BAC_AI_Enthalpy_01
Functional description
The template logs the two analog input values temperature and relative humidity of a Bus Terminal (see IO linking) and converts them to real process values.
The function block HX is used to calculate the dew point temperature, the specific enthalpy, the wet bulb temperature and the absolute humidity.
Interface
Block diagram
rH : REAL;
rT : REAL;
rX : REAL;
rE : REAL;
H_bHiLmt : BOOL;
H_bLoLmt : BOOL;
T_bHiLmt : BOOL;
T_bLoLmt : BOOL;
rH: current value of the analog input object H - relative humidity [%]
rT: current value of the analog input object T - temperature [°C]
rX: current value of the analog value object X - absolute humidity g water in kg of dry air [g/kg]
rE: calculated value enthalpy [kJ/kg]
H_bHiLmt: relative humidity High Limit
H_bLoLmt: relative humidity Low Limit
T_bHiLmt: temperature High Limit
T_bLoLmt: temperature Low Limit
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | optional | Task |
T |
| Analog input object for temperature display | |
AlmT |
| Logging and further processing of the status flag Fault of the temperature | |
T_TLog |
| Trend logging of the measured value of the AI object T | |
H |
| Analog input object for relative humidity display | |
AlmH |
| Logging and further processing of the status flag Fault of the relative humidity | |
H_TLog |
| Trend logging of the measured value of the AI object H | |
HX |
| This function block is used to calculate the dew point temperature, the specific enthalpy and the absolute humidity. The temperature, the relative humidity and the barometric air pressure are required for the calculation of these parameters. | |
X |
| Analog value object for absolute humidity display | |
X_TLog |
| Trend logging of the measured value of the AV object X |
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
AI_Temperature | INT |
| Input | Analog input - temperature |
AI_Relative_Humidity | INT |
| Input | Analog input - relative humidity |
Version history
Version number | Comments |
1.0.1 | First release |