EL9195 - Introduction and Technical Data
Shield terminal
EL9195 - Introduction and Technical Data 1:
Fig.28: EL9195
The EL9195 shield terminal enables the connection of the shield from the front via 2 terminal contacts, which are connected directly to the DIN rail, in order to be able to optimally dissipate electromagnetic irradiation.
The multiple tapping of the supply voltage via the front-side terminal contacts is additionally ensured by the EL9195 EtherCAT Terminal. 24 V and 0 V can each be tapped twice from the front. The power contacts are connected to the front-side terminal contacts and are passed through to the adjacent terminal. With the EL9195, the use of additional terminal blocks on the terminal strip can be reduced.
Technical data
Technical data
EL9195
Technology
Shield terminal for dissipating EMC interference
Power contact current load
max. 10 A
Power LED
Defect LED
Current consumption via E-bus
Nominal voltage
any up to 230 V AC/DC
Built-in fine-wire fuse
Electrical isolation
500 V (E-bus/field voltage)
Diagnostics
Message to E-bus
Power contact
2 x power contact
Renewed infeed
Connection facility to additional power contact
2
Side by side mounting on EtherCAT Terminals with power contact
only 2 power contacts
Side by side mounting on EtherCAT Terminals without power contact
Shield connection
2 x
Electrical connection to mounting rail
yes
Bit width in process image
0
Configuration
no address or configuration settings required
Weight
approx. 50 g
Permissible ambient temperature range during operation
-25 °C ... +60 °C
Permissible ambient temperature range during storage
-40 °C ... +85 °C
Permissible relative air humidity
95 %, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Enhanced mechanical load capacity
yes, see also Installation instructions for enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable, see chapter Mounting of passive terminals
Approvals / markings*
CE, cULus, UKCA, EAC, CCC,
ATEX, IECEx,
Ex markings
Standard
Marking
ATEX
II 3 G Ex ec IIC T4 Gc
IECEx
Ex ec IIC T4 Gc
EL9195 connection
CAUTION
Danger for persons and equipment!
  • In the project planning of the bus terminal system, observe the different potentials on the power contacts (24 V DC and 230 V AC) and if necessary use potential separation terminals (EL9080) to isolate the potentials!
  • Bring the bus terminal system into a safe, de-energized state before starting installation, disassembly or wiring of the terminal modules!
EL9195 - Introduction and Technical Data 2:
Fig.28: EL9195 connection
Terminal point
No.
1
internally connected to terminal point 5
…230 V AC/DC
2
Supply input: any voltage up to 230 V AC/DC
internally connected to terminal point 6 and positive or phase power contact
N
3
0 V / N
internally connected to terminal point 7 and negative or neutral conductor power contact
Shield
4
Shield (internally connected to terminal point 8 and DIN rail contact)
5
internally connected to terminal point 1
…230 V AC / DC
6
N
7
0 V / N
internally connected to terminal point 3 and negative or neutral conductor power contact
Shield
8
Shield (internally connected to terminal points 4 and 8 and DIN rail contact)