Contact assignment
WARNING
Risk of electric shock and damage of device!
Bring the bus terminal system into a safe, powered down state before starting installation, disassembly or wiring of the bus terminals!
Contact assignment 1:Fig.1: Contact assignment
Terminal point
No.:
Connection for
Comment
L1
1
Phase L1
Connections for the voltage measurement. (See note under Make sure terminal point N is zeroed or grounded!)
L2
2
Phase L2
L3
3
Phase L3
N
4
Neutral conductor N (internally connected to terminal point IN,
capacitively connected to the grounding contact for the mounting rail)
IL1
5
Current transformer at L1
Connections for the current transformers. (See note under Operate the current transformer as intended!)
IL2
6
Current transformer at L2
IL3
7
Current transformer at L3
IN
8
Star point of the current transformers
(internally connected to terminal point N,
*) The KL3403-0026 has no capacitive connection to the grounding contact of the mounting rail!
CAUTION
Make sure terminal point N is zeroed or earthed!
If you do not connect the terminal point N with the neutral conductor of your mains supply (e.g. if the KL3403 is used purely for current measurements), terminal point N should be earthed, in order to avoid dangerous overvoltages in the event of a current transformer fault!
CAUTION
Please note that many manufacturers do not permit their current transformers to be operated in no-load mode! Connect the KL3403 to the secondary windings of the current transformers before using the current transformer!
UL compliance
Follow the instructions indicated below, in order to comply with the specifications of Underwriters Laboratories.
CAUTION
Contact assignment 2:
Intended use
The terminals are exclusively intended for application with the UL-listed I/O systems of the series BKxxxx, BCxxxx, BXxxxx, LCxxxx, CXxxxx, KLxxxx, KSxxxx or KMxxxx from Beckhoff.
CAUTION
Contact assignment 3:
cULus verification
For the cULus verification, the Beckhoff I/O system only examined for risk of fire or electric shock (in accordance with UL508 and CSA C22.2 No. 142).
CAUTION
Contact assignment 4:
Phase voltage according to UL specifications 300 V max.
The maximum phase voltage of 500 V described in the technical data should be limited to 300 V for applications requiring UL approval.
CAUTION
Contact assignment 5:
Current transformer
Current measurement inputs with the IDs IL1, IL2, IL3, N may only be connected to isolating current transformers, which limit the available current to max. 5 A, 20 V.
CAUTION
Contact assignment 6:
No extended temperature range
The limited temperature range applies, if the KL3403-0000 / KS3403-0000 are used according to UL conditions (see Technical data).