Functions
The following table shows a summary of the controller functions with references to chapters of VDE AR-N 4110/20/30 and EN 50549-2:
Description | Name | VDE 4110/20/30 | EN 50549-2 | FGW TR3 |
Setpoint specification of a max. active power | 10.2.4.1 / 10.2.4.2 / 11.2.7 | 4.11.2 | 6.1.3.6 | |
Frequency-dependent active power control P(f) | 10.2.4.3 / 11.2.8 | 4.6.1 / 4.6.2 | 6.1.4.5 | |
Provision of primary control power | 10.5.3 / 11.2.8.3 | N/A | 6.1.7 | |
Active power gradient after voltage loss | 11.3.2 | 4.10.2 | 6.1.11 | |
Voltage related active power reduction | - | 4.7.3 | - | |
Reactive power control with constant setpoint | 10.2.2 / 11.3.2 | 4.7.2.3.2 | 6.1.4.1 | |
Reactive power control with displacement factor CosPhi | 10.2.2.4 / 11.3.2 | 4.7.2.3.2 | 6.1.4.2 | |
Reactive power control with voltage limitation | Reactive power control with voltage limiting function Q(Ulim) | 10.2.2.4 / 11.3 | - | 6.1.4.3 |
Reactive power-voltage characteristic curve Q(U) | Reactive power control with voltage characteristic curve Q(U) | 10.2.2.4 / 11.3 | 4.7.2.3.3 | 6.1.4.4 |
Reactive power-active power characteristic curve Q(P) | Reactive power control with active power characteristic curve Q(P) | 10.2.2.4 / 11.3 | 4.7.2.3.4 | 6.1.4.5 |
Behavior in the event of communication errors | 10.2.2.4 / 11.3 | - | 6.1.8.2 | |
Behavior in the event of a power supply / UPS failure | 10.2.2.4 / 11.4.21 | - | 6.1.8.1 | |
Controller bypass (slave mode) | 11.3.2 | - | 6.1.9 | |
Automatic activation after protective tripping | 10.4 / 11.2.11 | 4.10.2 | 6.1.12 | |
Switching behavior during operation | - | - | 6.1.5 | |
Prioritization with multiple setpoint specifications | 11.3.2 | - | 6.1.10 |