Defining and configuring an application object database of controlling station
Here you can unpack the complete PLC sources: TutorialSample.zip
Application objects = single points, double points, measured values, short floating point values, etc.
In this example the commands were configured such that the process data for the commands are located in the same memory area as the information data in monitoring direction, although in a different byte/bit offset. If required the commands may have the same byte/bit offset as the information in monitoring direction.
Example:
C_SC_NA_1 with IOA = 10 on the same byte/bit offset as M_SP_NA_1 with IOA = 100 (both byte offset = 100 and bit offset = 0). In this case a change in value of the single point in the substation (M_SP_NA_1 with object address 100) would trigger a data transfer with cause of transmission <3> (spontaneous) to the control station. In the control station the new value is copied to the bit/byte offset address of the command (C_SC_NA_1 with object address 10) and triggers a command transfer to the substation.
As an example we will configure the following application objects as part of the introductory project:
ASDU | Object address | Group | Base time | PLC | Byte | Bit | Process data width in the TwinCAT PLC |
M_SP_NA_1 | 100 | General interrogation group global | 0 | Memory | 100 | 0 | 1 bit |
M_SP_NA_1 | 101 | General interrogation group global | 0 | Memory | 100 | 1 | 1 Bit |
M_SP_TB_1 | 102 | General interrogation group global | 0 | Memory | 100 | 2 | 1 Bit |
M_DP_NA_1 | 200 | General interrogation group global | 0 | Memory | 200 | 0 | 2 Bits |
M_DP_NA_1 | 201 | General interrogation group global | 0 | Memory | 200 | 2 | 2 Bits |
M_DP_TB_1 | 202 | General interrogation group global | 0 | Memory | 200 | 4 | 2 Bits |
M_ST_NA_1 | 300 | General interrogation group global | 0 | Memory | 300 | 0 | 1 Byte |
M_ST_NA_1 | 301 | General interrogation group global | 0 | Memory | 301 | 0 | 1 Byte |
M_ST_TB_1 | 302 | General interrogation group global | 0 | Memory | 302 | 0 | 1 Byte |
M_BO_NA_1 | 400 | General interrogation group global | 0 | Memory | 400 | 0 | 4 Byte |
M_BO_NA_1 | 401 | General interrogation group global | 0 | Memory | 404 | 0 | 4 Byte |
M_BO_TB_1 | 402 | General interrogation group global | 0 | Memory | 408 | 0 | 4 Byte |
M_ME_NA_1 | 500 | General interrogation group global | 0 | Memory | 500 | 0 | 2 Byte |
M_ME_NA_1 | 501 | General interrogation group global | 0 | Memory | 502 | 0 | 2 Byte |
M_ME_TD_1 | 502 | General interrogation group global | 0 | Memory | 504 | 0 | 2 Byte |
M_ME_NB_1 | 600 | General interrogation group global | 0 | Memory | 600 | 0 | 2 Byte |
M_ME_NB_1 | 601 | General interrogation group global | 0 | Memory | 602 | 0 | 2 Byte |
M_ME_TE_1 | 602 | General interrogation group global | 0 | Memory | 604 | 0 | 2 Byte |
M_ME_NC_1 | 700 | General interrogation group global | 0 | Memory | 700 | 0 | 4 Byte |
M_ME_NC_1 | 701 | General interrogation group global | 0 | Memory | 704 | 0 | 4 Byte |
M_ME_TF_1 | 702 | General interrogation group global | 0 | Memory | 708 | 0 | 4 Byte |
M_IT_NA_1 | 800 | General counter interrogation | 0 | Memory | 800 | 0 | 4 Byte |
M_IT_NA_1 | 801 | General counter interrogation | 0 | Memory | 804 | 0 | 4 Byte |
M_IT_TB_1 | 802 | General counter interrogation | 0 | Memory | 808 | 0 | 4 Byte |
Commands |
C_SC_NA_1 | 10 | - | 0 | Memory | 2100 | 0 | 1 Bit |
C_SC_NA_1 | 11 | - | 0 | Memory | 2100 | 1 | 1 Bit |
C_SC_TA_1 | 12 | - | 0 | Memory | 2100 | 2 | 1 Bit |
C_DC_NA_1 | 20 | - | 0 | Memory | 2200 | 0 | 2 Bit |
C_DC_NA_1 | 21 | - | 0 | Memory | 2200 | 2 | 2 Bit |
C_DC_TA_1 | 22 | - | 0 | Memory | 2200 | 4 | 2 Bit |
C_BO_NA_1 | 40 | - | 0 | Memory | 2400 | 0 | 4 Byte |
C_BO_NA_1 | 41 | - | 0 | Memory | 2404 | 0 | 4 Byte |
C_BO_TA_1 | 42 | - | 0 | Memory | 2408 | 0 | 4 Byte |
C_SE_NA_1 | 50 | - | 0 | Memory | 2500 | 0 | 2 Byte |
C_SE_NA_1 | 51 | - | 0 | Memory | 2502 | 0 | 2 Byte |
C_SE_TA_1 | 52 | - | 0 | Memory | 2504 | 0 | 2 Byte |
C_SE_NB_1 | 60 | - | 0 | Memory | 2600 | 0 | 2 Byte |
C_SE_NB_1 | 61 | - | 0 | Memory | 2602 | 0 | 2 Byte |
C_SE_TB_1 | 62 | - | 0 | Memory | 2604 | 0 | 2 Byte |
C_SE_NC_1 | 70 | - | 0 | Memory | 2700 | 0 | 4 Byte |
C_SE_NC_1 | 71 | - | 0 | Memory | 2704 | 0 | 4 Byte |
C_SE_TC_1 | 72 | - | 0 | Memory | 2708 | 0 | 4 Byte |
Declaring a database variable
The application object database is an array variable of type ST_IEC870_5_101AODBEntry. Each array element corresponds to an application object.
