Configuration objects
8020 STM Motor Settings Ch.1
8030 STM Motor Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8020:0
8030:0
STM Motor Settings Ch.n
USINT
RO
0x19 (25dec)
8020:01
8030:01
Peak current
If the motor current exceeds this value, the output stage of the affected channel is disabled and the diagnostic bit "Channel n short circuit" is set
Unit: [mA].
UINT
RW
0x3e (62dec)
8020:02
8030:02
Rated current
The nominal current of the motor. See motor data sheet. This parameter is used for the I2T calculation of the motor. (Thermal overload protection)
Unit: [mA].
UINT
RW
0x3e (62dec)
8020:03
8030:03
Rated voltage
The nominal voltage of the motor. See motor data sheet.
Unit: [0.01 V].
UINT
RW
0x960 (2400dec)
8020:04
8030:04
Phase to phase resistance
The ohmic resistance between two motor phases.
Unit: [0.01 ohm].
UINT
RW
0x64 (100dec)
8020:09
8030:09
Start velocity
Threshold value: the motor remains in the alignment phase as long as the output variable "Velocity" is smaller than this parameter.
If the value of this parameter is too low, commutation errors may occur.
Unit: [°/s].
UINT
RW
0xbb8 (3000dec)
8020:13
8030:13
Mechanical to electrical ratio
You can experimentally determine or calculate the value for this parameter.
UINT
RW
0x1 (1dec)
8020:14
8030:14
Rated velocity
Unit: [°/s].
UINT
RW
0x1388 (5000dec)
8020:16
8030:16
I2T warn level
Warning threshold value of the I2T overload protection for the motor.
If the I2T value exceeds this threshold, the diagnostic bit "Channel n overload I2T warning" is set.
Unit: [%].
USINT
RW
0x50 (80dec)
8020:18
8030:18
I2T error level
Fault threshold value of the I2T overload protection for the motor.
If the I2T value exceeds this threshold, the diagnostic bit "Channel n overload I2T error" is set. The motor is switched torque-free.
Unit: [%].
USINT
RW
0x6e (110dec)
8020:19
8030:19
Motor thermal time constant
Thermal time constant of the I2T overload protection for the motor.
You can find the thermal time constant in the motor data sheet.
Unit: [0.1 s].
UINT
RW
0xf (15dec)
8022 STM Features Ch.1
8032 STM Features Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8022:0
8032:0
STM Features Ch.n
USINT
RO
0x51 (81dec)
8022:11
8032:11
Select info data 1
Possible values:
  • 7dec: Motor velocity
  • 8dec: Motor velocity filtered
  • 11dec: Motor I2T load
  • 12dec: Amplifier I2T load
  • 13dec: Motor dc current
  • 14dec: Motor dc current filtered
  • 17dec: Motor back emf
  • 18dec: Motor restart counter
  • 101dec: Internal temperature
  • 104dec: Motor supply voltage
USINT
RW
0x7 (7dec)
8022:19
8032:19
Select info data 2
Possible values:
USINT
RW
0xb (11dec)
8022:51
8032:51
Select info data 3
Possible values:
USINT
RW
0xd (13dec)
8023 STM Controller Settings 4 Ch.1
8033 STM Controller Settings 4 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8023:0
8033:0
STM Controller Settings 4 Ch.n
USINT
RO
0x26 (38dec)
8023:03
8033:03
Disable motor diagnosis
Deactivates the motor protection functions for the duration of the alignment phase.
RW
00
8023:04
8033:04
Disable I2T current limitting
Disables the current limitation that is triggered if the I2T value of the motor becomes too high.
  • FALSE: The output current is limited if the I2T value of the motor exceeds 97 %.
  • TRUE: no current limitation.
RW
00
8023:11
8033:11
Velocity loop integral time
Integral component Ti of the speed controller.
Unit: [0.1 ms].
