0x8000 PAI Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8000:0
PAI Settings Ch.1
UINT8
RO
0x34 (52dec)
0x41 (65dec) 2)
8000:01
Interface
Selection of the measurement configuration:
0 - None
1 - V ±30V
2 - V ±10V
3 - V ±5V
4 - V ±2.5V
5 - V ±1.25V
6 - V ±640mV
7 - V ±320mV
8 - V ±160mV
9 - V ±80mV
10 - V ±40mV
11 - V ±20mV
12 - V ±10mV
13 - V ±5mV
14 - V 0...10V
15 - V 0...5V
17 - I ±20mA
18 - I 0-20mA
19 - I 4-20mA
20 - I 4-20mA NAMUR
33 - RTD/R 2Wire
34 - RTD/R 3Wire
35 - RTD/R 4Wire
49 - SG 1/4 2Wire 350R
50 - SG 1/4 2Wire 120R
51 - SG 1/4 3Wire 350R
52 - SG 1/4 3Wire 120R
53 - SG 1/2 3Wire
54 - SG 1/2 5Wire
55 - SG 1/1 4Wire
56 - SG 1/1 6Wire
65 - Poti 3Wire
66 - Poti 5Wire
UINT16
RW
0x0000 (0dec)
8000:02
SG Voltage
Selection of the SG voltage:
0 - 0 V
1 - 0.5 V
2 - 1.0 V
3 - 1.5 V
4 - 2.0 V
5 - 2.5 V
6 - 3.0 V
7 - 3.5 V
8 - 4.0 V
9 - 4.5 V
10 - 5.0 V
UINT16
RW
0x0000 (0dec)
8000:04
Wire Break Detection
Broken wire detection
TRUE = on
FALSE = off
(see section “Broken wire detection/ optional connection diagnosis”)
BOOLEAN
RW
0x00 (FALSE)
8000:13
Wire Resistance Compensation 640 µΩ/ Step
Compensation of the wire resistance with resolution 640 µΩ/ step (only in 2-wire mode, "R/RTD 2-wire" possible)
UINT16
RW
0x0000 (0dec)
8000:14
RTD Element
Selection of the RTD element:
0 - None
1 - PT100 (-200...850°C)
2 - NI100 (-60...250°C)
3 - PT1000 (-200...850°C)
4 - PT500 (-200...850°C)
5 - PT200 (-200...850°C)
6 - NI1000 (-60...250°C)
7 - NI1000 TK5000 or rather 100°C: 1500Ohm (-30...160°C)
8 - NI120 (-60...320°C)
9 - KT100/110/130/210/230 KTY10/11/13/16/19 (-50...150°C)
10 - KTY81/82-110,120,150 (-50...150°C)
11 - KTY81-121 (-50...150°C)
12 - KTY81-122 (-50...150°C)
13 - KTY81-151 (-50...150°C)
14 - KTY81-152 (-50...150°C)
15 - KTY81/82-210,220,250 (-50...150°C)
16 - KTY81-221 (-50...150°C)
17 - KTY81-222 (-50...150°C)
18 - KTY81-251 (-50...150°C)
19 - KTY81-252 (-50...150°C)
20 - KTY83-110,120,150 (-50...175°C)
21 - KTY83-121 (-50...175°C)
22 - KTY83-122 (-50...175°C)
23 - KTY83-151 (-50...175°C)
24 - KTY83-152 (-50...175°C)
25 - KTY84-130,150 (-40...300°C)
26 - KTY84-151 (-40...300°C)
27 - KTY21/23-6 (-50...150°C)
28 - KTY1x-5 (-50...150°C)
29 - KTY1x-7 (-50...150°C)
30 - KTY21/23-5 (-50...150°C)
31 - KTY21/23-7 (-50...150°C)
UINT16
RW
0x0000 (0dec)
8000:16
Filter 1
Options for filter 1:
0 - None
1 - FIR Notch 50 Hz
2 - FIR Notch 60 Hz
3 - FIR LP 100 Hz
4 - FIR LP 1000 Hz
5 - FIR HP 150 Hz
6 - FIR HP 1500 Hz
16 - IIR Notch 50 Hz
17 - IIR Notch 60 Hz
18 - IIR Butterw. LP 5th Ord. 1 Hz
19 - IIR Butterw. LP 5th Ord. 25 Hz
20 - IIR Butterw. LP 5th Ord. 100 Hz
21 - IIR Butterw. LP 5th Ord. 250 Hz
22 - IIR Butterw. LP 5th Ord. 1000 Hz
32 - User defined FIR Filter
33 - User defined IIR Filter
34 - User defined Average Filter
UINT16
RW
0x0000 (0dec)
8000:17
Average Filter 1 No of Samples
Number of samples for user-defined Average Filter 1
UINT16
RW
0x0001 (1dec)
8000:18
Decimation Factor
Factor for individual sampling rate (min. 1)
UINT16
RW
0x0001 (1dec)
8000:19
Filter 2
Options for filter 2:
0 - None
1 - IIR 1
2 - IIR 2
3 - IIR 3
4 - IIR 4
5 - IIR 5
6 - IIR 6
7 - IIR 7
8 - IIR 8
16 - User defined FIR Filter
17 - User defined IIR Filter
18 - User defined Average Filter
UINT16
RW
0x0000 (0dec)
8000:1A
Average Filter 2 No of Samples
Number of samples for user-defined Average Filter 2
UINT16
RW
0x0001 (1dec)
8000:1B
True RMS No. of Samples
Number of samples for “True RMS“ calculation (min. 1, max. 1000);
also see chapter TrueRMS
UINT16
RW
0x00C2 (200dec)
8000:1C
Enable True RMS
Activation of "True RMS" calculation
BOOLEAN
RW
0x00 (FALSE)
8000:2B
Extended Functions
Options for future functions /settings
UINT16
RW
0x0000 (0dec)
8000:2C
Integrator/Differentiator
Options:
0 – Off
1 - Integrator 1x
2 - Integrator 2x 1)
3 - Differentiator 1x
4 - Differentiator 2x 1)
UINT16
RW
0x0000 (0dec)
8000:2D
Differentiator Samples Delta
Distance of samples for the differentiation
UINT16
RW
0x0001 (1dec)
8000:2E
Scaler
Scaling (enum):
0 - Extended Range
1 - Linear
2 - Lookup Table
3 - Legacy Range
4 - Lookup Table (additive)
UINT16
RW
0x0000 (0dec)
8000:30
Low Limiter
Smallest PDO output value
INT32
RW
0x80000000 (-2147483648dec)
8000:31
High Limiter
Largest PDO output value
INT32
RW
0x7FFFFFFF (2147483647dec)
8000:32
Low Range Error
Lowest limit at which the error bit and the error LED are set
INT32
RW
0xFF800000
(-8388608dec)
8000:33
High Range Error
Highest limit at which the error bit and the error LED are set
INT32
RW
0x007FFFFF
(8388607dec)
8000:34
Timestamp Correction
Value for correcting StartNextLatchTime (timestamp of the first sample)
INT32
RW
0xFFFB6C20
(-300000dec)
8000:40
Filter 1 Type Info
Filter 1 type information 2)
STRING
RW
N/A
8000:41
Filter 2 Type Info
Filter 2 type information 2)
STRING
RW
N/A
1) Functionality is only available from FW03
2) Functionality is only available from FW11, revision -0022