Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 6000-67C0 DP Inputs Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
6000+n*16:0
DP Inputs Slave yyy
This object exists for each configured DP slave and contains the DP input data of the DP slave. There is an entry in the input data object 0x6000+(n*16) for each DP module with DP input data configured in object 0x8002+(n*16). DP module m thereby corresponds to SubIndex m; if a DP module does not contain any DP input data, then this SubIndex does not exist. If a DP slave does not contain any DP input data, then object 0x6000+(n*16) does not exist. SubIndex 0 contains the number of DP modules of the (n+1)th configured DP slave.
UINT8
RO
(6000+n*16):01
if the first DP module has DP input data: DP input data of the first DP module
OCTET-STRING
RO
(6000+n*16):m
if the mth DP module has DP input data: DP input data of the mth DP module
OCTET-STRING
RO
Index 7000-77C0 DP Outputs Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
7000+n*16:0
This object exists for each configured DP slave and contains the DP output data of the DP slave. There is an entry in the input data object 0x7000+(n*16) for each DP module with DP output data configured in object 0x8002+(n*16). DP module m thereby corresponds to SubIndex m; if a DP module does not contain any DP output data, then this SubIndex does not exist. If a DP slave does not contain any DP output data, then object 0x7000+(n*16) does not exist. SubIndex 0 contains the number of DP modules of the (n+1)th configured DP slave.
UINT8
RO
(7000+n*16):01
if the first DP module has DP output data: DP output data of the first DP module
OCTET-STRING
RO
(7000+n*16):F4
if the mth DP module has DP output data: DP output data of the mth DP module
OCTET-STRING
RO
Index 8000-87C0 DP Slave Parameter Set Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
8000+n*16:0
This object contains the DP configuration of the (n+1)th configured DP slave (0 <= n <125). The object is to be transmitted with Complete Access, or SubIndex 0 must first be set to 0, then the individual SubIndexes transmitted (non-existent SubIndexes or gaps are thereby to be omitted) and finally SubIndex 0 set to the correct value.
UINT8
RW
0x33 (51dec)
(8000+n*16):01
Station Address
DP station address of the DP slave, permitted values: 0-125, the entry 0xF020:(n+1) is automatically updated with this
UINT16
RW
0x0000 (0dec)
(8000+n*16):04
Device type
DP Ident Number of the DP slave
UINT32
RW
0x00000000 (0dec)
(8000+n*16):1D
Network Flags
reserved for AMS via DP
UINT16
RW
0x0000 (0dec)
(8000+n*16):1E
Network Port
UINT16
RW
0x0000 (0dec)
(8000+n*16):1F
Network Segment Address
OCTET-STRING[6]
RW
{0}
(8000+n*16):20
Sl_Flag
Sl_flag
UINT8
RW
0x80 (128dec)
Bits 0-2
Reserve, must be 0
Bit 3
Activate DPV1 communication for DP slave
Bit 4
Data exchange telegram is sent as a DXB Broadcast
Bit 5
FailSafe function (send data exchange without data in the CLEAR (SAFE-OP) state) is active
Bit 6
Reserve, must be 0
Bit 7
Reserve, must be 1
(8000+n*16):21
Slave_Type
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):22
Max_Diag_Data_Len
maximum length of the DP DiagData of the DP slave (6 <= Max_Diag_Data_Len <= 244)
UINT8
RW
(8000+n*16):23
Max_Alarm_Len
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):24