The array elements are not manipulated directly but through specially provided functions and a database handle (table handle). The database handle must be initialized via a F_iecCreateTableHnd function call before it can be used. During this process the array elements are linked as a hash table. With a larger number of data points the hash table enables faster access to individual data points.
The maximum number of application objects is freely selectable and is only limited by the available memory. During PLC programming you have to specify a constant maximum number. The maximum number of application objects cannot be changed at runtime. In our example 50 application objects are declared. This number is sufficient for most applications. Please note that many application objects require adequate memory and runtime resources.
Define the following variable in MAIN:
PROGRAM MAIN
AODB : ARRAY[0..49] OF ST_IEC870_5_101AODBEntry;
hTable : T_HAODBTable;
Configuring application objects
The object type (M_SP_NA_1, M_DP_NA_1, M_ST_NA_1 etc.), the object address and further object parameters are specified during configuration of the individual application objects.
After initialization of the database handle is the application object database (database array) is empty and must be filled with the required data (data points). The data point configuration for the central station must match the data point configuration for the substation, i.e. in the central station data points of the same type and with the same common ASDU address and the same information object address must be configured as in the substation. Other parameters such as the mapping range and byte/bit offset can be configured as required.
The following functions are available for manipulating the application database:
Function | Description |
Initializes the hash table handle | |
Configures and adds a new hash table entry | |
Removes a hash table entry | |
Checks if a special hash table entry exists | |
Determines the linear position of a hash table entry |
The required application objects are configured during program runtime. The data base handle is transferred to the function via VAR_IN_OUT. Configuration is usually carried out once during PLC program start-up via an Init routine.
To configure the application objects during program start-up, add the following PLC code in MAIN:
PROGRAM MAIN
hTable: T_HAODBTable;
init : BOOL := TRUE;
initError : UDINT;
asduAddr : UDINT := 7;
IF init THEN
init := FALSE;
initError := F_iecCreateTableHnd( ADR( AODB ), SIZEOF( AODB ), hTable );
IF initError <> 0 THEN
ADSLOGSTR( ADSLOG_MSGTYPE_HINT OR ADSLOG_MSGTYPE_LOG,
'F_iecCreateTableHnd() error: %s',
DWORD_TO_HEXSTR( initError, 8, FALSE ) );
RETURN;
END_IF
(* Monitored Single Points *)
initError := F_iecAddTableEntry( M_SP_NA_1, asduAddr, 100, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 100, 0, 0, hTable );
initError := F_iecAddTableEntry( M_SP_NA_1, asduAddr, 101, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 100, 1, 0, hTable );
initError := F_iecAddTableEntry( M_SP_TB_1, asduAddr, 102, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 100, 2, 0, hTable );
(* Double Points*)
initError := F_iecAddTableEntry( M_DP_NA_1, asduAddr, 200, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 200, 0, 0, hTable );
initError := F_iecAddTableEntry( M_DP_NA_1, asduAddr, 201, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 200, 2, 0, hTable );
initError := F_iecAddTableEntry( M_DP_TB_1, asduAddr, 202, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 200, 4, 0, hTable );
(* Regulating step value *)
initError := F_iecAddTableEntry( M_ST_NA_1, asduAddr, 300, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 300, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ST_NA_1, asduAddr, 301, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 301, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ST_TB_1, asduAddr, 302, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 302, 0, 0, hTable );
(* 32 bit string *)
