MC_ExtSetPointGenFeed
MC_ExtSetPointGenFeed 1:
The MC_ExtSetPointGenFeed function is used to feed set values from an external setpoint generator into an axis. The function copies the data instantaneously into the cyclic axis interface (fExtSetPos, fExtSetVelo, fExtSetAcc and nExtSetDirection). The function result of MC_ExtSetPointGenFeed is not used and therefore always FALSE.
An external setpoint generator is usually a PLC function block that calculates cyclic set values for an axis and can therefore substitute the internal setpoint generator in an NC axis.
See also: MC_ExtSetPointGenEnable and MC_ExtSetPointGenDisable
MC_ExtSetPointGenFeed 2: Inputs
    Position     : LREAL;
    Velocity     : LREAL;
    Acceleration : LREAL;
    Direction    : DINT;
Type
Position
LREAL
Set position from an external setpoint generator
Velocity
LREAL
Set velocity from an external setpoint generator
Acceleration
LREAL
Set acceleration from an external setpoint generator
Direction
DINT
Set direction from an external setpoint generator. ( -1 = negative direction, 0 = standstill, 1 = positive direction)
MC_ExtSetPointGenFeed 3: Inputs/outputs
    Axis : AXIS_REF;
Type
Axis
AXIS_REF
Axis data structure that unambiguously addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
Development environment
Target system type
PLC libraries to include
TwinCAT v3.0.0
PC or CX (x86 or x64)
Tc2_MC2