EL9100, EL9110, EL9190 - Introduction and Technical Data
Power supply terminal 24 V DC
The EL9100, EL9110, and EL9190 power supply terminals can be placed at any position between the input/output terminals to create an additional potential group or to supply the terminals to the right with higher currents in case of high current loads.
The E-bus will pass through.
Unlike the EL9100 and EL9190, the EL9110 has diagnostics displayed in the process image.
Technical data
Technical data | EL9100 | EL9110 | EL9190 | |
Nominal voltage | 24 V DC | variable, up to 230 V AC/DC | ||
Power contact current load | max. 10 A | |||
Electrical isolation | 500 V (E-bus/field voltage) | |||
Current consumption via E-bus | - | typ. 90 mA | - | |
Bit width in process image | - | 1 diagnostic bit | - | |
Configuration | no address or configuration settings required | |||
Power LED | yes | yes | no | |
Diagnostics | no | yes, in the process image | no | |
Electrical connection to mounting rail | no | |||
Renewed infeed | yes | |||
Connection facility to additional power contact | 1 | |||
Side by side mounting on EtherCAT Terminals with power contact | yes | |||
Side by side mounting on EtherCAT Terminals without power contact | yes | |||
Weight | approx. 50 g | |||
Permissible ambient temperature range during operation | -25 °C ... +60 °C | |||
Permissible ambient temperature range during storage | -40 °C ... +85 °C | |||
Permissible relative air humidity | 95 %, no condensation | |||
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |||
on 35 mm mounting rail, conforms to EN 60715 | ||||
Enhanced mechanical load capacity | yes, see also Installation instructions for enhanced mechanical load capacity | - | ||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |||
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |||
Protection rating | IP20 | |||
Installation position | variable, see chapter | variable | variable, see chapter | |
Approvals / markings* | CE, cULus, UKCA, EAC | |||
Ex markings
Standard | Marking |
ATEX | II 3 G Ex ec IIC T4 Gc |
IECEx | Ex ec IIC T4 Gc |
EL9100, EL9110, EL9190 connection
Danger for persons and equipment!
EL91100, EL9110 | EL9190 | ||||
Terminal point | Description | Terminal point | Description | ||
Name | No. | Name | No. |
| 1 | not used |
| 1 | not used |
+24 V | 2 | Supply input +24 V | 230 V AC/DC | 2 | Supply input 230 V AC/DC [any voltage up to 230 V AC/DC] |
0 V | 3 | 0 V | N | 3 | N |
⏚* | 4 | Ground (internally connected to terminal point 8 and power contact ground) | ⏚* | 4 | Ground (internally connected to terminal point 8 and power contact ground) |
| 5 | not used |
| 5 | not used |
+24 V | 6 | Supply input +24 V internally connected to terminal point 2 and positive power contact | 230 V AC/DC | 6 | Supply input 230 V AC/DC [any voltage up to 230 V AC/DC] |
0 V | 7 | 0 V | N | 7 | N |
⏚* | 8 | Protective conductor (internally connected with terminal point 4 and power contact ground) | ⏚* | 8 | Ground (internally connected to terminal point 4 and power contact ground) |
* from hardware version 02 | |||||
LEDs (EL9100 and EL9110 only)
LED | Color | Meaning | |
Power LED | green | off | No supply voltage |
on | 24 V DC at the supply input | ||
Process data (EL9110 only)
The EL9110 has a bit width of 1 bit (diagnostic bit for voltage at the power contacts, "PowerOK") in the process image and is represented in the TwinCAT tree as follows:
If there is no voltage at the power contacts, the corresponding diagnostic bit "PowerOK" is set to FALSE (0).