FB_Dpv1ReadPNET
FB_Dpv1ReadPNET 1:
The function block FB_Dpv1ReadPNET reads one or more parameters of a Sinamics Profidrive via DPV1 (Profidrive specification 3.1) via Profinet. The DPV1 read telegram must be created with F_CreateDpv1ReadReqPkgPNET before a rising edge is present at bExecute. The DPV1 answer telegram must be evaluated with F_SplitDpv1ReadResPkgPNET, after which bBusy displays a falling edge.
The execution of this function block requires some time, depending on the number of parameters to be read. The function block sends the DPV1 telegram and polls for an answer telegram.
FB_Dpv1ReadPNET 2: Inputs
    bExecute        : BOOL;(* drive access info *)
    aNetId          : T_AmsNetId; (* NetID of Profibus Master EL6631 *)
    iProfinetPort   : UINT; (* Port of ProfiDrive *)
    iDriveId        : USINT; (* 0..255 possible *)
    pDpv1ReqData    : POINTER TO ARRAY [1..iMAX_DPV1_SIZE_PNET_REQ] OF BYTE;
    iDpv1ReqDataLen : UDINT;
    pDpv1ResData    : POINTER TO ARRAY [1..iMAX_DPV1_SIZE_PNET_RES] OF BYTE;
    iDpv1ResDataLen : UDINT;
    tTmOut          : TIME;
Type
bExecute
The function block is enabled by a positive edge at this input.
aNetId
T_AmsNetID
The network address of the Profibus master device (see ADS tab of the Profibus master device in the I/O configuration in the TwinCAT system)
iProfinetPort
UINT
The Profinet port number of the drive. This is an address for several axes, specified in the TwinCAT system in the I/O configuration.
iDriveID
USINT
The ID is 1 for the ControllerUnit, 2 for the drive object A, 3 for the drive object B of a double/triple drive. The drive ID is set in the starter software. 1..16 is possible.
pDpv1ReqData
POINTER TO ARRAY
Pointer to an array of 240 bytes containing the DPV1 read telegram. This telegram must be created by the F_CreateDpv1ReadReqPkg function before the DPV1 read is activated via bExecute.
iDv1ReqDataLen
UDINT
Maximum length of the DPV1 data buffer (240 bytes).
pDpv1ResData
POINTER TO ARRAY
Pointer to an array of 240 bytes containing the DPV1 read answer telegram. This telegram must be evaluated by the F_SplitDpv1ReadResPkg function after a falling edge appears at bBusy.
iDpv1ResDataLen
UDINT
Maximum length of the DPV1 response data buffer (240 bytes).
tTmOut
TIME
Maximum time allowed for the execution of the command.
FB_Dpv1ReadPNET 3: Inputs/outputs
    iRequestRef : USINT; (* 1..127; 0: reserved *)
Type
iRefRequest
USINT
Reference that is automatically incremented with each telegram. The reference is required for the allocation of the responses to the write/read requests.
FB_Dpv1ReadPNET 4: Outputs
    bBusy        : BOOL;
    bError       : BOOL;
    bErrorValues : BOOL;
    iErrId       : UDINT;
    iErrorClass  : BYTE;
    iErrorCode   : BYTE;
Type
bBusy
This output goes TRUE as soon as the function block is activated via bExecute and remains TRUE as long as the function block has not received a response.
In case of errors this output goes TRUE and bBusy goes FALSE.
bErrorValues
TRUE if the DPV1 Read was unsuccessful or only partly successful. The error causes are returned via the error ID (as well as Class and Code).
iErrId
UDINT
Returns the ADS error number or function-block-specific error numbers if bError = TRUE.
iErrClass
BYTE
Profidrive error class
iErrCode
BYTE
Profidrive error code
Function-block-specific error codes
0x2
Incorrect response reference
0x3
DPV1 Read faulty or partially faulty
0x4
Incorrect response ID
other error IDs
See ADS error codes
Error classes
Error code
0x0 - 0x9
Reserved
0xA
Application errors
0x0: read error
0x1: write error 0x2: module error
0x3 - 0x7: reserved
0x8: version conflict
0x9: not supported
0xA - 0xF: user-dependent
0xB
Access errors
0x0: invalid index (no data block DB47, parameter access is not supported)
0x1: write length error
0x2: invalid slot
0x3: type conflict
0x4: invalid range
0x5: state conflict (access to DB47 temporarily not possible due to internal process states)
0x6: access denied
0x7: invalid range (write error in DB47 header) 0x8: invalid parameter
0x9: invalid type
0xC
Resource errors
0x0: read conflict
0x1: write conflict
0x2: resource busy
0x3: resource not accessible 0x4 - 0x7: reserved
0x8 - 0xF: user-dependent
0xD - 0xF
User-defined errors
Development environment
Target platform
IO hardware
PLC libraries to be integrated (category group)
TwinCAT v3.1.0
PC or CX (x86)
Beckhoff EL6632
Tc2_IoFunctions (IO)