Overview of EL5102 functions
The EL5102 offers a wide range of functions. The following table provides an overview of the available functions. A detailed description can be found in the individual chapters.
To use the extended functions, the corresponding functions must be selected via the "Predefined PDO Assignment". The assignment is described in chapter "Process data".
Basic functions
Selecting the encoder type
Encoders or counters/pulse generators with signal levels according to RS422, TTL or OpenCollector can be selected.
Encoder operating voltage
The encoder supply can be set separately for each channel to either 5 VDC, 12 VDC or 24 VDC.
Evaluation of the counter value
The input signal can be subject to 4-fold, 2-fold or 1-fold evaluation.
Counter limits
The value range within which counting takes place can be defined.
Counter overflow / counter underflow
If the count limit is exceeded or underrun, this is indicated in separate process data.
Counting direction
The counting direction can be adapted to the application.
Reversion of counting direction
The counting direction and a reversion of the counting direction can be detected and output via the process data. This function can also be used for standstill monitoring.
Counter value reset
Allows a recurring reset of the counter value via zero pulse C or an edge (positive/negative) at the Latch extern input.
Set counter value
The counter value can be set at runtime to a predefined counter value via a PLC variable, zero pulse C or an edge (positive/negative) at the Latch extern input.
Save counter value
The current counter value can be saved, independent of the cycle time, in separate process data via an edge (positive/negative) at the Latch extern and Gate/Latch input or the zero pulse C.
You can parameterize whether the function is executed at each external edge or only once after each activation.
By using both latch inputs a workpiece measurement can also be realized.
Lock counter value
The counter value can be disabled via an edge (positive/negative) at the Gate input or a PLC variable.
Extended functions
Frequency measurement
The average frequency of the input signal within a given timeframe can be output directly.
Period value measurement
The period value of the last period within the PLC cycle can be output directly.
Velocity, speed calculation
The average velocity or speed of the input signal within a specified timeframe can be output directly.
Duty cycle measurement
The ratio of pulse duration tON to period value T in the last PLC cycle can be output directly.
Timestamp
A timestamp based on the distributed clocks system (DC) can be output for the last counting pulse, the zero pulse and the Latch extern and Latch extern 2 inputs.
Micro-increments
Allows additional increments (256 steps) to be interpolated between the counted encoder increments, thus increasing the resolution of the counter value.
Adjustable interference pulse filters
To suppress interference, a filter can be set for each of the input signals.
Diagnostic data
Error messages are communicated to the EtherCAT Master / TwinCAT via "DiagMessages".
Process data
Operation modes
The scope of the process data can be selected via "Predefined PDO Assignment".
Synchronicity mode
In addition to the frame-triggered operation mode (SM mode), a mode based on synchronization via the distributed clocks is available.
Description of the inputs
zero pulse C
With incremental encoders, a full revolution is marked by a special marker of the zero pulse C. This can be used for resetting, setting and storing the counter value.
Latch extern
A latch input is provided for 24 VDC signals with a minimum pulse duration of tON > 1 µs. This can be used for resetting, setting and storing the counter value.
Gate/Latch
An external gate input is provided for 24 VDC signals with a minimum pulse duration of tON > 1 µs. This can be used for resetting, setting and storing the counter value.
Status Input
If the encoder has a fault signal output, this can be evaluated.