MC_GearInMultiMaster
The function block MC_GearInMultiMaster is used to activate linear master/slave coupling (gear coupling) for up to four different master axes. The gear ratio can be adjusted dynamically during each PLC cycle. The slave movement is determined by the superimposed master movements. The "Acceleration" parameter has a limiting effect in situations with large gear ratio variations.
The slave axis can be decoupled with the function block MC_GearOut. If the slave is decoupled while it is moving, then it retains its velocity and can be halted using MC_Stop.
If less than four masters are used, an empty data structure can be transferred for each of the parameters "Master2" to "Master4" (the axis ID must be 0).
Master1 : Reference To AXIS_REF;
Master2 : Reference To AXIS_REF;
Master3 : Reference To AXIS_REF;
Master4 : Reference To AXIS_REF;
Enable : BOOL;
GearRatio1 : LREAL;
GearRatio2 : LREAL;
GearRatio3 : LREAL;
GearRatio4 : LREAL;
Acceleration : LREAL;
Deceleration : LREAL;
Jerk : LREAL;
BufferMode : MC_BufferMode;
Options : ST_GearInMultiMasterOptions;
Master1 | Reference To AXIS_REF | Axis data structure of the first master |
Master2 | Reference To AXIS_REF | Axis data structure of the second master |
Master3 | Reference To AXIS_REF | Axis data structure of the third master |
Master4 | Reference To AXIS_REF | Axis data structure of the fourth master |
Enable | BOOL | If "Enable" is TRUE, the function block establishes a coupling. If an MC_GearOut is executed while the MC_GearInMultiMaster continues to be called with "Enable" TRUE, it is only decoupled briefly and then immediately attempts to re-establish the coupling. As long as "Enable" is TRUE, the gear factors can be changed cyclically. If "Enable" becomes FALSE after coupling, the command is terminated. The gear factors are frozen at their last values, but the slave is not decoupled. |
GearRatio1 | LREAL | Gear ratio as floating point value for the first master axis. The gear ratio can be changed cyclically as long as "Enable" is TRUE. If "Enable" is FALSE, the gear ratio remains unchanged. |
GearRatio2 | LREAL | Gear ratio as floating point value for the second master axis. The gear ratio can be changed cyclically as long as "Enable" is TRUE. If "Enable" is FALSE, the gear ratio remains unchanged. |
GearRatio3 | LREAL | Gear ratio as floating point value for the third master axis. The gear ratio can be changed cyclically as long as "Enable" is TRUE. If "Enable" is FALSE, the gear ratio remains unchanged. |
GearRatio4 | LREAL | Gear ratio as floating point value for the fourth master axis. The gear ratio can be changed cyclically as long as "Enable" is TRUE. If "Enable" is FALSE, the gear ratio remains unchanged. |
Acceleration | LREAL | Acceleration (≥0). If the value is 0, the standard acceleration from the axis configuration in the System Manager is used. The parameter limits the acceleration of the slave in situations with large gear ratio variations. |
Deceleration | LREAL | Deceleration (≥0). If the value is 0, the standard deceleration from the axis configuration in the System Manager is used. The parameter limits the deceleration of the slave in situations with large gear ratio variations. Used only for the option "AdvancedSlaveDynamics". |
Jerk | LREAL | Jerk (≥0). If the value is 0, the standard jerk from the axis configuration in the System Manager is used. The parameter limits the jerk of the slave in situations with large gear ratio variations. Used only for the option "AdvancedSlaveDynamics". |
BufferMode | MC_BufferMode | Currently not implemented |
Options |
Overview: Which user command results in a permanent position difference or catches it up depending on the SyncMode?
![]() | If coupling takes place with a constant gear ratio with the axes at a standstill (and the gear ratio no longer changes during the course of coupling), then the two SyncModes POSSYNC1 and POSSYNC2 behave identically. |
Inputs/outputs
Slave : AXIS_REF;
Slave | AXIS_REF | Axis data structure of the slave |
The axis data structure of type AXIS_REF addresses an axis unambiguously within the system. Among other parameters it contains the current axis status, including position, velocity or error state.
Outputs
InGear : BOOL;
Busy : BOOL;
Active : BOOL;
CommandAborted : BOOL;
Error : BOOL;
ErrorID : UDINT;
InGear | BOOL | TRUE if the coupling was successful. |
Busy | BOOL | TRUE as soon as the command is started with "Enable" and as long as the command is processed. If "Busy" is FALSE, the function block is ready for a new order. At the same time, one of the outputs "InGear", "CommandAborted" or "Error" is set. |
Active | BOOL | Indicates that the command is executed. (Currently Active = Busy) |
CommandAborted | BOOL | TRUE if the command could not be executed completely. The axis may have become decoupled during the coupling process (simultaneous command execution). |
Error | BOOL | TRUE, if an error occurs. |
ErrorID | UDINT | If the error output is set, this parameter supplies the error number. |
Development environment | Target system type | PLC libraries to include |
TwinCAT v3.0.0 | PC or CX (x86 or x64) | Tc2_MC2 |