Technical data
Technical data | KL3403-... / KS3403-... | |||||||||
0000 | 0010 | 0014 | 0020 | 0022 | 0025 | 0026 | 0333 | |||
Measured values | U, I | U, I | U1) | U, I | I2) | U, I | U, I | U, I | ||
Calculated parameters | Active power, energy, power factor (cosj) | |||||||||
Measuring voltage | max. 500 VAC 3~ | - | max. 500 VAC 3~ | |||||||
Measuring voltage according to UL specifications (see UL compliance) | max. 300 VAC 3~ | - | max. 300 VAC 3~ | |||||||
Measuring current | direct (max.) | 1 A | 5 A | 60 mV1) | 20 mA | 20 mA | 250 mA | 1 A | 333 mV (AC) | |
via current transformers with transformation | R x 1 A | R x 5 A | - | R x 20 mA | R x 20 mA | R x 250 mA | R x 1 A | R x 333 mV | ||
Voltage circuit input resistance (typical) | 500 kΩ | 500 kΩ | 500 kΩ | 500 kΩ | 10 Ω2) | 500 kΩ | 500 kΩ | 500 kΩ | ||
Current circuit input resistance (typical) | 33 mΩ | 6.8 mΩ | app. 10 kΩ1) | 10 Ω | 10 Ω | 100 mΩ | 33 mΩ | 40 kΩ | ||
Resolution | 16 bit (internal 21 bit) | |||||||||
Frequency range4 | 10 Hz to 500 Hz | |||||||||
0 Hz to 500 Hz (with deactivated DC filter and with current transformers, which support this frequency range) | ||||||||||
Limit frequency | app. 2 kHz | |||||||||
Signal type | any (taking into account the frequency range and the limit frequency) | |||||||||
Measuring accuracy for sinusoidal current/voltage (total measuring range, based on the full scale value) | Voltage | 0.5% | 0.5% | 0.5% | 0.5% | - | 0.5% | |||
Current | 0.5% | 1.0% | - | 0.5% | 0.5% | 0.5% | ||||
Power (calculated) | 1.0% | 1.5% | - | 1.0% | - | 1.0% | ||||
Measuring procedure | True RMS with 64000 samples / s | |||||||||
Measuring cycle time | freely configurable (50 ms per measured value pre-set) | |||||||||
Dielectric strength | 1500 V (terminal/K-Bus) | |||||||||
Bit width in the input process image | 72 bits inputs (3 x 8 bits status, 3 x 16 bits data) | |||||||||
Bit width in the output process image | 72 bits outputs (3 x 8 bits control, 3 x 16 bits data) | |||||||||
Power supply for the electronics | via the K-bus | |||||||||
Current consumption from K-bus | typically 115 mA | |||||||||
Pluggable wiring | at all KSxxxx series terminals | |||||||||
Permissible ambient temperature range during operation | -25°C ... + 60°C | 0°C ... + 55°C | ||||||||
Permissible ambient temperature range during storage | -40°C ... + 85°C | -25°C ... + 85°C | ||||||||
Permissible relative air humidity | 95%, no condensation | |||||||||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |||||||||
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |||||||||
Weight | app. 75 g | |||||||||
Dimensions (W x H x D) | app. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |||||||||
on 35 mm mounting rail conforms to EN 60715 | ||||||||||
Installation position | variable | |||||||||
Protection class | IP20 | |||||||||
Approvals / markings* | CE, UKCA, cULus, EAC | CE, UKCA, EAC | CE, UKCA, cULus, EAC | CE, UKCA, EAC | ||||||
*) Real applicable approvals/markings see type plate on the side (product marking). 1) for KL3403-0014: three additional voltage circuits instead of the current circuits: 60 mV for connection of external shunts 2) for KL3403-22: three additional current circuits instead of the voltage circuits: also 20 mA 3) the measuring accuracy is reduced, if the extended temperature range is used (-25°C ... + 60°C) |
4) see also chapter Additional frequency-dependent measuring error |