Standard objects
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave:
  • The low word contains the CoE profile used (5001).
  • The high word contains the module profile according to the modular device profile.
UINT32
RO
0x00001389 (5001dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EL5101-0011
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x13ED3052 (334311506dec)
1018:03
Revision
Revision number of the EtherCAT slave:
  • The low word (bit 0–15) identifies the special terminal number.
  • The high word (bit 16–31) refers to the device description.
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave:
  • Low word
    • The low byte (bit 0–7) of the low word contains the year of production.
    • The high byte (bit 8–15) of the low word contains the week of production.
  • The high word (bit 16–31) is 0.
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1600 ENC RxPDO-Map Control
Index (hex)
Meaning
Data type
Flags
Default
1600:0
PDO Mapping RxPDO 1
UINT8
RO
0x04 (4dec)
1600:01
SubIndex 001
1. PDO Mapping entry (2 bits align)
UINT32
RO
0x0000:00, 2
1600:02
SubIndex 002
2. PDO Mapping entry (object 0x7000 (ENC Outputs), entry 0x03 (Set counter))
UINT32
RO
0x7000:03, 1
1600:03
SubIndex 003
3. PDO Mapping entry (13 bits align)
UINT32
RO
0x0000:00, 13
1600:04
SubIndex 004
4. PDO Mapping entry (object 0x7000 (ENC Outputs), entry 0x11 (Set counter value))
UINT32
RO
0x7000:11, 32
Index 1810 ENC TxPDO-Par TxPdo 1 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1810:0
PDO Parameter TxPDO 17
UINT8
RO
0x06 (6dec)
1810:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must be transferred together with TxPDO 17.
OCTET-STRING[28]
RO
11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1811 ENC TxPDO-Par TxPdo 2 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1811:0
PDO Parameter TxPDO 18
UINT8
RO
0x06 (6dec)
1811:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 18.
OCTET-STRING[28]
RO
10 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1812 ENC TxPDO-Par TxPdo 4 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1812:0
PDO Parameter TxPDO 19
UINT8
RO
0x06 (6dec)
1812:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 19.
OCTET-STRING[28]
RO
10 1A 11 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1813 ENC TxPDO-Par TxPdo 5 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1813:0
PDO Parameter TxPDO 20
UINT8
RO
0x06 (6dec)
1813:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 20.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1814 ENC TxPDO-Par TxPdo 8 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1814:0
PDO Parameter TxPDO 21
UINT8
RO
0x06 (6dec)
1814:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 21.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1815 ENC TxPDO-Par TxPdo 10 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1815:0
PDO Parameter TxPDO 22
UINT8
RO
0x06 (6dec)
1815:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 22.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1816 ENC TxPDO-Par TxPdo 16 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1816:0
PDO Parameter TxPDO 23
UINT8
RO
0x06 (6dec)
1816:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 23.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1817 ENC TxPDO-Par TxPdo 20 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1817:0
PDO Parameter TxPDO 24
UINT8
RO
0x06 (6dec)
1817:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 24.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1818 ENC TxPDO-Par TxPdo 25 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1818:0
PDO Parameter TxPDO 25
UINT8
RO
0x06 (6dec)
1818:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 25.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 1819 ENC TxPDO-Par TxPdo 32 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1819:0
PDO Parameter TxPDO 26
UINT8
RO
0x06 (6dec)
1819:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 26.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 1A 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 181A ENC TxPDO-Par TxPdo 40 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
181A:0
PDO Parameter TxPDO 27
UINT8
RO
0x06 (6dec)
181A:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 27.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1B 1A 1C 1A 1D 1A 1E 1A
Index 181B ENC TxPDO-Par TxPdo 50 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
181B:0
PDO Parameter TxPDO 28
UINT8
RO
0x06 (6dec)
181B:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 28.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1C 1A 1D 1A 1E 1A
Index 181C ENC TxPDO-Par TxPdo 64 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
181C:0
PDO Parameter TxPDO 29
UINT8
RO
0x06 (6dec)
181C:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 29.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1D 1A 1E 1A
Index 181D ENC TxPDO-Par TxPdo 80 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
181D:0
PDO Parameter TxPDO 30
UINT8
RO
0x06 (6dec)
181D:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 30.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1E 1A
Index 181E ENC TxPDO-Par TxPdo 100 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
181E:0
PDO Parameter TxPDO 31
UINT8
RO
0x06 (6dec)
181E:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 31.
