Limit value monitoring
You can define two limit values for each analog input:
- Limit 1
- Limit 2
For each limit value, there is a variable of the same name in the process data. See Process image chapter. The variable shows whether the current measured value lies above or below the limit value.
Defining a limit value
Enter the limit value in the corresponding CoE parameter.
Value range: 0x8000 … 0x7FFF (-32768 … 32767)
Connection | CoE object | Parameter | ||
X01 | 8100hex | AI Settings Ch.1 | 13hex | Limit 1 |
14hex | Limit 2 | |||
X02 | 8110hex | AI Settings Ch.2 | 13hex | Limit 1 |
X05 | 8120hex | AI Settings Ch.3 | 13hex | Limit 1 |
X06 | 8130hex | AI Settings Ch.4 | 13hex | Limit 1 |
Activating the monitoring
The limit value monitoring for both limit values is disabled in the factory setting.
Set the CoE parameter for the respective limit value to TRUE:
X01 | 8100hex | AI Settings Ch.1 | 07 | Enable limit 1 |
08 | Enable limit 2 | |||
X02 | 8110hex | AI Settings Ch.2 | 07 | Enable limit 1 |
X05 | 8120hex | AI Settings Ch.3 | 07 | Enable limit 1 |
X06 | 8130hex | AI Settings Ch.4 | 07 | Enable limit 1 |
Evaluation
Evaluate the input variables "Limit 1" and "Limit 2" in the process data in accordance with the following table:
Variable value | Meaning | |
"Swap limit bits" 1) = FALSE | "Swap limit bits" 1) = TRUE | |
0 | Monitoring is not activated for this limit value. | |
1 | The measured value is smaller than the limit value. | The measured value is greater than the limit value. |
2 | The measured value is greater than the limit value. | The measured value is smaller than the limit value. |
3 | The measured value is exactly the same size as the limit value. | |
1) "Swap limit bits" is a CoE parameter. "Swap limit bits" is FALSE in the factory setting.
X01 | 8100hex | AI Settings Ch.1 | 0Ehex | Swap limit bits |
X02 | 8110hex | AI Settings Ch.2 | 0Ehex | Swap limit bits |
X05 | 8120hex | AI Settings Ch.3 | 0Ehex | Swap limit bits |
X06 | 8130hex | AI Settings Ch.4 | 0Ehex | Swap limit bits |