BAC_GenWthT_01
Functional description
The template BAC_GenWthT_01 reads the measured outside temperature via the global variable g_WthT_rPrVal.
The measured outside temperature is used to calculate an averaged or attenuated outside temperature. This is made available to other templates via the global variable g_WthTDamp_rPrVal.
The BACnet object WthTLmtCrit describes the global variable g_WthTLmtCrit. It describes an outside temperature value below which the frost protection mode should be activated in the systems.
The SpFrost AV object is used to describe the global variable g_H_SpFrost. This global value can be used to assign a setpoint for frost protection operation to one or more plants.
For the application of many other templates it is necessary to position this template once!
Interface
Block diagram
Program description
Instance | Type | Task |
WthT | AV object for displaying the current outside temperature | |
WthTLmtCrit | AV object for entering and providing a global value for the critical outside temperature | |
SpFrost | AV object for input and provision of a global frost protection setpoint | |
DlyEn | TON | Delays reading of the first temperature value by 2 seconds after the start of the PLC |
Avrg | The function block Avrg measures the outside temperature every 15 minutes (900 seconds) and writes the value into a FIFO buffer (first in first out). The buffer has capacity for 96 elements. This results in a timeframe of 24 hours for averaging of the outside temperature. | |
WthTDamp | Output of the value of the averaged outside temperature |
Version history
Version number | Comments |
1.0.1 | First release |