EL3443 – LED and connection
WARNING
Caution: Risk of injury through electric shock!
If you do not connect the terminal point N with the neutral conductor of your mains supply (e.g. when using for current measurement only), terminal point N should be grounded, in order to avoid dangerous overvoltages in the event of a current transformer fault!
WARNING
Please note that many vendors do not permit their current transformers to be operated in no-load mode! Connect the terminal to the secondary winding of the current transformers before using the current transformer!
EL3443 - LEDs and connection
EL3443 – LED and connection 1:Fig.6: EL3443 LEDs and connection
Terminal point
Comment
No.
L1
1
Phase L1
Connections for the voltage measurement
Note the Warnings above " Caution: Risk of electric shock! "
L2
2
Phase L2
L3
3
Phase L3
N
4
Neutral conductor N
(internally connected to terminal point 8)
IL1
5
Consumer at phase L1
Connections for the current transformers. Note the Warnings above " Caution: Risk of electric shock!"
IL2
6
Consumer at phase L2
IL3
7
Consumer at phase L3
N
8
Neutral conductor N
(internally connected to terminal point 4)
LED
Color
Meaning
RUN
green
This LED indicates the terminal's operating state:
off
State of the EtherCAT State Machine:
INIT = initialization of the terminal
flashing rapidly
BOOTSTRAP = function for terminal firmware updates
flashing
PREOP = function for mailbox communication and different default settings set
Single flash
SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state.
on
OP = normal operating state; mailbox and process data communication is possible
System OK
green
on
System OK,
(the "SystemOK"-LED is the representation of the "System State" bit, F600:01)
L1 - L3
OK
green
on
Voltage in the normal range
L1 EL3443 – LED and connection 2: L2 EL3443 – LED and connection 3: L3 EL3443 – LED and connection 4:
flashes
Voltage in the critical range
(warning threshold exceeded)
L1 EL3443 – LED and connection 5: L2 EL3443 – LED and connection 6: L3 EL3443 – LED and connection 7:
off
Voltage in prohibited range
(error threshold exceeded)
L1 EL3443 – LED and connection 8: L2 EL3443 – LED and connection 9: L3 EL3443 – LED and connection 10:
L1 - L3
Error
red
on