Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x0C1C1389 (203166601dec) |
Index 1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL6731 |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
06 |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
10 |
Index 1011 Restore default parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1011:0 |
Restore default parameters |
UINT8 |
RO |
0x01 (1dec) |
1011:01 |
SubIndex 001 |
If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state. |
UINT32 |
RW |
0x00000000 (0dec) |
Index 1018 Identity
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1018:0 |
Identity |
Information for identifying the slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
0x1A4B3052 (441135186dec) |
1018:03 |
Revision |
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description |
UINT32 |
RO |
0x00000000 (0dec) |
1018:04 |
Serial number |
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 |
UINT32 |
RO |
0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum of the Backup Parameter Storage (object 0x10F2, word 2-3) |
UINT32 |
RO |
0x00000000 (0dec) |
Index 10F2 Backup parameter storage
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default | |
10F2:0 |
Backup parameter storage |
If this object is used, no StartUp SDOs may be transmitted in the PREOP state, since the Backup Parameter Storage contains the complete StartUp SDOs (see Configuration of the EL6731 with Backup Parameter Storage). The EL6731 is rebooted 5s after the flashing of the Backup Parameter Storage (switches to INIT with AL status code = 0x60). The data have the following meaning: |
OCTET-STRING[n] |
RW |
Word-Offset |
Description | |||||
0 |
Command: with 0xC0DE, the received data are stored in the flash memory | |||||
1 |
Length of the data from word offset 4 in bytes | |||||
2-3 |
Checksum, which is calculated locally | |||||
4 |
Index of the object of the 1st StartUp SDO | |||||
5 |
len1: Length of the object of the 1st StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
6-n1 |
Data of the object of the 1st StartUp SDO as CompleteAccess (n1 = 2*((len1+1)/2)+5) | |||||
n1+1 |
Index of the object of the 2nd StartUp SDO | |||||
n1+2 |
len2: Length of the object of the 2nd StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
(n1+3)-n2 |
Data of the object of the 2nd StartUp SDO as CompleteAccess (n2 = 2*((len2+1)/2)+n1+2) | |||||
m |
Index of the object of the 3rd StartUp SDO | |||||
m+1 |
len3: Length of the object of the 3rd StartUp SDO as CompleteAccess (from SubIndex 0) in bytes | |||||
(m+2)-n3 |
Data of the object of the 3rd StartUp SDO as CompleteAccess (n3 = 2*((len3+1)/2)+m+1) | |||||
Index 10F3 Diagnosis History
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F3:0 |
Diagnosis History |
Maximum subindex |
UINT8 |
RO |
0x45 (69dec) |
10F3:01 |
Maximum Messages |
Maximum number of stored messages |
UINT8 |
RO |
0x00 (0dec) |
10F3:02 |
Newest Message |
Subindex of the latest message |
UINT8 |
RO |
0x00 (0dec) |
10F3:03 |
Newest Acknowledged Message |
Subindex of the last confirmed message |
UINT8 |
RW |
0x00 (0dec) |
10F3:04 |
New Messages Available |
Indicates that a new message is available |
BOOLEAN |
RO |
0x00 (0dec) |
10F3:05 |
Flags |
not used |
UINT16 |
RW |
0x0000 (0dec) |
10F3:06 |
Diagnosis Message 001 |
Message 1 |
OCTET-STRING[20] |
RO |
{0} |
10F3:45 |
Diagnosis Message 064 |
Message 64 |
OCTET-STRING[20] |
RO |
{0} |
Index 10F8 Actual Time Stamp
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F8:0 |
Actual Time Stamp |
Time stamp |
UINT64 |
RO |
Index 1600-167C RxPDO-Map DP-Slave yyy
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1600+n:0 |
