General technical data
Analog inputs | EL3314‑0020 |
Number of inputs | 4 |
Thermocouple sensor types, measured variables | Type B, C, E, J, K, L, N, R, S, T, U (default setting: type K), voltage measurement |
Connection technology | 2-wire |
Maximum cable length to the thermocouple | 30 m (without protective measures), suitable surge protection must be provided for longer cable lengths |
Resolution | internal 24 bit |
Sampling type | multiplex |
Ground reference | Differential |
Conversion time | approx. 1.6 s to 5 ms depending on configuration and filter setting; Preset: approx. 110 ms at 50/60 Hz |
Input filter cut-off frequency | typ. 1 kHz |
Software filter | 5 Hz...30 kHz, adjustable, notch characteristic; preset: disabled additional low-pass filter possible |
Wire break detection | yes (can be disabled) |
Supports NoCoeStorage function | yes |
Special features | High-precision, calibration certificate |
Voltage measurement | EL3314-0020 |
Measuring range, technically available | approx. ± 80 mV |
Measuring range, nominal | ± 78 mV |
Resolution | 10 nV per digit |
Measurement uncertainty |
Temperature measurement | EL3314-0020 |
Electrical measuring range used | ± 78 mV |
Measuring ranges | Type B: +200...+1820 °C Type C: 0...+2320 °C Type E: -270...+1000 °C Type J: -210...+1200 °C Type K: -270…+1372 °C (preset) Type L: -50...+900 °C Type N: -270...+1300 °C Type R: -50...+1768 °C Type S: -50...+1768 °C Type T: -270...+400 °C Type U: -50...+600 °C |
Resolution | Temperature display 0.1/0.01/0.001 °C per digit, preset 0.01 °C |
Supply and potentials | EL3314-0020 | |
Power supply for the electronics | via the E-bus | |
Current consumption via E-bus | typ. 200 mA | |
Differential voltage between +TC and -TC | Recommended area of application | respective measuring range |
Destruction limit, short-term/continuous | ±15 V | |
Max. potential of the twisted TC ends to one another (non-isolated/grounded TC) | Recommended area of application | ±2 V |
Max. potential UCM (CommonMode voltage) of the twisted TC to GND | Recommended area of application | Not applicable because GND is not accessible |
Destruction limit, short-term/continuous | ||
Max. potential of twisted TC or GND to SGND or 0 V power | Recommended area of application | ±30 V |
Destruction limit, short-term/continuous | ±50 V | |
Electrical isolation: max. potential of twisted TC or GND to bus side | Recommended area of application and short-term/continuous destruction limit | 500 V |
Communication | EL3314-0020 |
Configuration | via TwinCAT System Manager |
Width in the process image | max. 24 bytes input, |
Distributed Clocks | - |
Environmental conditions | EL3314-0020 |
Permissible temperature range during operation | 0 °C... + 55 °C |
Permissible temperature range during storage | -25 °C... + 85 °C |
Permissible relative air humidity | 95 %, no condensation |
General data | EL3314-0020 |
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) |
Weight | approx. 60 g |
on 35 mm mounting rail, conforms to EN 60715 | |
Installation position | To ensure enhanced measuring accuracy, the terminal must be installed in the prescribed standard position! See note! |
Standards and approvals | EL3314-0020 |
Protection rating | IP20 |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Identification / approval*) |
Ex markings
Standard | Marking |
ATEX | II 3 G Ex nA IIC T4 Gc |
IECEx | Ex nA IIC T4 Gc |
Terminal | Extended features | |||
Electrical isolation | TwinSAFE SC | high-precision | Calibration certificate | |
No | No | No | No | |
Yes | No | Yes | No | |
No | No | Yes | No | |
No | No | Yes | Factory working standard calibration certificate | |
No | No | Yes | External calibration certificate (ISO17025 or DAkkS certificate) | |
No | Yes | No | No | |
Yes | Yes | Yes | No |