UDINT
RW
0x1f4 (500dec)
8023:12
8033:12
Velocity loop proportional gain
Proportional component KP of the speed controller.
Unit: [µV (°/s)].
UDINT
RW
0x0 (0dec)
8023:13
8033:13
Velocity feed forward gain
Speed controller feedforward: This parameter determines the proportion of the speed setpoint that is bypassed by the speed controller.
USINT
RW
0x64 (100dec)
8023:14
8033:14
Sensorless offset scaling
Output current during the alignment phase and the start-up phase, specified in % of the nominal current (parameter 80n0:02 "Rated current").
SINT
RW
0x32 (50dec)
8023:15
8033:15
Align duration
Duration of the alignment phase.
Unit: [ms].
UINT
RW
0x3e8 (1000dec)
8023:18
8033:18
Rampup duration
Duration of the start-up phase.
Unit: [ms].
UINT
RW
0xc8 (200dec)
8023:19
8033:19
Rampup velocity
Target speed that the conveyor roller should have at the end of the start-up phase.
Unit: [°/s].
UINT
RW
0x341 (833dec)
8023:21
8033:21
Rampup needed switchover events
Number of successful commutations required within the start-up phase for the start-up phase to be considered "successful". If the start-up phase is not successful, the output stage is shutdown and a commutation error is output.
UINT
RW
0x1 (1dec)
8023:22
8033:22
Commutation threshold
This parameter is used to adapt the commutation for different motors.
UINT
RW
0x32 (50dec)
8023:23
8033:23
Current loop proportional gain
Proportional component of the current controller.
Unit: [0.1 V/A].
UINT
RW
0x2 (2dec)
8023:24
8033:24
Current loop integral time
Integral action time (Tn) of the current controller.
Unit: [0.1 ms].
UINT
RW
0x14 (20dec)
8023:25
8033:25
Restart after error number of repetition
After a commutation error has occurred, the motor can be restarted automatically. See chapter Autoacknowledge: acknowledge errors automatically.
This parameter defines how many commutation errors with subsequent restart may occur before the motor is finally switched off. If this parameter is zero, the motor is switched off immediately after a commutation error in nominal operation.
UINT
RW
0x0 (0dec)
8023:26
8033:26
Restart after error delay
This parameter fixes how long to wait after a commutation error in nominal operation before restarting the motor. See also 80n3:25.
Unit: [ms].
UINT
RW
0x3e (62dec)
8040 ZNCTRL Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8040:0
USINT
RO
0x24 (36dec)
8040:01
Disable zone
Disable ZPA mode for this zone.
RW
00
8040:03
Invert motor direction
Reversal of the direction of rotation of the motor.
If the motor phases have been connected the wrong way round, the motor will rotate in the wrong direction.
With this parameter you can correct this without having to rewire the motor.
RW
00
8040:04
Disable motor in stop
Switches the motor torque-free at standstill.
RW
00
8040:12
External reset input hardware selection
Selection of the digital input for an external reset signal.
The assignment of the connection designations can be found in the chapter Digital inputs / outputs.
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
  • 65dec: Control input 1
  • 66dec: Control input 2
  • 67dec: Control input 3
  • 68dec: Control input 4
  • 4097dec: Input 1 low active
  • 4098dec: Input 2 low active
  • 4099dec: Input 3 low active
  • 4100dec: Input 4 low active
  • 4161dec: Control input 1 low active
  • 4162dec: Control input 2 low active
  • 4163dec: Control input 3 low active
  • 4164dec: Control input 4 low active
UINT
RW
0x0 (0dec)
8040:13
Zone sensor input hardware selection
Selection of the digital input for the zone sensor.
Recommendation: change this parameter only if you need to invert the sensor signal. See chapter "Cabling", section Sensor signals.
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
UINT
RW
0x1 (1dec)
Index (hex)
Meaning
Data type
Flags
Default
8040:14
Upstream control input hardware selection
Configuration of digital inputs for ZPA communication.