RxPDO-Map DP-Slave yyy |
There is an RxPDO containing the DP output data of the DP slave for each configured DP slave. There is an entry in the RxPDO mapping object 0x1600+n for each DP module with DP output data configured in object 0x8002+(n*16). If a DP slave does not contain any DP output data, then the PDO mapping object 0x1600+n does not exist. These PDOs are mandatory and must always be contained in the PDO Assign object 0x1C12, depending on the configured DP slaves. SubIndex 0 contains the number of DP modules with DP output data of the (n+1)th configured DP slave. |
UINT8 |
RO |
(1600+n):01 |
first DP module with DP output data of the (n+1)th configured DP slave |
UINT32 |
RO |
(1600+n):FF |
last DP module with DP output data of the (n+1)th configured DP slave |
UINT32 |
RO |
Index 167F DPM RxPDO-Map Control
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
167F:0 |
DPM RxPDO-Map Control |
PDO Mapping RxPDO 128 |
UINT8 |
RO |
0x02 (2dec) |
167F:01 |
SubIndex 001 |
1st PDO Mapping entry (object 0xF200, entry 0x01) |
UINT32 |
RO |
0xF200:01, 1 |
167F:02 |
SubIndex 002 |
2nd PDO Mapping entry (15 bits align) |
UINT32 |
RO |
0x0000:00, 15 |
Index 187F DPM TxPDO-Par Status PDO
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
187F:0 |
DPM TxPDO-Par Status PDO |
PDO parameter TxPDO 128 |
UINT8 |
RO |
0x06 (6dec) |
187F:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 128 |
OCTET-STRING[10] |
RO |
80 1A 00 00 00 00 00 00 00 00 |
Index 1880 DPM TxPDO-Par Status PDO
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1880:0 |
PDO parameter TxPDO 129 |
UINT8 |
RO |
0x06 (6dec) |
1880:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 129 |
OCTET-STRING[10] |
RO |
81 1A 82 1A 83 1A 84 1A 85 1A |
Index 1881 DPM TxPDO-Par PDO State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1881:0 |
DPM TxPDO-Par PDO State |
PDO parameter TxPDO 130 |
UINT8 |
RO |
0x06 (6dec) |
1881:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 130 |
OCTET-STRING[10] |
RO |
Index 1882 DPM TxPDO-Par PDO Toggle
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1882:0 |
DPM TxPDO-Par PDO Toggle |
PDO parameter TxPDO 131 |
UINT8 |
RO |
0x06 (6dec) |
1882:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 131 |
OCTET-STRING[10] |
RO |
Index 1883 DPM TxPDO-Par DP Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1883:0 |
DPM TxPDO-Par DP Diag |
PDO parameter TxPDO 132 |
UINT8 |
RO |
0x06 (6dec) |
1883:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 132 |
OCTET-STRING[10] |
RO |
Index 1884 DPM TxPDO-Par DP Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1884:0 |
DPM TxPDO-Par DP Status |
PDO parameter TxPDO 133 |
UINT8 |
RO |
0x06 (6dec) |
1884:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 133 |
OCTET-STRING[10] |
RO |
Index 1885 DPM TxPDO-Par DP-Master Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1885:0 |
DPM TxPDO-Par DP-Master Diag |
PDO parameter TxPDO 134 |
UINT8 |
RO |
0x06 (6dec) |
1885:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 134 |
OCTET-STRING[10] |
RO |
Index 1886 DPM TxPDO-Par Cycle Statistics
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1886:0 |
DPM TxPDO-Par Cycle Statistics |
PDO parameter TxPDO 135 |
UINT8 |
RO |
0x06 (6dec) |
1886:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 135 |
OCTET-STRING[10] |
RO |
80 1A 87 1A 00 00 00 00 00 00 |
Index 1887 DPM TxPDO-Par DC Cyclic Statistics
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1887:0 |
DPM TxPDO-Par DC Cyclic Statistics |
PDO parameter TxPDO 136 |
UINT8 |
RO |
0x06 (6dec) |
1887:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 136 |
