General technical data
Analog inputs
EL3314‑0020
Number of inputs
4
Thermocouple sensor types, measured variables
Type B, C, E, J, K, L, N, R, S, T, U (default setting: type K), voltage measurement
Connection technology
2-wire
Maximum cable length to the thermocouple
30 m (without protective measures), suitable surge protection must be provided for longer cable lengths
Resolution
internal 24 bit
Sampling type
multiplex
Ground reference
Differential
Conversion time
approx. 1.6 s to 5 ms depending on configuration and filter setting;
Preset: approx. 110 ms at 50/60 Hz
Input filter cut-off frequency
typ. 1 kHz
Software filter
5 Hz...30 kHz, adjustable, notch characteristic; preset: disabled
additional low-pass filter possible
Wire break detection
yes (can be disabled)
Supports NoCoeStorage function
yes
Special features
High-precision, calibration certificate
Voltage measurement
EL3314-0020
Measuring range, technically available
approx. ± 80 mV
Measuring range, nominal
± 78 mV
Resolution
10 nV per digit
Measurement uncertainty
See Measurement ±78 mV
Temperature measurement
EL3314-0020
Electrical measuring range used
± 78 mV
Measuring ranges
Type B: +200...+1820 °C
Type C: 0...+2320 °C
Type E: -270...+1000 °C
Type J: -210...+1200 °C
Type K: -270…+1372 °C (preset)
Type L: -50...+900 °C
Type N: -270...+1300 °C
Type R: -50...+1768 °C
Type S: -50...+1768 °C
Type T: -270...+400 °C
Type U: -50...+600 °C
Resolution
Temperature display 0.1/0.01/0.001 °C per digit, preset 0.01 °C
See Thermocouples measurement
Supply and potentials
EL3314-0020
Power supply for the electronics
via the E-bus
Current consumption via E-bus
typ. 200 mA
Differential voltage between +TC and -TC
Recommended area of application
respective measuring range
Destruction limit, short-term/continuous
±15 V
Max. potential of the twisted TC ends to one another
(non-isolated/grounded TC)
±2 V
±15 V
Max. potential UCM (CommonMode voltage) of the twisted TC to GND
Not applicable because GND is not accessible
Max. potential of twisted TC or GND to SGND or 0 V power
±30 V
±50 V
Electrical isolation: max. potential of twisted TC or GND to bus side
Recommended area of application and short-term/continuous destruction limit
500 V
Communication
EL3314-0020
Configuration
via TwinCAT System Manager
Width in the process image
max. 24 bytes input,
max. 8 bytes output
Distributed Clocks
Environmental conditions
EL3314-0020
Permissible temperature range during operation
0 °C... + 55 °C
Permissible temperature range during storage
-25 °C... + 85 °C
Permissible relative air humidity
95 %, no condensation
General data
EL3314-0020
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Weight
approx. 60 g
Installation
on 35 mm mounting rail, conforms to EN 60715
Installation position
To ensure enhanced measuring accuracy, the terminal must be installed in the prescribed standard position! See note!
Standards and approvals
EL3314-0020
Protection rating
IP20
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Identification / approval*)
CE, UKCA, EAC
ATEX, IECEx, cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex nA IIC T4 Gc
IECEx
Ex nA IIC T4 Gc
Terminal
Extended features
TwinSAFE SC
high-precision
Calibration certificate
EL3314
No
No
No
No
EL3314-0002
Yes
No
Yes
No
EL3314-0010
No
No
Yes
No
EL3314-0020
No
No
Yes
Factory working standard calibration certificate
EL3314-0030
No
No
Yes
External calibration certificate (ISO17025 or DAkkS certificate)
EL3314-0090
No
Yes
No
No
EL3314-0092
Yes
Yes
Yes
No