Change these parameters only if you know exactly what you are doing.
These parameters must be in the factory setting for the ZPA communication via M8 cables to work.
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
  • 129dec: Internal variable 1
  • 130dec: Internal variable 2
  • 144dec: PDO value
  • 4097dec: Input 1 [low active]
  • 4098dec: Input 2 [low active]
  • 4099dec: Input 3 [low active]
  • 4100dec: Input 4 [low active]
  • 4161dec: Control input 1 [low active]
  • 4162dec: Control input 2 [low active]
  • 4163dec: Control input 3 [low active]
  • 4164dec: Control input 4 [low active]
UINT
RW
0x41 (65dec)
8040:15
Upstream control output hardware selection
Configuration of digital outputs for ZPA communication.
Possible values:
  • 0dec: None
  • 1dec: Output 1
  • 2dec: Output 2
  • 3dec: Output 3
  • 4dec: Output 4
  • 65dec: Control output 1
  • 66dec: Control output 2
  • 67dec: Control output 3
  • 68dec: Control output 4
UINT
RW
0x42 (66dec)
8040:16
Downstream control input hardware selection
Configuration digital inputs for ZPA communication.
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
  • 144dec: PDO value
UINT
RW
0x82 (130dec)
8040:17
Downstream control output hardware selection
Possible values:
  • 0dec: None
  • 1dec: Output 1
  • 2dec: Output 2
  • 3dec: Output 3
  • 4dec: Output 4
UINT
RW
0x81 (129dec)
8040:1B
Initialisation run max duration
The maximum duration of the initialization run.
Unit: [ms].
UINT
RW
0x2710 (10000dec)
8040:1C
Loading timeout
The maximum duration for accepting a package from the previous zone.
If the time is exceeded, the zone is assumed to be empty.
Unit: [ms].
UINT
RW
0x2710 (10000dec)
8040:1D
Manual removing timeout
If a package leaves the detection zone of the sensor even though it was not conveyed further by the motor, it is assumed that the package was removed manually.
The controller then waits a period of time before assuming that the zone is actually empty.
The timespan is set by this parameter.
Unit: [ms].
UINT
RW
0x3e8 (1000dec)
8040:1E
Loading follow-up time
When the zone accepts a package, the motor runs until the sensor detects the package.
The motor then continues to run for a short period of time to ensure that the package is safely within the sensor's detection range.
Unit: [ms].
UINT
RW
0xc8 (200dec)
8040:1F
Unloading follow-up time
If the zone continues to convey a package, the motor runs until the package leaves the detection range of the sensor.
The motor then continues to run for a short period of time to ensure that the package has been detected by the rollers of the subsequent zone.
The closer the sensor is to the end of the zone, the shorter this timespan must be.
Unit: [ms].
UINT
RW
0x3e8 (1000dec)
8040:20
Motor velocity
Presetting of the motor speed.
Unit: [°/s].
INT
RW
0x168 (360dec)
8040:21
Motor acceleration
Preset of the acceleration ramp when starting the motor.
Unit: [°/s2].
UINT
RW
0x2710 (10000dec)
8040:22
Motor decceleration
Presetting of the braking ramp when stopping the motor.
Unit: [°/s2].
UINT
RW
0x2710 (10000dec)
8040:23
Train Release Delay
Delay time for the release type "Train Release".
This delay time prevents current peaks that would result from starting multiple motors at the same time.
Unit: [ms].
UINT
RW
0x64 (100dec)
8040:24
Unloading timeout
The maximum duration for conveying a package out of the zone.
If the time is exceeded, the zone is still assumed to be full.
Unit: [ms].
