General technical data
Analog inputs
EL3312
Number of inputs
2
Thermocouple sensor types, measured variables
Types B, C, E, J, K, L, N, R, S, T, U (default setting type K), mV measurement
Connection technology
2-wire
Maximum cable length to the thermocouple
30 m (without protective measures), suitable surge protection must be provided for longer cable lengths
Resolution
internal 16 bit
Sampling type
multiplex
Ground reference
Differential
Conversion time
approx. 1.2 s to 7 ms,
depending on the configuration and filter setting, default: approx. 125 ms
Input filter cut-off frequency
typ. 1 kHz
Software filter
5 Hz...30 kHz, adjustable, notch characteristic; preset: disabled
Wire break detection
yes
Supports NoCoeStorage function
yes, from firmware 01
Voltage measurement
EL3312
Measuring range, technically available
approx. ± 78 mV
Measuring ranges (nominal) and resolution
± 30 mV (1 µV per digit, thus max. 32.768 mV can be displayed)
± 60 mV (2 µV per digit, thus max. 65.536 mV can be displayed)
± 75 mV (4 µV per digit, thus max. 131 mV can be displayed, observe technical measuring range)
The measuring ranges 30 and 60 mV are executed in software to increase the resolution and always use the same electrical measuring range of ± 75 mV.
Measurement uncertainty
See Measurement ±30 mV...±75 mV
Temperature measurement
EL3312
Electrical measuring range used
± 75 mV
Measuring ranges 1)
Type B: +200...+1820 °C
Type C: 0...+2320 °C
Type E: -270...+1000 °C
Type J: -210...+1200 °C
Type K: -270…+1372 °C (preset)
Type L: -50...+900 °C
Type N: -270...+1300 °C
Type R: -50...+1768 °C
Type S: -50...+1768 °C
Type T: -270...+400 °C
Type U: -50...+600 °C
Resolution
Temperature display 0.1/0.01 °C per digit, preset 0.1 °C
Note: internally, 16 bit are used for the calculation up to the FSV; depending on the set thermocouple, therefore, jumps in value >0.01 °C occur with "resolution 0.01 °C"; e.g. type K: approx. 0.04 °C.
See Thermocouples measurement
1) from FW07, Rev0024
Supply and potentials
EL3312
Power supply for the electronics
via the E-bus
Current consumption via E-bus
typ. 200 mA
Differential voltage between +TC and -TC
Recommended area of application
respective measuring range
Destruction limit, short-term/continuous
±15 V
Max. potential of the twisted TC ends to one another
(non-isolated/grounded TC)
±10 V within UCM limits (CommonMode voltage)
±15 V
Max. potential UCM (CommonMode voltage) of the twisted TC to GND
±5 V
±15 V
Max. potential of twisted TC or GND to SGND or 0 V power
±30 V
±50 V
Electrical isolation: max. potential of twisted TC or GND to bus side
Recommended area of application and short-term/continuous destruction limit
500 V
Communication
EL3312
Configuration
via TwinCAT System Manager
Width in the process image
max. 8 bytes input,
max. 4 bytes output
Distributed Clocks
Environmental conditions
EL3312
Permissible ambient temperature range during operation
-25 °C...+60 °C (extended temperature range), from firmware 06
Permissible ambient temperature range during storage
-40 °C…+85 °C
Permissible relative air humidity
95 %, no condensation
General data
EL3312
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Weight
approx. 60 g
Installation
on 35 mm mounting rail, conforms to EN 60715
Installation position
variable
Extended features
EL3312
Pluggable connection level
TwinSAFE SC
Calibration certificate
Standards and approvals
EL3312
Protection rating
IP20
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27, see also Installation instructions for enhanced mechanical load capacity
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Identification / approval*)
CE, UKCA, EAC, CCC
ATEX, IECEx, cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex ec IIC T4 Gc
IECEx
Ex ec IIC T4 Gc