Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 6000 Input Data
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
6000:0 |
Input Data |
This object contains the DP output data of the DP slave (data are received by the DP master ). There is an entry in the object 0x6000 for each DP module with DP output data configured in object 0x8002. DP module m thereby corresponds to SubIndex m; if a DP module does not contain any DP output data, then this SubIndex does not exist. If the DP slave does not contain any DP output data, then object 0x6000 does not exist. SubIndex 0 contains the number of DP modules of the DP slave. |
UINT8 |
RO |
6000:01 |
if the first DP module has DP output data: DP output data of the first DP module |
OCTET-STRING |
RO |
6000:m |
if the mth DP module has DP output data: DP output data of the mth DP module |
OCTET-STRING |
RO |
Index 7000 Output Data
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
7000:0 |
Output Data |
This object contains the DP input data of the DP slave (data are sent to the DP master). There is an entry in object 0x7000 for each DP module with DP input data configured in object 0x8002. DP module m thereby corresponds to SubIndex m; if a DP module does not contain any DP input data, then this SubIndex does not exist. If the DP slave does not contain any DP input data, then object 0x7000 does not exist. SubIndex 0 contains the number of DP modules of the DP slave. |
UINT8 |
RO |
7000:01 |
if the first DP module has DP input data: DP input data of the first DP module |
OCTET-STRING |
RO |
7000:m |
if the mth DP module has DP input data: DP input data of the mth DP module |
OCTET-STRING |
RO |
Index 8000 DP Slave Parameter Set Slave
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default | |
8000:0 |
DP Slave Parameter Set Slave yyy |
This object contains the DP configuration of the (n+1)th configured DP slave (0 <= n <125). The object is to be transmitted with Complete Access, or SubIndex 0 must first be set to 0, then the individual SubIndexes transmitted (non-existent SubIndexes or gaps are thereby to be omitted) and finally SubIndex 0 set to the correct value. |
UINT8 |
RW |
0x33 (51dec) | |
8000:01 |
Station Address |
DP station address of the DP slave, permitted values: 0-125 |
UINT16 |
RW |
8000:04 |
Device type |
DP Ident Number of the DP slave |
UINT32 |
RW |
8000:1D |
Network Flags |
reserved for AMS via DP |
UINT16 |
RW |
0x0000 (0dec) | |
8000:1E |
Network Port |
UINT16 |
RW |
0x0000 (0dec) | |
8000:1F |
Network Segment Address |
OCTET-STRING[6] |
RW |
{0} | |
8000:20 |
Sl_Flag |
Sl_flag |
UINT8 |
RW |
0xA8 (168dec) | |
Bits 0-2 |
Reserve, must be 0 | |||||
Bit 3 |
Reserve, must be 1 | |||||
Bit 4 |
Bit 5 |
Bit 6 |
Bit 7 |
8000:21 |
Slave_Type |
UINT8 |
RW |
0x00 (0dec) | |
8000:22 |
Max_Diag_Data_Len |
Reserve, must be 244 |
UINT8 |
RW |
0xF4(244dec) | |
8000:23 |
Max_Alarm_Len |
UINT8 |
RW |
0x00 (0dec) | |
8000:24 |
Max_Channel_Data_Length |
Reserve, must be 240 |
UINT8 |
RW |
0xF0(240dec) | |
8000:25 |
Diag_Upd_Delay |
UINT8 |
RW |
0x00 (0dec) | |
8000:26 |
Alarm_Mode |
UINT8 |
RW |
0x00 (0dec) | |
8000:27 |
Add_Sl_Flag |
UINT8 |
RW |
0x01 (1dec) | |
8000:28 |
C1_Timeout |
Reserve, must be 1000 |
UINT16 |
RW |
0x03E8 (1000dec) | |
8000:29 |
Number of tolerated Data Exchange with no answer |
UINT8 |
RW |
0x00 (0dec) | |
8000:2A |
Parallel AoE Services |
Reserve, must be 5 |
UINT8 |
RW |
0x05 (5dec) | |
8000:2B |
Reaction on no answer |
BIT1 |
RW |
0x00 (0dec) | |
8000:2C |
Restart behavior after DP fault |
BIT1 |
RW |
0x00 (0dec) | |
8000:2D |
Master reaction after DP fault |
BIT1 |
RW |
0x00 (0dec) | |
8000:2E |
Changes of DP Inputs after DP fault |
0 |
Data of TxPDO n are set to 0 |
BIT1 |
RW |
1 |
Data of TxPDO n remain unchanged | |||||
8000:2F |
PKW supported |
BOOLEAN |
RW |
FALSE | |
8000:30 |
FDL only |
BOOLEAN |
RW |
FALSE | |
8000:31 |
Watchdog Base 1 ms |
BOOLEAN |
RW |
FALSE | |
8000:33 |
Cycle Access Divider |
UINT8 |
RW |
0x00 (0dec) | |
8000:34 |
Cycle Access Modulo |
UINT8 |
RW |
0x00 (0dec) | |
8000:35 |
Vendor specific reserved |
OCTET-STRING[25] |
RW |
{0} | |
Index 8002 DP CfgData Slave
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
8002:0 |
DP CfgData Slave |
This object contains the DP Cfg Data of the DP slave. |
OCTET-STRING[244] |
RW |
{0} |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F000:0 |
Modular device profile |
General information for the modular device profile |
UINT8 |
RO |
0x02 (2dec) |
F000:01 |
Module index distance |
Index distance of the objects of the individual channels |
UINT16 |
RO |
0x0010 (16dec) |
F000:02 |
Maximum number of modules |
Number of channels |
UINT16 |
RO |
0x0001 (1dec) |
Index F100 DP Status
Index (hex) | Name | Meaning | Data type | Flags | Default | |
F100:0 | DP Status | This object contains the DP status data, which are mapped into TxPDO 128 (Index 0x1A7F) | UINT8 | RO |
F100:01 | DP Communication Status | 0 | Slave is exchanging data | UINT8 | RO |
128 | Slave is ready for data exchange | |||||
129 | Slave is waiting for the ChkCfg telegram | |||||
130 | Slave is waiting for the SetPrm telegram | |||||
F100:0E | Sync Error | this is set if a synchronization error occurred in the preceding cycle in Distributed Clocks mode | BOOLEAN | RO |
F100:10 | TxPDO State | this is set if the DP slave is not exchanging data | BOOLEAN | RO |
F100:0F | TxPDO Toggle | this toggles if new DP outputs received by the DP master have been entered in the EtherCAT input buffer for the first time after an EtherCAT input update. | BOOLEAN | RO |