Max_Channel_Data_Length
maximum length of the DPV1 telegram of the DP slave (4 <= Max_Channel_Data_Length <= 244)
UINT8
RW
(8000+n*16):25
Diag_Upd_Delay
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):26
Alarm_Mode
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):27
Add_Sl_Flag
Reserve, must be 1
UINT8
RW
0x01 (1dec)
(8000+n*16):28
C1_Timeout
Timeout during waiting for a DPV1 response (in 10 ms)
UINT16
RW
(8000+n*16):29
Number of tolerated Data Exchange with no answer
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):2A
Parallel AoE Services
Number of parallel AoE services (e.g. for DPV1); the value 0 corresponds to 5 parallel services
UINT8
RW
0x00 (0dec)
(8000+n*16):2B
Reaction on no answer
0
Data exchange is quit
BIT1
RW
0x00 (0dec)
1
DP slave remains in Data Exchange if a valid Data Exchange response is received within the DP watchdog time
(8000+n*16):2C
Restart behavior after DP fault
0
DP slave is automatically restarted (Set_Prm-Unlock, then Slave_Diag, Set_Prm-Lock, Chk_Cfg, Slave_Diag)
BIT1
RW
0x00 (0dec)
1
The DP slave must be manually restarted via AoE
Index (hex)
Meaning
Data type
Flags
Default
(8000+n*16):2D
Master reaction after DP fault
0
no response
BIT1
RW
0x00 (0dec)
1
Data exchange with all DP slaves is stopped (Set_Prm-Unlock to all slaves); DP communication must be restarted via AoE
(8000+n*16):2E
Changes of DP Inputs after DP fault
0
Data of TxPDO n are set to 0
BIT1
RW
0x00 (0dec)
1
Data of TxPDO n remain unchanged
(8000+n*16):2F
PKW supported
Reserve, must be 0
BOOLEAN
RW
0x00 (0dec)
(8000+n*16):30
FDL only
Reserve, must be 0
BOOLEAN
RW
0x00 (0dec)
(8000+n*16):31
Watchdog Base 1 ms
FALSE
The basis for the DP watchdog is 10 ms
BOOLEAN
RW
0x00 (0dec)
TRUE
The basis for the DP watchdog is 1 ms
(8000+n*16):33
Cycle Access Divider
Reserve, must be 1
UINT8
RW
0x01 (1dec)
(8000+n*16):34
Cycle Access Modulo
Reserve, must be 0
UINT8
RW
0x00 (0dec)
(8000+n*16):35
Vendor specific reserved
Reserve, must be 0
OCTET-STRING[25]
RW
{0}
Index 8001-87C1 DP PrmData Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
8001+n*16:0
This object contains the DP Prm Data of the (n+1)th configured DP slave.
OCTET-STRING[244]
RW
{0}
Index 8002-87C2 DP CfgData Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
8002+n*16:0
This object contains the DP Cfg Data of the (n+1)th configured DP slave.
OCTET-STRING[244]
RW
{0}
Index A000-A7C0DP Status data Slave yyy
Index (hex)
Meaning
Data type
Flags
Default
A000+n*16:0
DP Status data Slave.000
This object contains the status data of the (n+1)th configured DP slave.
UINT8
RO
0x04 (4dec)
(A000+n*16):01
DP state
State of the DP connection (identical to entry 0xF102:(n+1))
UINT8
RO
0x00 (0dec)
(A000+n*16):02
Ext Diag
This entry indicates whether the diagnostic information in object 0xA002+(n*16) has changed
BOOLEAN
RO
0x00 (0dec)
(A000+n*16):03
Repeat Counter
This entry increments on each repeat telegram to the DP slave
UINT32
RO
0x00000000 (0dec)
(A000+n*16):04
No Answer Counter
This entry increments on each telegram to the DP slave to which no response is received
UINT32
RO
0x00000000 (0dec)
Index A002-A07E DP Diag data Slave.000
Index (hex)
Meaning
Data type
Flags
Default
A002+n*16:0
This object contains the DP DiagData of the (n+1)th configured DP slave.
