IP202x-Bxxx, IE202x
8 Channel Digital Output 24 VDC, Imax = 2.0 A (total current max. 4 A)
The IP202x digital output modules connect the binary control signals from the automation unit on to the actuators at the process level. The 8 outputs handle load currents of up to 2 A each, although the total current is limited to 4 A. This makes these modules particularly suitable for applications in which not all of the outputs are active at the same time, or in which not all of the actuators draw 2 A signal current. The signal state is indicated by means of light emitting diodes.
The signals are optionally connected via 8 mm snap-in plugs (IP2020), screw-in M8 connectors (IP2021) or screw-in M12 connectors (IP2022). The outputs are short-circuit proof and protected against inverse connection.
Technical data
IP2020-Bxxx / IE2020
IP2021-Bxxx / IE2021
IP2022-Bxxx / IE2022
Number of outputs
8
Output connections
Ø 8 snap on
M8 screw-in
M12 screw-in
Load type
ohmic, inductive, lamp load
Nominal voltage
24 VDC (20 V ... 29 V)
Output current
max. 2.0 A each channel, individually short-circuit proof, total current max. 4 A
Short circuit current
typical 4.0 A
Load voltage current consumption
typical 30 mA per channel
Sensor supply
derived from the control voltage, max. 0.5 A per channel, fully short-circuit proof
Power supply
Feed: 1 x M8 connector, 4-pin; downstream connection: 1 x M8 socket, 4-pin
Bits in process image
8 bits output
Electrical isolation
control voltage / fieldbus: yes
channels / control voltage: no
between the channels: no
Permissible ambient temperature during operation
0°C ... +55°C
Permissible ambient temperature during storage
-25 °C ... +85°C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC resistance burst / ESD
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Installation position
variable
See the connection diagram for details of the connection.
See the mapping description for details of the mapping.
See dimension page for weight and dimensions.