OCTET-STRING[10] |
RO |
80 1A 86 1A 00 00 00 00 00 00 |
Index 1A00-1A7C DPS TxPDO-Map Slave yyy
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A00+n:0 |
DPS TxPDO-Map Slave yyy |
There is one TxPDO containing the DP input data of the DP slave for each configured DP slave. There is an entry in the TxPDO mapping object 0x1A00+n for each DP module with DP input data configured in object 0x8002+(n*16). If a DP slave does not contain any DP input data, then the PDO mapping object 0x1A00+n does not exist. These PDOs are mandatory and must always be contained in the PDO Assign object 0x1C13, depending on the configured DP slaves. SubIndex 0 contains the number of DP modules with DP input data of the (n+1)th configured DP slave. |
UINT8 |
RO |
(1A00+n):01 |
first DP module with DP input data of the (n+1)th configured DP slave |
UINT32 |
RO |
(1A00+n):FF |
last DP module with DP input data of the (n+1)th configured DP slave |
UINT32 |
RO |
Index 1A7F DPM TxPDO-Map Status PDO
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A7F:0 |
DPM TxPDO-Map Status PDO |
PDO Mapping TxPDO 128 |
UINT8 |
RO |
0x03 (3dec) |
1A7F:01 |
SubIndex 001 |
1st PDO Mapping entry (object 0xF100, entry 0x01) |
UINT32 |
RO |
0xF100:01, 8 |
1A7F:02 |
SubIndex 002 |
2nd PDO Mapping entry (7 bits align) |
UINT32 |
RO |
0x0000:00, 7 |
1A7F:03 |
SubIndex 003 |
3rd PDO Mapping entry (object 0xF100, entry 0x0F) |
UINT32 |
RO |
0xF100:0F, 1 |
Index 1A80 DPM TxPDO-Map PDO Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A82:0 |
DPM TxPDO-Map PDO Status |
This PDO is assigned if Legacy Mapping (no MDP) is active |
UINT8 |
RO |
1A82:01 |
first PDO mapping entry in the case of Legacy Mapping |
UINT32 |
RO |
1A82:m |
last PDO mapping entry in the case of Legacy Mapping |
UINT32 |
RO |
Index 1A81 DPM TxPDO-Map PDO State
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A81:0 |
DPM TxPDO-Map PDO State |
In this PDO there is a bit for each configured DP slave that is set if the latter is not in exchanging data (a more detailed error cause can be found in 0xF102:m for the mth configured DP slave). If the bit is set, the data of the associated TxPDO m is to be ignored. This PDO is optional. |
UINT8 |
RO |
1A81:01 |
PDO state of the first configured DP slave (configured via the objects 0x800z) |
UINT32 |
RO |
1A81:m |
PDO state of the last (mth) configured DP slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
Index 1A82 DPM TxPDO-Map PDO Toggle
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A82:0 |
DPM TxPDO-Map PDO Toggle |
For each configured DP slave there is a bit in this PDO that toggles every time new DP input data has been received from the DP slave and updated in the EtherCAT input data. This PDO is optional. |
UINT8 |
RO |
1A82:01 |
PDO toggle of the first configured DP slave (configured via the objects 0x800z) |
UINT32 |
RO |
1A82:m |
PDO toggle of the last (mth) configured DP slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
Index 1A83 DPM TxPDO-Map DP Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A83:0 |
DPM TxPDO-Map DP Status |
In this PDO there is a byte for each configured DP slave that contains the communication state (object 0xF102) to the DP slave. This PDO is optional. |
UINT8 |
RO |
Number of configured DP slaves |
1A83:01 |
Node state of the first configured DP slave (configured via the objects 0x800z) |
UINT32 |
RO |
0xF102:01,8 |
1A83:m |
Node state of the last (mth) configured DP slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
0xF102:m,8 |
Index 1A84 DPM TxPDO-Map DP Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A84:0 |
DPM TxPDO-Map DP Diag |