UINT
RW
0x2710 (10000dec)
8050 ZNCTRL Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8050:0
USINT
RO
0x24 (36dec)
8050:01
Disable zone
RW
00
8050:03
RW
00
8050:04
RW
00
8050:12
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
UINT
RW
0x0 (0dec)
8050:13
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
UINT
RW
0x3 (3dec)
Index (hex)
Meaning
Data type
Flags
Default
8050:14
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
  • 144dec: PDO value
UINT
RW
0x81 (129dec)
8050:15
Possible values:
  • 0dec: None
  • 1dec: Output 1
  • 2dec: Output 2
  • 3dec: Output 3
  • 4dec: Output 4
UINT
RW
0x82 (130dec)
8050:16
Possible values:
  • 0dec: None
  • 1dec: Input 1
  • 2dec: Input 2
  • 3dec: Input 3
  • 4dec: Input 4
  • 144dec: PDO value
UINT
RW
0x44 (68dec)
8050:17
Possible values:
  • 0dec: None
  • 1dec: Output 1
  • 2dec: Output 2
  • 3dec: Output 3
  • 4dec: Output 4
UINT
RW
0x43 (67dec)
8050:1B
Unit: [ms].
UINT
RW
0x2710 (10000dec)
8050:1C
Loading timeout
Unit: [ms].
UINT
RW
0x2710 (10000dec)
8050:1D
Unit: [ms].
UINT
RW
0x3e8 (1000dec)
8050:1E
Unit: [ms].
UINT
RW
0xc8 (200dec)
8050:1F
Unit: [ms].
UINT
RW
0x3e8 (1000dec)
8050:20
Motor velocity
Unit: [°/s].
INT
RW
0x168 (360dec)
8050:21
Motor acceleration
Unit: [°/s2].
UINT
RW
0x2710 (10000dec)
8050:22
Motor decceleration
Unit: [°/s2].
UINT
RW
0x2710 (10000dec)
8050:23
Train Release Delay
Unit: [ms].
UINT
RW
0x64 (100dec)
8050:24
Unloading timeout
Unit: [ms].
UINT
RW
0x2710 (10000dec)
F80F STM Vendor data
Index (hex)
Meaning
Data type
Flags
Default
F80F:0
STM Vendor data
USINT
RO
0xf (15dec)
F80F:04
Warning temperature
Unit: [°C].
SINT
RW
0x50 (80dec)
F80F:05
Switch off temperature
Unit: [°C].
SINT
RW
0x64 (100dec)
F80F:09
Amplifier switchoff current
Unit: [mA].
UINT
RW
0x4650 (18000dec)
F80F:0A
Amplifier peak current
Unit: [mA].
UINT
RW
0x2ee0 (12000dec)
F80F:0B
Amplifier rated current
Unit: [mA].
UINT
RW
0xdac (3500dec)
F80F:0C
Amplifier minimal voltage
Unit: [0.01 V].
UINT
RW
0x708 (1800dec)
F80F:0D
Amplifier maximal voltage
Unit: [0.01 V].
UINT
RW
EP7402-0057: 0xbb8 (3000dec)
EP7402-0067: 0x1770 (6000dec)
EP7402-0167: 0x1770 (6000dec)
F80F:0E
Amplifier thermal time constant
Unit: [0.1 s].
UINT
RW
0x23 (35dec)
F80F:0F
Maximum rotary field frequency
Unit: [Hz].
UINT
RW
0x257 (599dec)
F810 ZNCTRL Device Settings
Index (hex)
Meaning
Data type
Flags
Default
F810:0
USINT
RO
0x15 (21dec)
F810:11
Operation mode
Selection of the operation mode.
Possible values:
  • 0: PLC mode
  • 16: Local control
UINT
RW
0x0 (0dec)
F810:13
Local control mode
Selection of ZPA release type.
Possible values:
  • 0: ZPA singulated release
  • 1: ZPA train release
UINT
RW
0x0 (0dec)
F810:14
Autoacknowledge number of attempts
UINT
RW
0x0 (0dec)
F810:15
Autoacknowledge delay
Unit: [ms].
UINT
RW
0x3e (62dec)