F_iecInitAOEntry
F_iecInitAOEntry 1:
F_iecInitAOEntry
The function F_iecInitAOEntry configures application objects (Single Points, Double Points, Measured Values...) as linear table entries. The table element (array element ) to be configured has to be given to the function as VAR_IN_OUT function parameter.
FUNCTION F_iecInitAOEntry: UDINT
    eType       : E_IEC870_5_101TcTypeID := ASDU_TYPEUNDEF;
    objAddr     : DWORD := 0;
    group       : DWORD := 0;
    multiplier  : BYTE := 0;
    ioMapType   : E_IEC870_5_101IOMappingType := MAP_AREA_NONE;
    byteOffs    : UDINT := 0;
    bitOffs     : UDINT := 0;
    dbEntry     : ST_IEC870_5_101AODBEntry;
eType: Type of application object, ASDU identifier (e.g..: M_SP_NA_1 for Single Point or M_DP_NA_1 for Double Point ).
objAddr : Object address, any address can be given.
group: Object group configuration flags. See: Description of all Group Flags. The flags can be combined with OR-Linking. Not all combinations are sensefull!
multiplier: Base cycle time multiplicator for cyclic/periodic data transfer.  0 = disabled. The base cycle time can be configured by the tPerCyclicBase- parameter in the  system parameters.
ioMapType: TwinCAT PLC process data range. This parameter defines how the TwinCAT PLC and IEC applicatation object process data are to be mapped.
byteOffs: TwinCAT PLC process data byte offset.
bitOffs: TwinCAT PLC process data bit offset.
dbEntry: Application object to be configured (array element).
Return value
No error.
<> 0
Error: IEC60870-5-10x error code
Example in ST:
Configuration of three datapoints as linear table entries.
eType
objAddr
group
multiplier
ioMapType
byteOffs
bitOffs
M_SP_NA_1
100
IEC870_GRP_INRO1
0
MAP_AREA_MEMORY
100
0
M_DP_NA_1
200
IEC870_GRP_INROGEN
0
MAP_AREA_DATA
200
0
M_IT_NA_1
800
IEC870_GRP_REQCOGEN
0
MAP_AREA_MEMORY
800
0
VAR_GLOBAL CONSTANT
    MIN_TABLE_IDX : INT := 0;
    MAX_TABLE_IDX : INT := 49;
PROGRAM P_LinearTableConfig
    AODB : ARRAY[MIN_TABLE_IDX..MAX_TABLE_IDX] OF ST_IEC870_5_101AODBEntry;
    init        : BOOL := TRUE;
    initError       : UDINT;
IF init THEN
    init := FALSE;
    initError := F_iecInitAOEntry(  eType       := M_SP_NA_1,
                    objAddr         := 100,
                    group       := IEC870_GRP_INRO1,
                    multiplier      := 0,
                    ioMapType       := MAP_AREA_MEMORY,
                    byteOffs    := 100,
                    bitOffs         := 0,
                    dbEntry         := AODB[0] );
    IF initError <> 0 THEN
        ADSLOGSTR( ADSLOG_MSGTYPE_ERROR OR ADSLOG_MSGTYPE_LOG,
            'F_iecInitAOEntry() error: %s',
            DWORD_TO_HEXSTR( initError, 8, FALSE ) );
        RETURN;
    END_IF
    initError := F_iecInitAOEntry(  eType       := M_DP_NA_1,
                    objAddr         := 200,
                    group       := IEC870_GRP_INROGEN,
                    multiplier      := 0,
                    ioMapType       := MAP_AREA_DATA,
                    byteOffs    := 200,
                    bitOffs         := 0,
                    dbEntry         := AODB[1] );
        RETURN;
    END_IF
    initError := F_iecInitAOEntry(  eType       := M_IT_NA_1,
                    objAddr         := 800,
                    group       := IEC870_GRP_REQCOGEN,
                    multiplier      := 0,
                    byteOffs    := 800,
                    bitOffs         := 0,
                    dbEntry         := AODB[2] );
        RETURN;
    END_IF
END_IF
Development Environment
Target System
PLC libraries to include
TwinCAT v2.9.0 Build >= 1030
PC or CX (x86)
TcIEC870_5_101.Lib
( Standard.Lib; TcBase.Lib; TcSystem.Lib; TcUtilities.Lib;  are included automatically )
TwinCAT v2.10.0 Build >= 1301
CX (ARM)