Mapping of PLC and IEC process data
Here you can unpack the complete PLC sources: TutorialSample.zip
The TwinCAT PLC process data are cyclically mapped (copied) into the IEC process data (application objects) and vice versa at program runtime. For mapping of the IEC<->PLC process data up to 4 process data areas (IO inputs, IO outputs, memory area, data area) can be declared as buffer variables in the PLC program. The byte size of the buffers is freely selectable and may be different for each area. Its not necessary to declare unused buffer areas.
In our introductory example we declare 4 PLC process data areas with 3000 bytes each:
PROGRAM MAIN
AODB : ARRAY[0..49] OF ST_IEC870_5_101AODBEntry;
init : BOOL := TRUE;
initError : UDINT;
inputs AT%IB0 : ARRAY[0..2999] OF BYTE;
outputs AT%QB0 : ARRAY[0..2999] OF BYTE;
memory AT%MB0 : ARRAY[0..2999] OF BYTE;
data : ARRAY[0..2999] OF BYTE;
How the process data are to be mapped at runtime is specified during configuration of the application objects via the F_iecInitAOEntry function.
See also in: Declaration and configuration of application objects.
Now the buffer variables are declared as byte arrays. To have better access to the desired data the variables are declared a second time and assigned to the corresponding byte/bit offset addresses.
Now a change within the byte array causes a change of the corresponding variable and vice versa. This is not imperative necessary. You can also have access directly to the bits/bytes of the byte array buffer variables.
VAR_GLOBAL
(* Memory offset 0..99 unused *)
(* Single points *)
msgSingle_0 AT%MX100.0 : BOOL;
msgSingle_1 AT%MX100.1 : BOOL;
msgSingle_2 AT%MX100.2 : BOOL;
(* Double points *)
(* Bit 0..1 = first double point,
Bit 2..3 = second double point,
Bit 4..5 = third double point,
Bit 6..7 = fourth double point *)
msgDouble_0 AT%MB200 : BYTE;
(* Regulating step values *)
msgStep_0 AT%MB300 : BYTE;
msgStep_1 AT%MB301 : BYTE;
msgStep_2 AT%MB302 : BYTE;
(* 32 bit strings *)
msgBitStr_0 AT%MD400 : DWORD := 2#10001000_10001000_10001000_10001000;
msgBitStr_1 AT%MD404 : DWORD := 2#10001000_10001000_10001000_10001000;
msgBitStr_2 AT%MD408 : DWORD := 2#10001000_10001000_10001000_10001000;
(* Measured values, normalized values *)
msgNormalized_0 AT%MW500 : WORD;
msgNormalized_1 AT%MW502 : WORD;
msgNormalized_2 AT%MW504 : WORD;
(* Mesured values, scaled values *)
msgScaled_0 AT%MW600 : INT;
msgScaled_1 AT%MW602 : INT;
msgScaled_2 AT%MW604 : INT;
(* Measured values, short floating point values *)
msgFloating_0 AT%MD700 : REAL;
msgFloating_1 AT%MD704 : REAL;
msgFloating_2 AT%MD708 : REAL;
(* Integrated totals *)
msgTotal_0 AT%MD800 : UDINT;
msgTotal_1 AT%MD804 : UDINT;
msgTotal_2 AT%MD808 : UDINT;
(* Single commands *)
cmdSingle_0 AT%MX2100.0 : BOOL;
cmdSingle_1 AT%MX2100.1 : BOOL;
cmdSingle_2 AT%MX2100.2 : BOOL;
(* Double commands *)
(* Bit 0..1 = first double command,
Bit 2..3 = second double command,
Bit 4..5 = third double command,
Bit 6..7 = fourth double command *)
cmdDouble_0 AT%MB2200 : BYTE;
(* Regulating step commands *)
cmdStep_0 AT%MB2300 : BYTE;
cmdStep_1 AT%MB2301 : BYTE;
cmdStep_2 AT%MB2302 : BYTE;
(* 32 bit string commands *)
cmdBitStr_0 AT%MD2400 : DWORD;
cmdBitStr_1 AT%MD2404 : DWORD;
cmdBitStr_2 AT%MD2408 : DWORD;
(* Set point, normalized values *)
cmdNormalized_0 AT%MW2500 : WORD;
cmdNormalized_1 AT%MW2502 : WORD;
cmdNormalized_2 AT%MW2504 : WORD;
(* Set point, scaled values *)
cmdScaled_0 AT%MW2600 : INT;
cmdScaled_1 AT%MW2602 : INT;
cmdScaled_2 AT%MW2604 : INT;
(* Set point, short floating point values *)
cmdFloating_0 AT%MD2700 : REAL;
cmdFloating_1 AT%MD2704 : REAL;
cmdFloating_2 AT%MD2708 : REAL;
Mapping of the IEC<->PLC process data in controlled station
Process data in monitoring direction (slave->master information)
Example 1
Single point information (M_SP_NA_1) with the IOA = 100, PLC memory area, byte offset = 100, bit offset = 0.
msgSingle_0 == memory[100].0 -> Controlled station FB -> ... -> Controlling station
Example 2
Measured value, short floating point value (M_ME_NC_1) with the IOA = 700, PLC memory area, byte offset = 700, bit offset = 0 (irrelevant).
msgFloating_0 == memory[700..703] -> Controlled station FB -> ... -> Controlling station
Process data in control direction (master->slave commands)
Example 1
Single command state (C_SC_NA_1) with the IOA = 10, PLC memory area, byte offset = 2100, bit offset = 0.
Controlling station -> ... -> Controlled station FB -> memory[2100].0 == cmdSingle_0
Example 2
Set point, short floating point value (C_SE_NC_1) with the IOA = 70, PLC memory area, byte offset = 2700, bit offset = 0 (irrelevant).
Controlling station -> ... -> Controlled station FB -> memory[2700..2703] == cmdFloating_0
