EL9400, EL9410 - Introduction and Technical Data
Power supply terminals
EL9400, EL9410 - Introduction and Technical Data 1:
Fig.36: EL9400, EL9410
The EL9400 and EL9410 power supply terminals are used to refresh the E-bus via which the data exchange between EtherCAT Couplers and Terminals takes place. Each EtherCAT Terminal requires a certain current from the E-bus (see technical data: "Current consumption via E-bus"). This current is fed into the E-bus by the power supply unit of the respective EtherCAT Coupler. For configurations with a large number of EtherCAT Terminals, the EL9400/EL9410 can be used to increase the power supply to the E-bus by 2 A.
Unlike the EL9400, the EL9410 has diagnostics displayed by LED and in the process image. At the same time, the EL9400/EL9410 can establish a further potential group on the right-hand side by means of an external 24 V supply via the power contacts.
Technical data
Technical data
EL9400
EL9410
Input voltage
24 VDC
Output current to supply the E-bus
2 A
Power contact voltage
24 VDC
Power contact current load
max. 10 A
Electrical isolation
500 V (E-bus/field voltage)
Diagnostics
no
via LED and in the process image
Electrical connection to mounting rail
no
Renewed infeed
yes
Connection facility to additional power contact
1
Side by side mounting on EtherCAT Terminals with power contact
yes
Side by side mounting on EtherCAT Terminals without power contact
yes
Bit width in process image
2 diagnostic bits
Configuration
no address or configuration settings required
Weight
approx. 65 g
Permissible ambient temperature range during operation
0 °C ... +55 °C
-25 °C ... +55 °C
Permissible ambient temperature range during storage
-25 °C ... +85 °C
-40 °C ... +85 °C
Permissible relative air humidity
95 %, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Enhanced mechanical load capacity
yes, see also Installation instructions for enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable, see chapter Mounting of passive terminals
variable
Approvals / markings*
CE, cULus, UKCA, EAC, CCC, ATEX, IECEx
CE, cULus, UKCA, EAC, CCC, ATEX, IECEx, DNV
Ex markings
Standard
Marking
ATEX
II 3 G Ex ec IIC T4 Gc
IECEx
Ex ec IIC T4 Gc
Connection and LEDs EL9400, EL9410
EL9400, EL9410 - Introduction and Technical Data 2:
Fig.36: EL9400, EL9410 connection
Terminal point
No.
+24 V for E-bus
1
Supply input +24 V for the E-bus
+24 V
2
Supply input +24 V (internally connected to terminal point 6 and positive power contact)
0 V
3
0 V for supply input (internally connected to terminal point 7 and negative power contact)
4
Ground (internally connected to terminal point 8)
0 V for E-bus
5
0 V for E-bus supply input
+24 V
6
Supply input +24 V (internally connected to terminal point 2 and positive power contact)
0 V
7
0 V for supply input (internally connected to terminal point 3 and negative power contact)
8
Ground (internally connected to terminal point 4)
LEDs
LED
Color
Meaning
Power
(E-bus)
green
off
No voltage at the supply input for the E-bus
on
24 VDC at the supply input for the E-bus
Power
green
off
on
Diag Us**
red
off
No error
on
Undervoltage: Us or Up below 17 V
Diag Up**
red
off
No error
on
RUN**
green
These LEDs indicate the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
Flashing (2 Hz)
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Flashing (1 Hz)
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
Flashing (10 Hz)
State of the EtherCAT State Machine: BOOTSTRAP = function for Firmware updates of the terminal, for example
**EL9410 only
Process data (EL9410 only)
The EL9410 has a bit width of 2 bits (diagnostic bits for voltage Us [supply voltage for E-bus] and Up [voltage at the power contacts], "undervoltage") in the process image and is represented in the TwinCAT tree as follows:
EL9400, EL9410 - Introduction and Technical Data 3:
Fig.38: EL9410 in the TwinCAT tree
If the Up or Us voltage drops below 17 V, the corresponding "Undervoltage" diagnostic bit is set to TRUE (1).