FB_MTP_MonBinDrv
FB_MTP_MonBinDrv 1:
The function block FB_MTP_MonBinDrv is an object for controlling a binary drive from different sources: internal PLC logic or manual operation (e.g. via OPC UA). Switching requests are managed via the state machine of Operation Mode. It also includes the option of monitoring the output values with the respective feedback signals. The OPC UA access rights are described in the variable tables.
Controlling the drive
The direction of rotation of the drive is specified via the switching requests Fwd*, Rev*, and Stop*. The state machine of the Operation Mode manages whether and from which source new switching requests are processed.
If both requests are made simultaneously, the safety position is taken into account: Stop* has the highest priority over SafePos = FALSE, and the drive is stopped. If SafePos = TRUE, the switching requests Fwd*, Rev*, and Stop* are prioritized equally and the drive remains in its current state in the event of simultaneous requests.
When Locking is active, it is no longer possible to control the drive, depending on the type of interlock.
The variable Trip indicates the current state of the motor protection. If Trip = FALSE is true, this means that the motor protection has been triggered and the drive is stopped immediately by setting the variables FwdCtrl and RevCtrl to FALSE.
If Trip = TRUE is true, the motor protection is in a fault-free state. Once the motor protection has been restored after triggering (Trip = TRUE), the state must be acknowledged via Reset before operation can resume.
Safety position
The safety position is defined via the variables SafePos, SafePosDirEn, and SafePosDir.
The variable SafePos is used to specify whether the safety position of the drive is the de-energized state or an active state.
FB_MTP_MonBinDrv 2:
The variables SafePosDirEn and SafePosDir are not part of the MTP guideline. They have also been implemented and can be used to define a safety position in the active state. These variables are not listed in the MTP file and are not made available via OPC UA.
Safety position: de-energized state
In the de-energized state, the safety position of the drive is: FwdCtrl = FALSE and RevCtrl = FALSE.
Safety position: active state
For the active state, the default direction of rotation can be enabled (SafePosDirEn = TRUE) and the direction of rotation can be specified (SafePosDir).
If the specification of the direction of rotation is disabled SafePosDirEn = FALSE, the current movement state (forward, reverse, or stop) is the safety position.
If the default setting is enabled, the safety position SafePosDirEn = TRUE is forward (SafePosDir = FALSE) or reverse (SafePosDir = TRUE).
Monitoring
The control and the respective Feedback can be monitored via Feedback monitoring.
General definitions
Name of the object
Object description
WQC
OSLevel
Locking
Reset
Inheritance hierarchy
FB_MTP_BinDrv
   FB_MTP_MonBinDrv
Implemented interfaces
I_MTP_MonBinDrv
FB_MTP_MonBinDrv 3: Inputs
Type
OPC UA access
TagName
STRING
Name of the interface
TagDescription
STRING
Description of the interface
WQC
BYTE
Worst Quality Code
Read
OSLevel
BYTE
Level must be defined for system. Value 0 is reserved for local operation.
Read/write
StateChannel
StateOffAut
StateOpAut
StateAutAut
See Operation Mode
FwdEn
Enable forward movement:
1: Enabled
0: Disabled
Read
RevEn
Enable reverse movement:
1: Enabled
0: Disabled
Read
StopAut
Automatic switching request to set the drive to stop:
(Relevant if StateAutAct)
1: Execute stop.
0: No stop
Read
FwdAut
Automatic switching request to set the drive in forward motion:
(Relevant if StateAutAct & FwdEn)
1: Execute forward movement.
0: Do not execute any forward movement.
Read
RevAut
(Relevant if StateAutAct & RevEn)
1: Execute reverse movement.
0: Do not execute any reverse movement.
Read
FwdFbk
Feedback signal for forward movement:
1: Forward movement
0: No forward movement
Read
FwdFbkCaIc
Source of the forward movement feedback signal:
1: Calculated
0: Sensor
Read
RevFbk
Feedback signal for reverse movement:
1: Reverse movement
0: No reverse movement
Read
RevFbkCaIc
Source of the feedback signal for reverse motion:
1: Calculated
0: Sensor
Read
PermEn
Permit
IntlEn
Interlock
ProtEn
Protect
See Locking
Trip
Signaling contact for motor protection:
1: No error
0: Motor protection tripped.
Read
SafePos
1: Retain current state.
0: Stop
Read
SafePosDirEn
1: Direction of rotation specification for SafePos = TRUE
via variable SafePosDir
0: No direction of rotation specified
SafePosDir
Direction of rotation specification for SafePos = TRUE and SafePosDirRpmEn = TRUE
1: Reverse
0: Forward
MonEn
Enable FeedbackMonitoring:
1: FeeedbackMonitoring active
0: FeedbackMonitoring inactive
Read/write
MonStatTi
REAL
Monitoring time for static errors [s]
Read
MonDynTi
REAL
Monitoring time for dynamic errors [s]
Read
MonSafePos
Behavior of the interface after an error occurs:
1: Safe position should be approached.
0: The current state is retained.
Read
ResetAut
Automatic reset switching request:
1: Reset requested.
0: No reset requested.
Read
FB_MTP_MonBinDrv 4:
It is possible to change the value of the input variable MonEn during runtime; however, according to the MTP guideline, this is not permitted because the value is changed via manual operation (e.g., via OPC UA).
FB_MTP_MonBinDrv 5: Outputs
Type
OPC UA access
StateOffAct
StateOpAct
StateAutAct
See Operation Mode
FwdCtrl
Forward movement:
1: Active
0: Inactive
Read
RevCtrl
Reverse movement:
1: Active
0: Inactive
Read
SafePosAct
Safety position enabled:
1: Safety position is active.
0: Safety position is not active.
Read
MonStatErr
REAL
Static error:
1: active
0: inactive
Read
MonDynErr
REAL
Dynamic error:
1: active
0: inactive
Read
External variables
Type
OPC UA access
StateOffOp
StateOpOp
StateAutOp
See Operation Mode
StopOp
Operator switching request to set the drive to stop:
(Relevant if StateOpAct)
1: Execute stop.
0: Do not execute a stop.
Read/write
FwdOp
Operator switching request to set the drive in forward motion:
(Relevant if StateOpAct & FwdEn)
Read/write
RevOp
(Relevant if StateOpAct & RevEn)
Read/write
ResetOp
Operator reset switching request:
0→1: Operator request
1→0: Request has been processed.
Read/write
FB_MTP_MonBinDrv 6: Methods
Type
IsOffline
IsOperator
IsAutomatic
SetOffline
SetOperator
SetAutomatic
See Operation Mode
Forward
The Forward method allows the drive to start moving forward. In this process, the OperationMode is transformed into the state SetAutomatic using the method Automatic. The Aut switching requests are set to defined values, and the internal logic is invoked. Finally, the *Aut switching requests are reset to FAlSE.
Returns TRUE if FwdFbk = TRUE and RevFbk = FALSE.
Reverse
The Reverse method allows the drive to start moving in reverse. In this process, the OperationMode is transformed into the state SetAutomatic using the method Automatic. The Aut switching requests are set to defined values, and the internal logic is invoked. Finally, the *Aut switching requests are reset to FALSE.
Returns TRUE if FwdFbk = FALSE and RevFbk = TRUE.
Stop
The Stop method allows you to stop the drive. In this process, the OperationMode is transformed into the state SetAutomatic using the method Automatic. The *Aut switching requests are set to defined values, and the internal logic is invoked. Finally, the *Aut switching requests are reset to False.
Returns TRUE if FwdFbk = FALSE and RevFbk = FALSE.