Configuration data
Index 8000 RTD Settings Ch.1
Index (hex)  | Name  | Meaning  | Data type  | Flags  | Default  | |
8000:0  | RTD Settings Ch.1  | Maximum subindex  | UINT8  | RO  | 0x1B (27dec)  | |
8000:01  | Enable user scale  | User scaling is active.  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:02  | Presentation  | 0  | Signed presentation  | BIT3  | RW  | 0x00 (0dec)  |
1  | Absolute value with MSB as sign  | |||||
2  | High resolution (1/100°C)  | |||||
8000:05  | Siemens bits  | The S5 bits are displayed in the three low-order bits  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:06  | Enable filter  | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:07  | Enable limit 1  | The status bits are set in relation to Limit 1  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:08  | Enable limit 2  | The status bits are set in relation to Limit 2  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:09  | Enable automatic calibration  | not implemented  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:0A  | Enable user calibration  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:0B  | Enable vendor calibration  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  | |
8000:11  | User scale offset  | User scaling offset  | INT16  | RW  | 0x0000 (0dec)  | |
8000:12  | User scale gain  | This is the gain of the user scaling.  | INT32  | RW  | 0x00010000 (65536dec)  | |
8000:13  | Limit 1  | First limit value for setting the status bits (resolution 0.1 °C)  | INT16  | RW  | 0x0000 (0dec)  | |
8000:14  | Limit 2  | Second limit value for setting the status bits (resolution 0.1 °C)  | INT16  | RW  | 0x0000 (0dec)  | |
8000:15  | Filter settings  | This object determines the digital filter settings if it is active via Enable filter (Index 0x8000:06).  | UINT16  | RW  | 0x0000 (0dec)  | |
0  | 50 Hz  | |||||
1  | 60 Hz  | |||||
2  | 100 Hz  | |||||
3  | 500 Hz  | |||||
4  | 1 kHz  | |||||
5  | 2 kHz  | |||||
6  | 3.75 kHz  | |||||
7  | 7.5 kHz  | |||||
8  | 15 kHz  | |||||
9  | 30 kHz  | |||||
10  | 5 Hz  | |||||
11  | 10 Hz  | |||||
![]()  | The filter properties are set only via index 0x8000:15 The filter frequencies are set for all RTD channels of the EL3204-0162 terminals centrally via index 0x8000:15 (channel 1).  |
8000:16  | Calibration interval  | not implemented  | UINT16  | RW  | 0x0000 (0dec)  | |
8000:17  | User calibration offset  | User calibration offset  | INT16  | RW  | 0x0000 (0dec)  | |
8000:18  | User calibration gain  | User calibration gain  | UINT16  | RW  | 0xFFFF (65535dec)  | |
8000:19  | RTD element  | UINT16  | RW  | 0x0000 (0dec)  | ||
0  | Pt100  | |||||
1  | Ni100  | |||||
2  | Pt1000  | |||||
3  | Pt500  | |||||
4  | Pt200  | |||||
5  | Ni1000  | |||||
6  | Ni1000  | |||||
7  | Ni120  | |||||
8  | Output in ohm  | |||||
9  | Output in ohm  | |||||
10-32  | KT100/110/130/210/230 KTY10/11/13/16/19   | |||||
8000:1A  | Connection technology  | UINT16  | RW  | 0x0000 (0dec)  | ||
0  | Two-wire connection  | |||||
1  | 3-wire connection (without effect, not to be used)  | |||||
2  | 4-wire connection (without effect, not to be used)  | |||||
3  | not connected: sets the process data to 0 and switches off the LED  | |||||
8000:1B  | Calibration of the supply lines  | INT16  | RW  | 0x0000 (0dec)  | ||
Index 8010 RTD Settings Ch.2
8010:0  | RTD Settings Ch.2  | Maximum subindex  | UINT8  | RO  | 0x1B (27dec)  | |
8010:01  | Enable user scale  | User scaling is active.  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:02  | Presentation  | 0  | Signed presentation  | BIT3  | RW  | 0x00 (0dec)  |
2  | High resolution (1/100 C°)  | |||||
8010:05  | Siemens bits  | The S5 bits are displayed in the three low-order bits  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:06  | Enable filter  | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:07  | Enable limit 1  | The status bits are set in relation to Limit 1  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:08  | Enable limit 2  | The status bits are set in relation to Limit 2  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:09  | Enable automatic calibration  | not implemented  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:0A  | Enable user calibration  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8010:0B  | Enable vendor calibration  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  | |
8010:11  | User scale offset  | User scaling offset  | INT16  | RW  | 0x0000 (0dec)  | |
8010:12  | User scale gain  | This is the gain of the user scaling.  | INT32  | RW  | 0x00010000 (65536dec)  | |
8010:13  | Limit 1  | First limit value for setting the status bits (resolution 0.1°C)  | INT16  | RW  | 0x0000 (0dec)  | |
8010:14  | Limit 2  | Second limit value for setting the status bits (resolution 0.1°C)  | INT16  | RW  | 0x0000 (0dec)  | |
8010:15  | Filter settings  | (see note below)  | UINT16  | RW  | 0x0000 (0dec)  | |
8010:16  | Calibration interval  | not implemented  | UINT16  | RW  | 0x0000 (0dec)  | |
8010:17  | User calibration offset  | User calibration offset  | INT16  | RW  | 0x0000 (0dec)  | |
8010:18  | User calibration gain  | User calibration gain  | UINT16  | RW  | 0xFFFF (65535dec)  | |
8010:19  | RTD element  | UINT16  | RW  | 0x0000 (0dec)  | ||
0  | Pt100  | |||||
1  | Ni100  | |||||
2  | Pt1000  | |||||
3  | Pt500  | |||||
4  | Pt200  | |||||
5  | Ni1000  | |||||
6  | Ni1000  | |||||
7  | Ni120  | |||||
10 - 32  | KT100/110/130/210/230 KTY10/11/13/16/19   | |||||
8010:1A  | Connection technology  | UINT16  | RW  | 0x0000 (0dec)  | ||
8010:1B  | Calibration of the supply lines  | INT16  | RW  | 0x0000 (0dec)  | ||
Index 8020 AI Settings Ch. 3
8020:0  | AI Settings Ch. 3  | Maximum subindex  | UINT8  | RO  | 0x19 (25dec)  |
8020:01  | Enable user scale  | User scaling is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
8020:02  | Presentation  | 0: Signed presentation  | BIT3  | RW  | 0x00 (0dec)  |
8020:05  | Siemens bits  | The S5 bits are displayed in the three low-order bits  | BOOLEAN  | RW  | 0x00 (0dec)  |
8020:06  | Enable filter  | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary  | BOOLEAN  | RW  | 0x01 (1dec)  |
8020:07  | Enable limit 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
8020:08  | Enable limit 2  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
8020:0A  | Enable user calibration  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
8020:0B  | Enable vendor calibration  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
8020:0E  | Swap limit bits  | Reversal of the limit bits  | BOOLEAN  | RW  | 0x00 (1dec)  |
8020:11  | User scale offset  | User scaling offset  | INT16  | RW  | 0x0000 (0dec)  |
8020:12  | User scale gain  | Gain of the user scaling.  | INT32  | RW  | 0x00010000 (65536dec)  |
8020:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  |
8020:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  |
8020:15  | Filter settings  | This object determines the digital filter settings if it is active via Enable filter (Index 0x8020:06).  | UINT16  | RW  | 0x0000 (0dec)  |
![]()  | The filter characteristics are set via index 0x8020:15 The filter frequencies are set for all AI channels of the EL3204-0162 terminals centrally via index 0x8020:15 (channel 1).  |
8020:17  | User calibration offset  | User calibration offset  | INT16  | RW  | 0x0000 (0dec)  |
8020:18  | User calibration gain  | User calibration gain  | INT16  | RW  | 0x4000 (16384dec)  |
8020:19  | Range  | Setting the input range  | INT32  | RW  | 0x00000006 (6dec)  |
Index 8030 AI Settings Ch. 4
8030:0  | AI Settings Ch. 4  | Maximum subindex  | UINT8  | RO  | 0x19 (25dec)  |
8030:01  | Enable user scale  | User scaling is active.  | BOOLEAN  | RW  | 0x00 (0dec)  |
8030:02  | Presentation  | 0: Signed presentation  | BIT3  | RW  | 0x00 (0dec)  |
8030:05  | Siemens bits  | The S5 bits are displayed in the three low-order bits  | BOOLEAN  | RW  | 0x00 (0dec)  |
8030:06  | Enable filter  | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary  | BOOLEAN  | RW  | 0x01 (1dec)  |
8030:07  | Enable limit 1  | Limit 1 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
8030:08  | Enable limit 2  | Limit 2 enabled  | BOOLEAN  | RW  | 0x00 (0dec)  |
8030:0A  | Enable user calibration  | Enabling of the user calibration  | BOOLEAN  | RW  | 0x00 (0dec)  |
8030:0B  | Enable vendor calibration  | Enabling of the vendor calibration  | BOOLEAN  | RW  | 0x01 (1dec)  |
8030:0E  | Swap limit bits  | Reversal of the limit bits  | BOOLEAN  | RW  | 0x00 (1dec)  |
8030:11  | User scale offset  | User scaling offset  | INT16  | RW  | 0x0000 (0dec)  |
8030:12  | User scale gain  | Gain of the user scaling.  | INT32  | RW  | 0x00010000 (65536dec)  |
8030:13  | Limit 1  | First limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  |
8030:14  | Limit 2  | Second limit value for setting the status bits  | INT16  | RW  | 0x0000 (0dec)  |
8030:15  | Filter settings  | (see note below)  | UINT16  | RW  | 0x0000 (0dec)  |
8030:17  | User calibration offset  | User calibration offset  | INT16  | RW  | 0x0000 (0dec)  |
8030:18  | User calibration gain  | User calibration gain  | INT16  | RW  | 0x4000 (16384dec)  |
8030:19  | Range  | Setting the input range  | INT32  | RW  | 0x00000006 (6dec)  |