IP204x-Bxxx, IE204x
8 Channel Digital Output 24 VDC, Imax = 2.0 A (total current max. 12 A)
The IP204x digital output modules connect the binary control signals from the automation unit on to the actuators at the process level. The 8 outputs handle load currents of up to 2 A each, although the total current is limited to 12 A. The outputs are supplied by three load circuits; for this reason these modules do not relay the supply voltage. The signal state is indicated by means of light emitting diodes. The signals are optionally connected via 8 mm snap-on plugs (IP2040), screw-in M8 connectors (IP2041) or screw-in M12 connectors (IP2042). The outputs are short-circuit proof and protected against inverse connection.
IP204x-Bxxx, IE204x 1:
Technical data
IP2040-Bxxx / IE2040
IP2041-Bxxx / IE2041
IP2042-Bxxx / IE2042
Number of outputs
8
Output connections
Ø 8 snap on
M8 screw-in
M12 screw-in
Load type
ohmic, inductive, lamp load
Nominal voltage
24 VDC (20 V ... 29 V)
Output current
max. 2.0 A per channel, individually short-circuit proof, total current 12 A:
- channels 0...3: S 4 A
- channels 4...5: S 4 A
- channels 6...7: S 4 A
Short circuit current
typical 4.0 A
Load voltage current consumption
typical 50 mA per channel
Sensor supply
derived from the control voltage, max. 0.5 A per channel, fully short-circuit proof
Power supply
Feed: 2 x M8 connector, 4-pin; no downstream connection
Bits in process image
8 bits output
Electrical isolation
control voltage / fieldbus: yes
channels / control voltage: no
between the channels: no
Permissible ambient temperature during operation
0°C ... +55°C
Permissible ambient temperature during storage
-25 °C ... +85°C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC resistance burst / ESD
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Installation position
variable
See the connection diagram for details of the connection.
See the mapping description for details of the mapping.
See dimension page for weight and dimensions.