MP_SR_actuator_Configuration
This function block is used to configure SR actuators. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
![]() | Restrictions Call only if the corresponding “Process” function block is not executed. |
MP_Address : USINT := 1;
bStart : BOOL;
bRead_Write : BOOL;
strDataKL6771 : DataKL6771;
rMinPositionRel_Write : LREAL := 0.0;
rMidPositionRel_Write : LREAL := 50.0;
rMaxPositionRel_Write : LREAL := 100.0;
bMotionDirection_Write : BOOL;
stLocationString_Write : STRING:='ABCDEFGHIJKLMNOP';
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. |
bRead_Write | BOOL | If FALSE then READ only; if TRUE then READ and WRITE. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
rMinPositionRel_Write | LREAL | Minimum operating range limit in % (0…100). Min must be <= Max − 20%. |
rMidPositionRel_Write | LREAL | Adjustable value between Min and Max in % (0…100). |
rMaxPositionRel_Write | LREAL | Maximum operating range limit in % (0…100). Max must be greater than or equal to Min plus 20%. |
bMotionDirection_Write | BOOL | FALSE = normal; TRUE = reversed |
stLocationString_Write | STRING | Location information, maximum 16 characters. |
Outputs
iErrorId : MP_Error;
rMinPositionRel : BOOL;
rMidPositionRel : BOOL;
rMaxPositionRel : BOOL;
bMotionDirection : BOOL;
stLocationString : STRING;
stDeviceString : STRING;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
rMinPositionRel | LREAL | Minimum operating range limit in % (0…100). Min must be <= Max − 20%. |
rMidPositionRel | LREAL | Adjustable value between Min and Max in % (0…100). |
rMaxPositionRel | LREAL | Maximum operating range limit in % (0…100). Max must be greater than or equal to Min plus 20%. |
bMotionDirection | BOOL | FALSE = normal; TRUE = reversed |
stLocationString | STRING | Location information. Maximum 16 characters. |
stDeviceString | STRING | Belimo part number corresponding to the product model number. |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.77 | Tc2_MPBus from 3.8.1.0 |