Reversion of rotation
To adapt the counting direction to the application, this logic can be inverted by setting the bit in index 0x80n0:0E "Reversion of rotation".
Reversion of rotation 1:Fig.155: Reversion of counting direction (Index 0x80n0:0E "Reversion of rotation") for an encoder
Setting the bit in index 0x80n0:0E "Reversion of rotation" also inverts the logic of the counting direction. An overview of the resulting counting direction is shown in the following table.
The current level at input B is displayed via process data 0x60n0:0A "Status of input B".
Reversion of rotation 2:Fig.156: Reversion of counting direction (Index 0x80n0:0E "Reversion of rotation") for a counter/pulse generator
0x80n1:1D
"Counter mode”
Level at input track B
0x80n0:0E
"Reversion of rotation”
Resulting
counting direction
1: Counter RS422
(diff. input)
Input open / LOW level
FALSE
positive
TRUE
negative
RS422 signal level
FALSE
negative
TRUE
positive
3: Counter TTL
(Single-Ended)
Input open / LOW level, voltage level < 0.8 V
FALSE
positive
TRUE
negative
TTL voltage level
2.0 V to 6.0 V,
with min. 2.1 mA current
FALSE
negative
TRUE
positive
5: Counter open collector
FALSE
positive
TRUE
negative
Open collector voltage level
2.0 V to 6.0 V,
FALSE
negative
TRUE
positive
Reversion of rotation 3:
Status LED input B as counter RS422 (diff. input)
If the input of track B is open in counter mode "RS422 (diff. Input)", a broken wire is detected and the status LED of input B lights up red. The error detection and indication via the LED can be deactivated via index 0x80n0:0C "Error detection B".