OCTET-STRING[244]
RO
{0}
Index (hex)
Meaning
Data type
Flags
Default
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index distance of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
0x007D (125dec)
F000:03
General Configuration Entries
General configuration entries
UINT32
RO
0x70000009 (1879048201dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default
F010:0
Module list
Max. subindex
UINT8
RW
0x00 (0dec)
F010:01
reserved
reserved
F010:7D
reserved
Index F101 DP Master Status data
Index (hex)
Meaning
Data type
Flags
Default
F101:0
This object contains the DP master status data, which are mapped into TxPDO 134 (Index 0x1A85)
UINT8
RO
0x17 (23dec)
F101:01
Bus Error Counter
increments on each bus error
UINT16
RO
0x0000 (0dec)
F101:02
Cycle Counter
increments on each DP cycle
UINT16
RO
0x0000 (0dec)
F101:03
Slave Status Counter
Number of DP slaves that were not exchanging data in the preceding cycle
UINT16
RO
0x0000 (0dec)
F101:04
Cycle Time
Cycle time of the preceding DP cycle in 1/9 µs
UINT16
RO
0x0000 (0dec)
F101:05
Repeat Counter
Number of repeats in the preceding DP cycle
UINT16
RO
0x0000 (0dec)
F101:14
Device Diag
indicates whether diagnostic information is present in the master that can be collected via AoE
BOOLEAN
RO
0x00 (0dec)
F101:15
Sync Error
this is set if a synchronization error occurred in the preceding cycle in Distributed Clocks mode
BOOLEAN
RO
0x00 (0dec)
F101:16
Cycle Toggle
toggles on each DP cycle
BOOLEAN
RO
0x00 (0dec)
F101:17
Cycle State
this is set if at least one DP slave is not exchanging data
BOOLEAN
RO
0x00 (0dec)
Index F102 DP Slave Status data
Index
Meaning
Data type
Flags
Default
F102:0
This object contains the status of communication to the DP slaves that is mapped to TxPDO 133 (index 0x1A84)
UINT8
RO
F102:01
Communication status of the first configured DP slave (in the objects 0x8000, 0x8001, 0x8002)
UINT8
RO
0
Slave is exchanging data; DP inputs are up to date
1
Slave is deactivated (via AoE)
2
Slave does not respond
3
slave currently exchanging data with another master
4
incorrect slave response (e.g. service not activated in the case of data exchange)
5
Slave reports parameterization error (error in the SetPrm telegram (usually Ident-Number or UserPrmData))
6
Slave reports that a DP function is not supported
7
Slave reports configuration error 8 - error in the ChkCfg telegram (usually incorrect DP module configured))
8
Slave is in DP bootup but is not yet ready for data exchange
9
Slave reports static diagnosis
11
Response with bus error (e.g. parity or checksum error)
14
Response with telegram error (e.g. request bit set)
15
Slave reports no resources (e.g. PrmData or CfgData is too long)
16
Slave reports that the DP service is not activated
17
Unexpected telegram received (e.g. token when waiting for a response from a slave)
18
Slave is ready for data exchange; however, no process data are exchanged over EtherCAT as yet
F102:7D
Communication status of the mth configured DP slave
UINT8
RO
Index F10F Cycle Statistic data
Index (hex)
Meaning
Data type
Flags
Default
F10F:0
This object contains the measured times of the respective last cycle. They can be transferred cyclically with TxPDO 135 (0x1A86) or TxPDO 136 (0x1A87) and they then always contain the values for the preceding cycle.
UINT8
RO
0x08 (8dec)
F10F:01
Multiplier
The entries 0xF10F:03, 0xF10F:04, 0xF10F:05 and 0xF10F:06 must be multiplied by this value in order to convert these entries into the unit 100 ns
UINT16
RO
0x0000 (0dec)
F10F:02
Divider
The entries 0xF10F:03, 0xF10F:04, 0xF10F:05 and 0xF10F:06 must be divided by this value in order to convert these entries into the unit 100 ns
UINT16
RO
0x0000 (0dec)
F10F:03
Cycle Time
Cycle time (0x1C32:05) of the preceding DP cycle in local ticks
UINT16
RO
0x0000 (0dec)
F10F:04
Cycle Distance Time
Distance between the last two SM2 events (only if 0x1C32:01 = 1 or 0x1C32:01 = 2)
UINT16
RO
0x0000 (0dec)
F10F:05
Output Calc And Copy Time
Output Calc And Copy Time (0x1C32:06) of the preceding DP cycle in local ticks
UINT16
RO
0x0000 (0dec)
F10F:06
Input Calc And Copy Time
Input Calc And Copy Time (0x1C33:06) of the preceding DP cycle in local ticks
UINT16
RO
0x0000 (0dec)
F10F:07
Output Delay Time
Output Delay Time (0x1C32:09) of the preceding cycle in ns
UINT32
RO
0x00000000 (0dec)
F10F:08
SM/SYNC Event Distance Time
SM/SYNC0 Event Distance Time (distance between SM2 and SYNC0 event) of the preceding cycle in ns (must be activated via register 0x816 in the ET1100).
INT32
RO
0x00000000 (0dec)
Index F800 DP Bus Parameter Set
Index (hex)
Meaning
Data type
Flags
Default
F800:0
This object contains the DP bus parameters. The object is to be transmitted with Complete Access, or SubIndex 0 must first be set to 0, then the individual SubIndexes transmitted (non-existent SubIndexes or gaps are thereby to be omitted) and finally SubIndex 0 set to the correct value.
