BAC_DHW_Ctrl_01
Application
The template controls the charging of a hot water tank.
The template is enabled via the input variable bEn. In the template the temperature at the top of the tank rTTop is compared with the value of the difference Sp - Hys. If the temperature at the top of the tank falls below the value, charging of the hot water tank is enabled.
If the temperature at the bottom of the tank rTBot exceeds the set value Sp, charging of the hot water tank is disabled.
Interface
System diagram
Block diagram
bEn : BOOL;
rTTop : REAL;
rTBot : REAL;
bEn: Template enable input. If this input is FALSE, the value 0 is output at rSp, and bQ becomes FALSE.
rTTop: Input for temperature at the top of the tank
rTBot: Input for temperature at the bottom of the tank
bQ : BOOL;
rSp : REAL;
bQ: Hot water tank charging output.
rSp: Hot water temperature set value output.
If enable En of the template is FALSE, the value 0 is output at rSp.
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
En | BV object for displaying the hot water tank charging template enable. | |
Sp | AV object for entering the set value for the hot water temperature. If the temperature at the bottom of the tank rTBot exceeds this value, charging of the hot water tank is disabled. The hot water tank has reached the required temperature. | |
Hys | AV object for entering the set value hysteresis. If the temperature at the top of the tank rTTop falls below the value of the difference Sp - Hys, charging of the hot water tank is enabled. This is indicated with BACnet object Q. | |
MultiCalc | The function block determines the maximum and minimum of the inputs r01-r04 and outputs the values at rMax and rMin. | |
DHW2P | The function block is the main control feature for charging the hot water tank. | |
Q | BV object for indicating whether charging of the hot water tank is enabled. |
Version history
Version number | Comments |
1.0.0.1 | First release |