Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | |
Connection | Power supply (X70): plug B17 5G 1.5mm² ENP Downstream connection (X71): socket B17 5G 1.5mm² ENP |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current IS,sum | max. 15.5 A at 45 °C |
Current consumption from US | 110 mA + Load: IS1, IS2, IS3, IS4 |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP sum current IP,sum | max. 15.5 A at 45 °C |
Current consumption from US | 40 mA + Load: IP1, IP2, IP3, IP4 |
EtherCAT P ports | from hardware 04 | up to hardware 03 |
Number | 4 | 4 |
Connection | 4 x M8 socket, P-coded, 4-pin, shielded | 4 x M8 socket, P-coded, 4-pin, shielded |
Number of EtherCAT P slaves per port | max. 10 1) | max. 10 1) |
Output current per port | max. 3 A per US and UP | max. 3 A per US and UP |
Current limitation per port | 3.3 A per US and UP | 5 A per US and UP.
Power limitation per port | 100 W per US and UP | -- |
Fuse per port | Fuse 5 A according to UL 248-1
| Rated current: 5 A |
Capacitive load per port | max. 2200 µF per US and UP | |
Time offset for switching on the ports 2) |
Power loss at full load | max. 10 W (at 3 A output current per US and UP on all ports)
1) This value is a typical value. The actual possible number of EtherCAT P slaves per port is influenced by the following factors:
- Cable lengths
- The inrush current of sensors/actuators connected to the EtherCAT P slaves
2) The output voltages of the EtherCAT P ports are switched on one after the other at the start so that the inrush currents do not add up. See chapter Switch output voltages.
Protective functions and diagnostics | |
Overtemperature protection | Threshold values: Twarn = 75 °C → Warning if exceeded |
Undervoltage protection | Threshold values: Uwarn = 21.6 V → Warning when falling below |
Data logger: sampling interval |
Data logger: buffer size | 25 entries. |
Measured values | |
Resolution | Measured current values: 10 mA Measured sum current values US + UP: 10 mA Measured voltage values: 100 mV Measured temperature values: 1 K |
Representation | Measured current values: 1 mA / LSB Measured sum current values US + UP: 10 mA / LSB Measured voltage values: 100 mV / LSB Measured temperature values: 1 K / LSB (Celsius scale) |
Housing data | |
Dimensions W × H × D | 60 mm × 150 mm × 26,5 mm (without connectors) |
Weight | approx. 540 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25 … +60 °C |
Ambient temperature during storage | -40 … +85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals / markings | |
Approvals / markings *) | CE, UL under preparation |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |