MC_StepReferencePulse
MC_StepReferencePulse 1:
This function block performs the search for a zero pulse of an encoder.
A zero pulse is not present in all encoders and occurs only once per encoder revolution. The advantage of using a zero pulse for referencing is the high accuracy of this signal compared to that of a standard sensor.
MC_StepReferencePulse 2: Inputs
    Execute         : BOOL;
    Direction       : MC_Home_Direction;
    SwitchMode      : MC_Switch_Mode;
    ReferenceSignal : MC_Ref_Signal_Ref;
    Velocity        : LREAL;
    Acceleration    : LREAL;
    Deceleration    : LREAL;
    Jerk            : LREAL;
    SetPosition     : LREAL;
    TimeLimit       : TIME;
    DistanceLimit   : LREAL;
    TorqueLimit     : LREAL;
    BufferMode      : MC_BufferMode;
    Options         : ST_Home_Options4;
Type
Execute
The command is executed with a rising edge at the Execute input.
Direction
MC_Home_Direction
Enumeration that defines the initial direction of movement for the search procedure.
SwitchMode
MC_Switch_Mode
Enumeration that defines the final condition for the search procedure.
ReferenceSignal
MC_Ref_Signal_Ref
This structure defines the source of the reference cam signal.
Velocity
LREAL
Maximum travel velocity (>0).
Acceleration
LREAL
Acceleration (≥0). If the value is 0, the standard acceleration from the axis configuration applies.
Deceleration
LREAL
Deceleration (≥0). If the value is 0, the standard deceleration from the axis configuration applies.
Jerk
LREAL
Jerk (≥0). If the value is 0, the standard jerk from the axis configuration applies.
SetPosition
LREAL
Position value to which the axis position is set to.
TimeLimit
TIME
Exceeding this time leads to the search procedure being aborted.
DistanceLimit
LREAL
Exceeding this distance in relation to the start position leads to the search procedure being aborted.
TorqueLimit
LREAL
The motor torque is limited to this value in order to avoid mechanical damage.
BufferMode
MC_BufferMode
Not implemented
Options
ST_Home_Options4
DisableDriveAccess: Set to FALSE for Beckhoff drives. Usually to TRUE for third-party drives (see info).
EnableLagErrorDetection: In the step functions, the lag error detection is switched off in order to ensure a smooth referencing process. If it would be purposeful to keep the lag error detection active in an application, this can be achieved by setting this flag.
MC_StepReferencePulse 3:
If DisableDriveAccess = TRUE, the user is responsible for modifying and reconstructing required drive parameters. The parameters required for the intended homing sequence must be agreed with the manufacturer of the third-party drive.
MC_StepReferencePulse 4:/MC_StepReferencePulse 5: Inputs/outputs
    Axis      : AXIS_REF;
    Parameter : MC_HomingParameter;
Type
Axis
AXIS_REF
Axis data structure of the type AXIS_REF, which uniquely addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
Parameters
MC_HomingParameter
Data structure of the type MC_HomingParameter, which must be transferred from function block to function block over the entire homing sequence.
MC_StepReferencePulse 6: Outputs
    Done           : BOOL;
    Busy           : BOOL;
    Active         : BOOL;
    CommandAborted : BOOL;
    Error          : BOOL;
    ErrorID        : UDINT;
Type
Done
Becomes TRUE if the command was completed successfully.
Busy
The Busy output becomes TRUE when the command is started with Execute and remains TRUE for as long as the command is processed. When Busy becomes FALSE again, the function block is ready for a new order. At the same time one of the outputs, Done, CommandAborted, or Error, is set.
Active
Indicates that the command is executed.
CommandAborted
Becomes TRUE, if the command could not be fully executed.
Error
Becomes TRUE as soon as an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.