UINT8
RW
0x18 (24dec)
F800:01
DL_Add
DP-Master station address
UINT8
RW
0x00 (0dec)
F800:02
Data_rate
Baud rate
UINT8
RW
0x00 (0dec)
0
9.6 kbaud
1
19.2 kbaud
2
93.75 kbaud
3
187.5 kbaud
4
500 kbaud
6
1.5 Mbaud
7
3 Mbaud
8
6 Mbaud
9
12 Mbaud
F800:03
Tsl
Slot time in bit times
UINT16
RW
F800:04
min Tsdr
Min. TSDR in bit times
UINT16
RW
0x0B (11dec)
F800:05
max Tsdr
Max. TSDR in bit times
UINT16
RW
F800:06
Tqui
Quiet Time in bit times
UINT8
RW
F800:07
Tset
Setup Time in bit times
UINT8
RW
F800:08
Ttr
Target Token Rotation Time in bit times
UINT32
RW
F800:09
G
GAP Update Factor (1-100)
UINT8
RW
0x64 (100dec)
F800:0A
HSA
Highest master address (0-126)
UINT8
RW
0x7E (126dec)
F800:0B
max_retry_limit
Maximum number of repeats (1-8)
UINT8
RW
F800:0C
Bp_Flag
Bit 0
Single master operation (no GAP update is sent)
UINT8
RW
0x00 (0dec)
Bits 1-6
Reserve, must be 0
Bit 8
Auto-Clear mode is on (DP master goes to CLEAR if a DP slave is not exchanging data)
Index F800 DP bus parameter set
Index (hex)
Meaning
Data type
Flags
Default
F800:0D
Min_Slave_Interval
Cycle time for DP telegrams (except data exchange (runs synchronously to the EtherCAT master))
UINT16
RW
F800:0E
Poll_Timeout
Reserve, must be 0
UINT16
RW
0x0000 (0dec)
F800:0F
Data_Control_Time
Cycle time of the Global_Control telegram
UINT16
RW
F800:10
Alarm_Max
Reserve, must be 0
UINT8
RW
0x00 (0dec)
F800:11
Max_User_Global_control
Reserve, must be 0
UINT8
RW
0x00 (0dec)
F800:12
Max Retry Limit (Data-Exchange)
Maximum number of data exchange repeats
BIT4
RW
F800:13
Send Set-Prm-Unlock
Reserve, must be 0
BIT2
RW
0x00 (0dec)
F800:14
Auto Clear Mode
Reserve, must be 0
BIT2
RW
0x00 (0dec)
F800:15
Operate Delay (in 100 ms)
Automatic switching to OPERATE in the OP state is delayed according to this setting
UINT8
RW
0x00 (0dec)
F800:16
Safety Time (in us)
Reserve, must be 0
UINT16
RW
0x0000 (0dec)
F800:17
Flags
Reserve, must be 0
UINT16
RW
0x0000 (0dec)
F800:18
Watchdog Reaction
0
DP Master in CLEAR Mode
OCTET-STRING[26]
RW
{0}
1
DP Master in OPERATE Mode
2
DP Master in STOP Mode
F800:1A
Vendor specific
Reserve, must be 0
OCTET-STRING[26]
RW
Index F920 AoE Settings
Index (hex)
Meaning
Data type
Flags
Default
F920:0
AoE Settings
Max. subindex
UINT8
RO
0x01 (1dec)
F920:01
Local AoE Net ID
Local AoE Net ID
OCTET-STRING[6]
RO
{0}
* These parameters depend on the baud rate; the following table shows the default values for the respective baud rate:
Data_rate
Tsl
max. Tsdr
Tqui
Tset
Ttr
max_retry_limit
Min_Slave_Interval
Data_Control_Time
Max Retry (DX)
9 (12 Mbaud)
1000
800
9
16
12000
4
10
1
4
8 (6 Mbaud)
600
450
6
8
12000
3
20
2
3
7 (3 Mbaud)
400
250
3
4
12000
2
40
4
2
6 (1.5 Mbaud)
300
150
0
1
12000
1
80
8
1
4 (500 kbaud)
200
100
0
1
12000
1
200
20
1
3 (187.5 kbaud)
150
100
0
1
12000
1
400
40
1
2 (93.75 kbaud)
150
100
0
1
12000
1
800
80
1
1 (19.2 kbaud)
150
100
0
1
12000
1
4000
400
1
0 (9.6 kbaud)
150
100
0
1
12000
1
8000
800
1