IP4112-Bxxx, IE4112
Notice | |
Do not apply UP without US If you apply the supply voltage UP before US has been applied, the analog outputs may output unwanted current signals. |
4 analog outputs, 0 to 20 mA
The IP/IE4112 analog output module generates analog output signals in the range from 0 to 20 mA. The current is supplied to the process level with a 15-bit resolution (default) and is electrically isolated. By not transmitting the sign, a 16-bit resolution can also be selected. The scaling of the outputs can be changed if required.
The 4 output channels have a common ground potential with the 24 VDC supply. The output drivers are powered by the control voltage. The applied load voltage (which can be any value up to 30 VDC) is fed through to supply the actuators.
Technical Data | IP4112-Bxxx, IE4112 |
Number of channels | 4 |
Output connections | M12 connectors |
Output range | 0/4…20 mA |
Load impedance | < 500 Ω |
Resolution | 15 bits, configurable to 16 bits |
Conversion time | < 4 ms |
Accuracy | < ± 0.1% of the full scale value |
Actuator power supply | from the load voltage UP |
Power supply | feed: 1 x M8 male socket, 4-pin |
Bits in the process image | A: 4 x 16 bit data, optional: 4 x 8 bit control/status |
Electrical isolation | Control voltage / fieldbus: depending on the bus system |
Permissible ambient temperature during operation | 0 °C ... 55°C |
Permissible ambient temperature during storage | -25 °C ... + 85 °C |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection rating | IP65, IP66, IP67 (conforms to EN 60529) |
Connection see Connection.
Parameterization, see Parameterization description.
Mapping see Mapping description.
Weight and dimensions see page Dimensions.