BAC_AC_Filter_01
Functional description
The template realises filter monitoring within an air conditioning plant via a differential pressure switch. If the differential pressure switch is triggered, filter contamination is logged.
A rising edge at the binary input of the differential pressure switch switches the RS flip-flop to latching. As a result, the filter contamination continues to be displayed, even if the plant shuts down. The RS flip-flop is reset after a plant restart without actuation of the differential pressure switch.
A BV object is used to display the filter contamination in the OWS.
Interface
System diagram
Block diagram
udiPltStp : UDINT;
udiPltStp : The input variable is used to supply the template with the plant steps of the air-conditioning plant.BAC_StartPltStpT_01.
bDst : BOOL;
bDst: The output variable indicates that filter monitoring was triggered and issues an error for further processing.
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
DiffPrssSwi | BI object differential pressure monitor for filter monitoring | |
tonDiffPrss | TON | Response delay of the filter monitoring |
tonDiffPrss | RS | Error message memory for filter monitoring |
AlmDiffPrss | The collective alarm function block logs the filter monitoring fault and forwards it via an internal variable to the plant alarm collector BAC_PltIniAlm_01 . | |
DiffPrssAlm | BV object for displaying the filter monitoring |
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
BI_Differential_Pressure_Switch | BOOL |
| Input | Digital input - message - differential pressure switch |
Version history
Version number | Comments |
1.0.1 | First release |