In this PDO there is a bit for each configured DP slave that is set if the diagnostic information (object 0xF103) has changed. This PDO is optional. |
UINT8 |
RO |
1A84:01 |
Diag Flag of the first configured DP slave (configured via the objects 0x800z) |
UINT32 |
RO |
0xF103:01,1 |
1A84:FF |
Diag Flag of the last (mth) configured DP slave (configured via the objects 0x800z+(m-1)*16 (1 <= m <= 127)) |
UINT32 |
RO |
0xF103:m,1 |
Index 1A85 DPM TxPDO-Map DP-Master Diag
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A85:0 |
DPM TxPDO-Map DP-Master Diag |
PDO Mapping TxPDO 134 contains the DP master status (object 0xF101) |
UINT8 |
RW |
0x0D (13dec) |
1A85:01 |
SubIndex 001 |
1st PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x01 (Bus Error Counter)) |
UINT32 |
RW |
0xF101:01, 16 |
1A85:02 |
SubIndex 002 |
2nd PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x02 (Cycle Counter)) |
UINT32 |
RW |
0xF101:02, 16 |
1A85:03 |
SubIndex 003 |
3rd PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x03 (Slave Status Counter)) |
UINT32 |
RW |
0xF101:03, 16 |
1A85:04 |
SubIndex 004 |
4th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x04 (Cycle Time)) |
UINT32 |
RW |
0xF101:04, 16 |
1A85:05 |
SubIndex 005 |
5th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x05 (Repeat Counter)) |
UINT32 |
RW |
0xF101:05, 16 |
1A85:06 |
SubIndex 006 |
6th PDO Mapping entry (16 bits align) |
UINT32 |
RW |
0x0000:00, 16 |
1A85:07 |
SubIndex 007 |
7th PDO Mapping entry (16 bits align) |
UINT32 |
RW |
0x0000:00, 16 |
1A85:08 |
SubIndex 008 |
8th PDO Mapping entry (8 bits align) |
UINT32 |
RW |
0x0000:00, 8 |
1A85:09 |
SubIndex 009 |
9th PDO Mapping entry (4 bits align) |
UINT32 |
RW |
0x0000:00, 4 |
1A85:0A |
SubIndex 010 |
10th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x14 (Device Diag)) |
UINT32 |
RW |
0xF101:14, 1 |
1A85:0B |
SubIndex 011 |
11th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x15 (Sync Error)) |
UINT32 |
RW |
0xF101:15, 1 |
1A85:0C |
SubIndex 012 |
12th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x16 (Cycle Toggle)) |
UINT32 |
RW |
0xF101:16, 1 |
1A85:0D |
SubIndex 013 |
13th PDO Mapping entry (object 0xF101 (DP Master Status data), entry 0x17 (Cycle State)) |
UINT32 |
RW |
0xF101:17, 1 |
Index 1A86 DPM TxPDO-Map Cycle Statistics
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A86:0 |
DPM TxPDO-Map Cycle Statistics |
PDO Mapping TxPDO 135 contains the DP master cycle statistics (object 0xF10F) for the SM synchronous mode |
UINT8 |
RW |
0x05 (5dec) |
1A86:01 |
SubIndex 001 |
1st PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x03 (Cycle Time)) |
UINT32 |
RW |
0xF10F:03, 16 |
1A86:02 |
SubIndex 002 |
2nd PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x04 (Cycle Distance Time)) |
UINT32 |
RW |
0xF10F:04, 16 |
1A86:03 |
SubIndex 003 |
3rd PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x05 (Output Calc And Copy Time)) |
UINT32 |
RW |
0xF10F:05, 16 |
1A86:04 |
SubIndex 004 |
4th PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x06 (Input Calc And Copy Time)) |
UINT32 |
RW |
0xF10F:04, 16 |
1A86:05 |
SubIndex 005 |
5th PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x07 (Output Delay Time)) |
UINT32 |
RW |
0xF10F:07, 16 |
Index 1A87 DPM TxPDO-Map DC Cyclic Statistics
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A87:0 |
DPM TxPDO-Map DC Cyclic Statistics |
PDO Mapping TxPDO 136 contains the DP master cycle statistics (object 0xF10F) for the DC mode |
UINT8 |
RW |
0x06 (6dec) |
1A87:01 |
SubIndex 001 |
UINT32 |
RW |
0xF10F:03, 16 |
1A87:02 |
SubIndex 002 |
UINT32 |
RW |
0xF10F:04, 16 |
1A87:03 |
SubIndex 003 |
UINT32 |
