BOOL;
bSND_NKE       : BOOL := TRUE;
bReadInit      : BOOL := TRUE;
tMinSendTime   : TIME := t#2s;
usiUnit        : USINT;
bDisabled      : BOOL := FALSE;

usiAddress: Primary address of the counter, that shall be readout with this module.

stSecAdr: Secondary address of the counter, that shall be readout with this module.

eBaudrate: 300, 2400 baud.

bStart: Positive edge on this input, the meter is read out once.

bSND_NKE: TRUE to initialize the meter at each reading, and sets the meter on the first telegram (SND_NKE).

bReadInit: After restarting the PLC, the meter is read out once.

tMinSendTime: Standard t#2s. When this time exceeds, the counter is rereadout. At t#0s the counter is not readout and can be readout with bStart manually.

usiUnit: Unit of the energy values. 0=W/J(h) / 1=KW/KJ(h) / 2=MW/MJ(h) / 3=GW/GJ(h).

bDisabled: TRUE = disable the function block.

VAR_OUTPUT

bBusy          : BOOL;
bReady         : BOOL;
bError         : BOOL;
eError         : E_MBUS_ERROR;
dwIdNumber     : DWORD;
byStatus       : BYTE;
byGEN          : BYTE;
byCounter      : BYTE;
usiRecivedAdr  : USINT;
eMedium        : E_MBUS_Medium;
sMan           : STRING(3);
stEnergy       : ST_MBus_Info;
stPower        : ST_MBus_Info;
stVolume       : ST_MBus_Info;
stFlow         : ST_MBus_Info;
stForwardTemp  : ST_MBus_Info;
stReturnTemp   : ST_MBus_Info;
stDiffTemp     : ST_MBus_Info;

bBusy: The bBusy output is TRUE while the meter is being read.

bReady: The bReady output is TRUE for one cycle, once meter reading is completed.

bError: The bError output becomes TRUE as soon as an error occurs. The error is described via the variable eError.

eError: The eError output issues an error code when an error occurs (see E_MBUS_ERROR).

dwIdNumber: Serial number of the meter (secondary address).

byStatus: Status of the meter. Please refer to device description for meanings.

byGEN: Meter software version.

byCounter: Transmission counter (number of transmitted RSP_UD).

usiRecivedAdr: Received primary address (0-250).

eMedium: Medium (see E_MBUS_Medium).

sMan: Manufacturer code.

stEnergy: Meter reading, energy consumption (see ST_MBus_Info).

stPower: Current energy consumption (see ST_MBus_Info).

stVolume: Meter reading, volume (see ST_MBus_Info).

stFlow: Current flow (see ST_MBus_Info).

stForwardTemp: Flow temperature (see ST_MBus_Info).

stReturnTemp: Return temperature (see ST_MBus_Info).

stDiffTemp: Temperature difference (see ST_MBus_Info).

VAR_IN_OUT

stCom          : ST_MBUS_Communication;

stCom: About this structure, the block FB_MBUSKL6781() is connected to the meter function blocks (see ST_MBUS_Communication).

Download sample program for PC/CX systems: FB_MBUS_AMT_CALEC 2:

Download sample program for BX systems: FB_MBUS_AMT_CALEC 3:

Controller configuration setting: "BCxx50 or BX serial"

Download sample program for BC systems: FB_MBUS_AMT_CALEC 4:

BCxx00 must be set to "Large Model" in the PLC under "Project/Options/Controller Settings".

Controller configuration setting: "BC serial"

VAR_IN_OUT

stCom          : ST_MBUS_Communication;

stCom: About this structure, the block FB_MBUSKL6781() is connected to the meter function blocks (see ST_MBUS_Communication).

Download sample program for PC/CX systems: FB_MBUS_AMT_CALEC 5:

Download sample program for BX systems: FB_MBUS_AMT_CALEC 6:

Controller configuration setting: "BCxx50 or BX serial"

Download sample program for BC systems: FB_MBUS_AMT_CALEC 7:

BCxx00 must be set to "Large Model" in the PLC under "Project/Options/Controller Settings".