Position controller deadband (P-AXIS-00395)
In order to prevent the position controller to continuosly output in standstill a setpoint value, with this parameter a minimal position lag can be defined, and if this limit is fallen below the output of a setpoint value is suppressed.
Variable name
Type
Permissible range
Axis type
Dimension
pos_control_deadband
UNS32
[0 ..P-AXIS-00236]
T, R
0.1 um
The deadband may not be bigger than the position window (P-AXIS-00236) set up for the axis (see also P-ERR-110528). With a value of zero (default) a setpoint value is output continuosly.
The value of P-AXIS-00395 scaled in encoder increments (see P-AXIS-00233, P-AXIS-00234) must be ≥ 1 (see also P-ERR-110529).
Position controller deadband (P-AXIS-00395) 1:
This parameter is only effective with CNC position control.