RTD measurement
In RTD measurement range, the measured resistance is internally converted to a temperature based on a set transformation. Since the channel internally measures based on 5 kΩ, the corresponding measurement error should be applied in this measuring range.
In some ranges a (relatively) higher measuring accuracy is achieved, which is why in the table below better temperature accuracy values may be specified for individual sensor types than can be calculated from the 5 kΩ accuracy1).
Please refer to the note on 2/3/4-wire measurement in the preceding chapter "Resistance".
Measurement mode
RTD
Operation mode
2.5 V feed voltage, fixed setting n +Uv
5 kΩ reference resistance at –I2
Supply current is given by:
2.5 V / (5 kΩ + Rmeasurement) → max. 0.5 mA
PDO resolution
0.01°C/digit
The transition resistance values of the terminal contacts affect the measurement. The measuring error can be reduced further through compensation by the user, with active signal connection.
The temperature end value corresponds to the nominal full scale value.
RTD measuring range
RTD measurement 1:Fig.42: Chart: RTD measuring range
RTD measurement 2:
Data of the sensor types in the following table
The data of the sensor types in the following table is provided for information only and serve as help for orientation. All details of data are without warranty and have to be verified with the data sheet of the respective used sensor.
CoE Enum
RTD
Element
RTD Type
Temperature
Starting value [°C]
Temperature
End value [°C]
Achievable accuracy @ sensor temperature (full scale value). 3-wire connection(2
Achievable accuracy @ sensor temperature (full scale value). 4-wire connection(2
Temperature coefficient (terminal-specific drift)
Measured value starting value [Ω]
Measured value end value [Ω]
0
None
1
PT100
-200
850
±1K (-200…+850°C)
see 1)
±0.5K (-200…+850°C)
see 1)
approx. 0.13 K/K
18.52
390.48
2
NI100
-60
250
approx. ±2.68K @ 0°C
approx. ±0.83K @ 0°C
approx. 0.083 K/K
69.52
289.2
3
PT1000
-200
850
approx. ±0.38K @ 0°C
approx. ±0.13K @ 0°C
approx. 0.013 K/K
185.2
3904.8
4
PT500
-200
850
approx. ±1.03K @ 0°C
approx. ±0.34K @ 0°C
approx. 0.034 K/K
92.6
1952.4
5
PT200
-200
850
approx. ±1.96K @ 0°C
approx. ±0.65K @ 0°C
approx. 0.065 K/K
37.04
780.96
6
NI1000
-60
250
approx. ±0.11K @ 0°C
approx. 0.011 K/K
695.2
2892.6
7
NI1000 (TK5000, 100°C: 1500 Ω)
-30
160
approx. ±0.27K @ 100°C
approx. ±0.089K @ 100°C
approx. 0.009 K/K
871.7
1863.6
8
NI120
-60
320
80.94
461.04
9
KT100/110/130/210/230 KTY10/11/13/16/19
-50
150
approx. ±0.109K @ 0°C
approx. ±0.036K @ 0°C
approx. 0.0036 K/K
1036
4470
10
KTY81/82-110.120.150
-50
150
approx. ±0.216K @ 0°C
approx. ±0.072K @ 0°C
approx. 0.0072 K/K
515
2211
11
KTY81-121
-50
150
approx. ±0.219K @ 0°C
approx. ±0.073K @ 0°C
approx. 0.0073 K/K
510
2189
12
KTY81-122
-50
150
approx. ±0.214K @ 0°C
approx. ±0.071K @ 0°C
approx. 0.0071 K/K
520
2233
13
KTY81-151
-50
150
approx. ±0.222K @ 0°C
approx. ±0.074K @ 0°C
approx. 0.0074 K/K
502
2156
14
KTY81-152
-50
150
approx. ±0.211K @ 0°C
approx. ±0.070K @ 0°C
approx. 0.0070 K/K
528
2266
15
KTY81/82-210.220.250
-50
150
approx. ±0.108K @ 0°C
approx. 0.0036 K/K
1030
4280
16
KTY81-221
-50
150
1019
4237
17
KTY81-222
-50
150
approx. ±0.107K @ 0°C
approx. 0.0036 K/K
1040
4323
18
KTY81-251
-50
150
approx. ±0.111K @ 0°C
approx. ±0.037K @ 0°C
approx. 0.0037 K/K
1004
4173
19
KTY81-252
-50
150
approx. ±0.105K @ 0°C
approx. ±0.035K @ 0°C
approx. 0.0035 K/K
1055
4387
20
KTY83-110.120.150
-50
175
approx. 0.0074 K/K
525
2535
21
KTY83-121
-50
175
approx. ±0.224K @ 0°C
approx. ±0.075K @ 0°C
approx. 0.0075 K/K
519
2509
22
KTY83-122
-50
175
approx. ±0.221K @ 0°C
approx. 0.0074 K/K
530
2560
23
KTY83-151
-50
175
approx. ±0.225K @ 0°C
approx. 0.0075 K/K
512
2471
24
KTY83-152
-50
175
approx. 0.0072 K/K
538
2598
25
KTY84-130.150
-40
300
approx. ±0.384K @ 0°C
approx. ±0.128K @ 0°C
approx. 0.013 K/K
359
2624
26
KTY84-151
-40
300
approx. ±0.396K @ 0°C
approx. ±0.132K @ 0°C
approx. 0.013 K/K
350
2558
27
KTY21/23-6
-50
150
approx. ±0.22K @ 0°C
approx. 0.0072 K/K
518
2235
28
KTY1x-5
-50
150
approx. ±0.110K @ 0°C
approx. 0.0037 K/K
1020
4403
29
KTY1x-7
-50
150
approx. 0.0036 K/K
1052
4537
30
KTY21/23-5
-50
150
approx. ±0.220K @ 0°C
approx. 0.0073 K/K
510
2202
31
KTY21/23-7
-50
150
approx. 0.0071 K/K
526
2268
1) Achievable at negligible offset part, e.g. through cross reference offset correction/ zero offset (ELM3xxx: zero offset function).
Higher measuring accuracy for individual sensor types whose resistance is in the smaller subrange of 0..5 kΩ.
2) Relative error according to the slope of the respective RTD characteristic diagram at 23°C ambient terminal temperature (not taking into account temperature drift of the sensor).
Notice
Extended Range mode not available
The Extended Range mode is not available for RTD measurement.
    • Until FW07: Object 0x8000:2E (Scaler) will be ignored by this setting. The “Legacy Range Mode” applies in the background.
    • From FW08: Object 0x8000:2E (Scaler) will then be set to the “Legacy Range Mode”. A change is not possible as long RTD measurement range is selected.