OCTET-STRING[28]
RO
10 1A 11 1A 12 1A 13 1A 14 1A 15 1A 16 1A 17 1A 18 1A 19 1A 1A 1A 1B 1A 1C 1A 1D 1A
Index 1A00 ENC TxPDO-Map Status
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
PDO Mapping TxPDO 1
UINT8
RO
0x0C (12dec)
1A00:01
SubIndex 001
UINT32
RO
0x0000:00, 2
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x03 (Set counter done))
UINT32
RO
0x6000:03, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (3 bits align)
UINT32
RO
0x0000:00, 3
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x07 (Open circuit))
UINT32
RO
0x6000:07, 1
1A00:05
SubIndex 005
5. PDO Mapping entry (1 bit align)
UINT32
RO
0x0000:00, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x09 (Status of input A))
UINT32
RO
0x6000:09, 1
1A00:07
SubIndex 007
7. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x0A (Status of input B))
UINT32
RO
0x6000:0A, 1
1A00:08
SubIndex 008
8. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x0B (Status of input C))
UINT32
RO
0x6000:0B, 1
1A00:09
SubIndex 009
9. PDO Mapping entry (2 bits align)
UINT32
RO
0x0000:00, 2
1A00:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x0E (Sync error))
UINT32
RO
0x6000:0E, 1
1A00:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x0F (TxPDO State))
UINT32
RO
0x6000:0F, 1
1A00:0C
SubIndex 012
12. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x10 (TxPDO Toggle))
UINT32
RO
0x6000:10, 1
Index 1A01 ENC TxPDO-Map NextSync1Time
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping TxPDO 2
UINT8
RO
0x01 (1dec)
1A01:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x19 (StartTimeNextLatch))
UINT32
RO
0x6000:19, 64
Index 1A10 ENC TxPDO-Map TxPdo 1 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A10:0
PDO Mapping TxPDO 17
UINT8
RO
0x01 (1dec)
1A10:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A11 ENC TxPDO-Map TxPdo 2 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A11:0
PDO Mapping TxPDO 18
UINT8
RO
0x02 (2dec)
1A11:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A11:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A12 ENC TxPDO-Map TxPdo 4 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A12:0
PDO Mapping TxPDO 19
UINT8
RO
0x04 (4dec)
1A12:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A12:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A13 ENC TxPDO-Map TxPdo 5 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A13:0
PDO Mapping TxPDO 20
UINT8
RO
0x05 (5dec)
1A13:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A13:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A14 ENC TxPDO-Map TxPdo 8 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A14:0
PDO Mapping TxPDO 21
UINT8
RO
0x08 (8dec)
1A14:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A14:08
SubIndex 008
8. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A15 ENC TxPDO-Map TxPdo 10 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A15:0
PDO Mapping TxPDO 22
UINT8
RO
0x0A (10dec)
1A15:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A15:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A16 ENC TxPDO-Map TxPdo 16 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A16:0
PDO Mapping TxPDO 23
UINT8
RO
0x10 (16dec)
1A16:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A16:10
SubIndex 016
16. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A17 ENC TxPDO-Map TxPdo 20 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A17:0
PDO Mapping TxPDO 24
UINT8
RO
0x14 (20dec)
1A17:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A17:14
SubIndex 020
20. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A18 ENC TxPDO-Map TxPdo 25 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A18:0
PDO Mapping TxPDO 25
UINT8
RO
0x19 (25dec)
1A18:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A18:19
SubIndex 025
25. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A19 ENC TxPDO-Map TxPdo 32 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A19:0
PDO Mapping TxPDO 26
UINT8
RO
0x20 (32dec)
1A19:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A19:20
SubIndex 032
32. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A1A ENC TxPDO-Map TxPdo 40 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A1A:0
PDO Mapping TxPDO 27
UINT8
RO
0x28 (40dec)
1A1A:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A1A:28
SubIndex 040
40. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A1B ENC TxPDO-Map TxPdo 50 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A1B:0
PDO Mapping TxPDO 28
UINT8
RO
0x32 (50dec)
1A1B:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A1B:32
SubIndex 050
50. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A1C ENC TxPDO-Map TxPdo 64 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A1C:0
