Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | EP92x4-0023 | EP92x4-0024 |
Connection | Input: 7/8-inch plug, 5-pin, 16-UN thread Forwarding connection: 7/8-inch socket, 5-pin, 16-UN thread | Input: M12 connector, 5-pin, L-coded Forwarding connection: M12 socket, 5-pin, L-coded |
US nominal voltage | 24 VDC (-15 % / +20 %) | 24 VDC (-15 % / +20 %) |
US sum current 1) | max. 16 A at 40 °C | max. 16 A |
Current consumption from US | 110 mA + sum of the output currents | 110 mA + sum of the output currents |
UP nominal voltage | 24 VDC (-15 % / +20 %) | 24 VDC (-15 % / +20 %) |
UP sum current 1) | max. 16 A at 40 °C | max. 16 A |
Current consumption from UP | 40 mA + sum of the output currents | 40 mA + sum of the output currents |
1) This value corresponds to the current carrying capacity of the connectors.
Outputs | EP92x4-0023 | EP92x4-0024 |
Number | 4 | 4 |
Connection | 4x M8 socket, black | 4x M8 socket, black |
Cable length | max. 30 m | max. 30 m |
Output current per channel | max. 4 A per US and UP | max. 4 A per US and UP |
Output current limitation per channel | Depending on the hardware version:
| 4.4 A per US and UP |
Output power limitation per channel | Only in HW 16 and higher: 100 W per US and UP. | 100 W per US and UP |
Overload switch-off | Individually configurable for each channel | Individually configurable for each channel |
Internal fuse | 7 A (FF) | 7 A (FF) |
Parallel connection of outputs | Not permissible | Not permissible |
Inrush delay 2) | adjustable: 10 ms, 100 ms, 200 ms | adjustable: 10 ms, 100 ms, 200 ms |
2) The output voltages are switched on one after the other at the start so that the
input inrush currents do not add up.
Protective functions and diagnostics | EP9214-002x | EP9224-002x |
Overtemperature protection | Threshold values:
The outputs can only be switched on if the temperature is below 70 °C. | |
Undervoltage protection | Threshold values:
The outputs can only be switched on if the voltage is higher than 21 V. | |
Data logging | -- | 40 entries Sample time: 1...1000 ms |
Reset contact and signaling contact | |
Connection | M8 connector X3: 3-pin, black M8 socket X4: 3-pin, black |
Reset contact | Digital input, nominal voltage: 24 VDC |
Signaling contact | Potential-free NO contact |
Measured values | EP9214-002x | EP9224-002x |
Presentation | -- | Measured current values:
Measured voltage values: 100 mV / LSB |
Resolution | -- | Measured current values: 10 mA Measured voltage values: 100 mV |
Accuracy | -- | 5 % of full scale value |
Housing data | |
Dimensions W × H × D | 60 mm × 150 mm × 26,5 mm (without connectors) |
Weight |
approx. 440 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25…+60 °C -25...+45 °C (+55 °C) according to UL, see chapter UL Requirements. |
Ambient temperature during storage | -40…+85 °C |
Vibration resistance, shock resistance | in accordance with EN 60068-2-6 / EN 60068-2-27 |
EMC immunity / emission | in accordance with EN 61000-6-2 / EN 61000-6-4 |
Protection rating | IP65, IP66, IP67 according to EN 60529 (not evaluated by UL) |
Approvals/markings | |
Approvals/markings *) |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |