Configuration data
Index 8000 AI Settings
Index (hex)
Meaning
Data type
Flags
Default
8000:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
8000:01
Enable user scale
User scaling is active.
BOOLEAN
RW
0x00 (0dec)
8000:02
Presentation
0: Signed presentation
1: Unsigned presentation
2: Absolute value with MSB as sign
Signed amount representation
BIT3
RW
0x00 (0dec)
8000:05
Siemens bits
The S5 bits are displayed in the three low-order bits
BOOLEAN
RW
0x00 (0dec)
8000:06
Enable filter
Enable filter, which makes PLC‑cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x01 (1dec)
8000:07
Enable limit 1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
8000:08
Enable limit 2
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable user calibration
Enabling of the user calibration
BOOLEAN
RW
0x00 (0dec)
8000:0B
Enable vendor calibration
Enabling of the vendor calibration
BOOLEAN
RW
0x01 (1dec)
8000:0E*
Swap limit bits
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8000:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
8000:12
User scale gain
Gain of the user scaling.
The gain has a fixed-point representation with the factor 2-16.
The value 1 corresponds to 65535dec (0x00010000hex) and is limited to +/- 0x7FFFF.
INT32
RW
0x00010000 (65536dec)
8000:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:15
Filter settings
This object determines the digital filter settings if it is active via “Enable filter” (Index 0x8000:06).
The possible settings are numbered consecutively.
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
Refer to the Note on setting the filter characteristics
UINT16
RW
0x0000 (0dec)
8000:17
User calibration offset
INT16
RW
0x0000 (0dec)
8000:18
User calibration gain
INT16
RW
0x4000 (16384dec)
* Available from Firmware / Rev. see Table Availability
Filter
The filters of the EL30xx/EL31xx are activated or deactivated via the CoE index 0x8000:15.
Configuration data 1:
The filter characteristics are set via index 0x8000:15
The filter frequencies are set for all channels centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set.