RW |
0xF10F:05, 16 |
1A87:04 |
SubIndex 004 |
UINT32 |
RW |
0xF10F:04, 16 |
1A87:05 |
SubIndex 005 |
UINT32 |
RW |
0xF10F:07, 32 |
1A87:06 |
SubIndex 006 |
6th PDO Mapping entry (object 0xF10F (Cycle Statistic data), entry 0x08 (SM/SYNC Event Distance Time)) |
UINT32 |
RW |
0xF10F:08, 32 |
Index 1A88 DPM TxPDO-Map Redundancy Status
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A88:0 |
DPM TxPDO-Map Redundancy Status |
PDO Mapping TxPDO 137 |
UINT8 |
RO |
0x05 (5dec) |
1A88:01 |
SubIndex 001 |
1st PDO Mapping entry (object 0xF118, entry 0x01) |
UINT32 |
RO |
0xF118:01, 1 |
1A88:02 |
SubIndex 002 |
UINT32 |
RO |
0x0000:00, 15 |
1A88:03 |
SubIndex 003 |
3rd PDO Mapping entry (object 0xF118, entry 0x11) |
UINT32 |
RO |
0xF118:11, 16 |
1A88:04 |
SubIndex 004 |
4th PDO Mapping entry (object 0xF118, entry 0x12) |
UINT32 |
RO |
0xF118:12, 16 |
1A88:05 |
SubIndex 005 |
5th PDO Mapping entry (object 0xF118, entry 0x11) |
UINT32 |
RO |
0xF118:13, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs: the RxPDOs must be assigned in the order of their indexes. The RxPDOs of the configured DP slaves (0x1600-0x167E) must be assigned if object 0x1C12 is transmitted in the StartUp SDOs. |
UINT8 |
RW |
0x00 (0dec) |
1C12:01 |
1st allocated RxPDO (contains the index of the associated RxPDO mapping object) |
1C12:7E |
126th allocated RxPDO (contains the index of the associated RxPDO mapping object) |
Index 1C13 TxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs: the TxPDOs must be assigned in the order of their indexes. The TxPDOs of the configured DP slaves (0x1A00-0x1A7C) must be assigned if object 0x1C13 is transmitted in the StartUp SDOs. It can then still be decided via TxPDO Assign whether or not the TxPDOs PDO State (index 0x1A81), PDO Toggle (index 0x1A82), DP Diag (index 0x1A83), DP Status (index 0x1A84), DP Master Diag (index 0x1A85), Cycle Statistics (index 0x1A86) and DC Cycle Statistics (index 0x1A87) are transferred to the EtherCAT input data. |
UINT8 |
RW |
1C13:01 |
1st allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
1C13:86 |
134th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C32:0 |
SM output parameter |
Synchronization parameters for the outputs |
UINT8 |
RO |
0x20 (32dec) |
1C32:01 |
Sync mode |
Current synchronization mode:
UINT16 |
RW |
0x0001 (1dec) |
1C32:02 |
Cycle time |
Cycle time (in ns):
UINT32 |
RW |
0x000F4240 (1000000dec) |
1C32:03 |
Shift time |
DC mode only (as for 0x1C32:09) |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:04 |
Sync modes supported |
Supported synchronization modes:
UINT16 |
RO |
0x440B (17419dec) |
1C32:05 |
Minimum cycle time |
This entry contains the measured cycle time (in ns) of the DP cycle, including the update of the EtherCAT process data; the maximum measured value (sum of 0x1C32:06+0x1C33:09+0x1C33:06) is located here. If the CycleExceeded counter (0x1C32:0C or 0x1C33:0C) increments, then the cycle time set in 0x1C32:02 is too low for the configured DP bus structure. |
UINT32 |
RO |
0x0003CFB1 (249777dec) |
1C32:06 |
Calc and copy time |
This entry contains the measured time after the first event (SM2 (SM-synchronous or DC SYNC0-synchronous) or SYNC0 (DC SYNC1-synchronous)) until the start of the DP cycle (SM-synchronous) or after which the second event (SYNC0 (DC SYNC0-synchronous) or SYNC1 (DC SYNC1-synchronous)) may occur at the earliest. When setting DC SYNC0-synchronous, this time may also to be considered for the SYNC shift time for the EtherCAT master outputs. When setting DC SYNC1-synchronous, this time may also to be considered for the SYNC1 shift time of the EL6731. If the ShiftTooShort counter (0x1C32:0D) increments, then the corresponding shift time is set too low. |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:07 |