initError := F_iecAddTableEntry( M_BO_NA_1, asduAddr, 400, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 400, 0, 0, hTable );
initError := F_iecAddTableEntry( M_BO_NA_1, asduAddr, 401, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 404, 0, 0, hTable );
initError := F_iecAddTableEntry( M_BO_TB_1, asduAddr, 402, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 408, 0, 0, hTable );
(* Measured value, normalized value *)
initError := F_iecAddTableEntry( M_ME_NA_1, asduAddr, 500, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 500, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_NA_1, asduAddr, 501, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 502, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_TD_1, asduAddr, 502, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 504, 0, 0, hTable );
(* Mesured value, scaled value *)
initError := F_iecAddTableEntry( M_ME_NB_1, asduAddr, 600, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 600, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_NB_1, asduAddr, 601, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 602, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_TE_1, asduAddr, 602, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 604, 0, 0, hTable );
(* Measured value , short floating point value *)
initError := F_iecAddTableEntry( M_ME_NC_1, asduAddr, 700, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 700, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_NC_1, asduAddr, 701, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 704, 0, 0, hTable );
initError := F_iecAddTableEntry( M_ME_TF_1, asduAddr, 702, IEC870_GRP_INROGEN, 0, MAP_AREA_MEMORY, 708, 0, 0, hTable );
(* Integrated totals *)
initError := F_iecAddTableEntry( M_IT_NA_1, asduAddr, 800, IEC870_GRP_REQCOGEN, 0, MAP_AREA_MEMORY, 800, 0, 0, hTable );
initError := F_iecAddTableEntry( M_IT_NA_1, asduAddr, 801, IEC870_GRP_REQCOGEN, 0, MAP_AREA_MEMORY, 804, 0, 0, hTable );
initError := F_iecAddTableEntry( M_IT_TB_1, asduAddr, 802, IEC870_GRP_REQCOGEN, 0, MAP_AREA_MEMORY, 808, 0, 0, hTable );
(* Single commands *)
initError := F_iecAddTableEntry( C_SC_NA_1, asduAddr, 10, 0, 0, MAP_AREA_MEMORY, 2100, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SC_NA_1, asduAddr, 11, 0, 0, MAP_AREA_MEMORY, 2100, 1, 0, hTable );
initError := F_iecAddTableEntry( C_SC_TA_1, asduAddr, 12, 0, 0, MAP_AREA_MEMORY, 2100, 2, 0, hTable );
(* Double commands *)
initError := F_iecAddTableEntry( C_DC_NA_1, asduAddr, 20, 0, 0, MAP_AREA_MEMORY, 2200, 0, 0, hTable );
initError := F_iecAddTableEntry( C_DC_NA_1, asduAddr, 21, 0, 0, MAP_AREA_MEMORY, 2200, 2, 0, hTable );
initError := F_iecAddTableEntry( C_DC_TA_1, asduAddr, 22, 0, 0, MAP_AREA_MEMORY, 2200, 4, 0, hTable );
(* 32 bit string commands *)
initError := F_iecAddTableEntry( C_BO_NA_1, asduAddr, 40, 0, 0, MAP_AREA_MEMORY, 2400, 0, 0, hTable );
initError := F_iecAddTableEntry( C_BO_NA_1, asduAddr, 41, 0, 0, MAP_AREA_MEMORY, 2404, 0, 0, hTable );
initError := F_iecAddTableEntry( C_BO_TA_1, asduAddr, 42, 0, 0, MAP_AREA_MEMORY, 2408, 0, 0, hTable );
(* Set point, normalized values*)
initError := F_iecAddTableEntry( C_SE_NA_1, asduAddr, 50, 0, 0, MAP_AREA_MEMORY, 2500, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_NA_1, asduAddr, 51, 0, 0, MAP_AREA_MEMORY, 2502, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_TA_1, asduAddr, 52, 0, 0, MAP_AREA_MEMORY, 2504, 0, 0, hTable );
(* Set point, scaled valuess *)
initError := F_iecAddTableEntry( C_SE_NB_1, asduAddr, 60, 0, 0, MAP_AREA_MEMORY, 2600, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_NB_1, asduAddr, 61, 0, 0, MAP_AREA_MEMORY, 2602, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_TB_1, asduAddr, 62, 0, 0, MAP_AREA_MEMORY, 2604, 0, 0, hTable );
(* Set point, short floating point values *)
initError := F_iecAddTableEntry( C_SE_NC_1, asduAddr, 70, 0, 0, MAP_AREA_MEMORY, 2700, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_NC_1, asduAddr, 71, 0, 0, MAP_AREA_MEMORY, 2704, 0, 0, hTable );
initError := F_iecAddTableEntry( C_SE_TC_1, asduAddr, 72, 0, 0, MAP_AREA_MEMORY, 2708, 0, 0, hTable );