PDO Mapping TxPDO 29
UINT8
RO
0x40 (64dec)
1A1C:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A1C:40
SubIndex 064
64. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A1D ENC TxPDO-Map TxPdo 80 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A1D:0
PDO Mapping TxPDO 30
UINT8
RO
0x50 (80dec)
1A1D:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A1D:50
SubIndex 080
80. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1A1E ENC TxPDO-Map TxPdo 100 Samples Counter value
Index (hex)
Meaning
Data type
Flags
Default
1A1E:0
PDO Mapping TxPDO 31
UINT8
RO
0x64 (100dec)
1A1E:01
SubIndex 001
UINT32
RO
0x6000:11, 32
1A1E:64
SubIndex 100
100. PDO Mapping entry (object 0x6000 (ENC Inputs), entry 0x11 (Counter value))
UINT32
RO
0x6000:11, 32
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the sync managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x01 (1dec)
1C12:01
SubIndex 001
1st allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1600 (5632dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x03 (3dec)
1C13:01
SubIndex 001
1st allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A00 (6656dec)
1C13:02
SubIndex 002
2nd allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A01 (6657dec)
1C13:03
SubIndex 003
3rd allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A10 (6672dec)
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameters for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 2 Event
  • 2: DC-Mode - Synchron with SYNC0 Event
  • 3: DC-Mode - Synchron with SYNC1 Event
UINT16
RW
0x0001 (1dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchronous with SM 2 event: Master cycle time
  • DC-Mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x00000000 (0dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: free run is supported
  • Bit 1 = 1: Synchronous with SM 2 event is supported
  • Bit 2–3 = 01: DC mode is supported
  • Bit 4–5 = 10: Output shift with SYNC1 event (DC mode only)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08)
UINT16
RO
0xC007 (49159dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
0x00000000 (0dec)
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C32:08
Command
With this entry the real required process data provision time can be measured.
  • 0: Measurement of the local cycle time is stopped
  • 1: Measurement of the local cycle time is started
The entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, and 0x1C33:09 are updated with the maximum measured values.
For a subsequent measurement the measured values are reset.
UINT16
RW
0x0000 (0dec)
1C32:09
Maximum delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only).
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: Free Run
  • 1: Synchronous with SM 3 event (no outputs available)
  • 2: DC – Synchronous with SYNC0 event
  • 3: DC – Synchronous with SYNC1 event
  • 34: Synchronous with SM 2 event (outputs available)
UINT16
RW
0x0000 (0dec)
1C33:02
Cycle time
as 0x1C32:02
UINT32
RW
0x00000000 (0dec)
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, DC Mode only)
UINT32
RO
0x00000000 (0dec)
1C33:04
  • Bit 0: Free Run is supported
  • Bit 1: Synchronization with SM 2 event is supported (outputs available)
  • Bit 1: Synchronization with SM 3 event is supported (no outputs available)
  • Bit 4–5 = 01: Input shift through local event (outputs available)
  • Bit 4–5 = 10: Input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08 or 0x1C33:08)
UINT16
RO
0x0000 (0dec)
1C33:05
Minimum cycle time
as 0x1C32:05
UINT32
RO
0x00000000 (0dec)
1C33:06
Calc and copy time
Time between reading of the inputs and the inputs being available for the master (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:07
Min. delay time
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
as 0x1C32:08
UINT16
RW
0x0000 (0dec)
1C33:09
Max. delay time
Time between SYNC1 event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:0B
as 0x1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
as 0x1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
as 0x1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 0x1C32:32
BOOLEAN
RO
0x00 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index spacing of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
0x0001 (1dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default
F010:0
Module list
Maximum subindex
UINT8
RW
0x01 (1dec)
F010:01
SubIndex 001
Profile 510
UINT32
RW
0x000001FF (511dec)
Index F082 MDP Profile Compatibility
Index (hex)
Meaning
Data type
Flags
Default
F082:0
 Maximum subindex
UINT8
RO
0x01 (1dec)
F082:01
Compatible input cycle counter
BOOLEAN
RW
0x00 (0dec)