Minimum delay time |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:08 |
Command |
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. |
UINT16 |
RW |
0x0000 (0dec) |
1C32:09 |
Delay time |
This entry contains the time after the second event (SYNC0 event (DC SYNC0-synchronous) or SYNC1 event (DC SYNC1 synchronous)) and the time and output of the outputs (in ns, DC mode only) |
UINT32 |
RO |
0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C32:0B |
SM event missed counter |
This entry contains the number of missed SM events in OPERATIONAL (DC mode only). The counter is automatically reset at the transition from SAFEOP to OP. If it increments, then the SYNC shift time for outputs in the case of the EtherCAT master is too short. |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0C |
Cycle exceeded counter |
This entry contains the number of cycle time infringements during OPERATIONAL (cycle was not completed in time or the next cycle began too early). The counter is automatically reset at the transition from SAFEOP to OP. If it increments, then the cycle time of the EtherCAT master is too short. |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0D |
Shift too short counter |
This entry contains the number of times the distance between SM2 and SYNC 0 event (DC SYNC0) or between SYNC0 and SYNC1 event (DC SYNC1) was too short. The counter is automatically reset at the transition from SAFEOP to OP. If it increments, then the SYNC shift time for outputs in the case of the EtherCAT master (DC SYNC0) or the SYNC1 shift time in the case of the EL6731 (DC SYNC1) is too short. |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0F |
Minimum Cycle Distance |
0x00000000 (0dec) |
1C32:10 |
Maximum Cycle Distance |
0x00000000 (0dec) |
1C32:11 |
Minimum SM SYNC Distance |
0x00000000 (0dec) |
1C32:12 |
Maximum SM SYNC Distance |
0x00000000 (0dec) |
1C32:13 |
Application Cycle Exceeded Counter |
0x0000 (0dec) |
1C32:14 |
Frame repeat time |
0x00000000 (0dec) |
1C32:20 |
Sync error |
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) |
BOOLEAN |
RO |
0x00 (0dec) |
Index 1C33 SM input parameter
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C33:0 |
SM input parameter |
Synchronization parameters for the inputs |
UINT8 |
RO |
0x20 (32dec) |
1C33:01 |
Sync mode |
UINT16 |
RW |
0x0022 (34dec) |
1C33:02 |
Cycle time |
as 0x1C32:02 |
UINT32 |
RW |
1C33:03 |
Shift time |
Time between SYNC0 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RW |
0x00000000 (0dec) |
1C33:04 |
UINT16 |
RO |
0x440B (17419dec) |
1C33:05 |
as 0x1C32:05 |
UINT32 |
RO |
1C33:06 |
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:07 |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:08 |
Command |
as 0x1C32:08 |
UINT16 |
RW |
0x0000 (0dec) |
1C33:09 |
Maximum delay time |
Time between SYNC1 event and reading of the inputs (in ns, only DC mode) |
UINT32 |
RO |
0x00000000 (0dec) |
1C33:0B |
as 0x1C32:11 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0C |
as 0x1C32:12 |
UINT16 |
RO |
0x0000 (0dec) |
1C33:0D |
as 0x1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C32:0F |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:10 |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:11 |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:12 |
UINT32 |
RO |
0x00000000 (0dec) |
1C32:13 |
UINT16 |
RO |
0x0000 (0dec) |
1C32:14 |
Frame repeat time |
UINT32 |
RW |
0x00000000 (0dec) |
1C33:20 |
Sync error |
as 0x1C32:32 |
BOOLEAN |
RO |
0x00 (0dec) |