FB_BA_FixedLimit
The template represents a limit switch with fixed limits.
A tolerance range is defined around the value fIn to be monitored.
The tolerance range results from a high limit value HighLimitValue and a low limit value LowLimitValue.
If the value fIn exceeds the upper limit value of the tolerance range, then the output bHighLimit is set.
A response delay of the output bHighLimit can be parameterized with the time variable TiDly.
The binary object HighLimitOn is used to display bHighLimit and can be used as a fault message object by changing the parameterization.
If the value fIn falls below the lower limit value of the tolerance range, then the output bLowLimit is set.
A response delay of the output bLowLimit and is to be parameterized with the time variable TiDly.
The binary object LowLimitOn is used to display bLowLimit and can be used as a fault message object by changing the parameterization.
![]() | The initialization of the template takes place within the method FB_Init. |
Block diagram
FUNCTION_BLOCK FB_BA_FixedLimit EXTENDS FB_BA_View
bEn : BOOL;
fIn : REAL;
bHighLimit : BOOL;
bLowLimit : BOOL;
VAR_INPUT CONSTANT
HighLimitValue : FB_BA_AV_Op;
LowLimitValue : FB_BA_AV_Op;
TiDly : FB_BA_AV_Op;
HighLimitOn : FB_BA_BV;
LowLimitOn : FB_BA_BV;
FixedLimit : FB_BA_FixedLimitCtrl;
Name | Type | Description |
bEn | BOOL | General enable of the template. |
fIn | REAL | The analog value to be monitored is connected to the input, e.g. a differential pressure sensor. |
Outputs
bHighLimit | BOOL | The output indicates that the upper limit value of the tolerance range has been exceeded. |
bLowLimit | BOOL | The output indicates that the value has fallen below the lower limit of the tolerance range. |
Inputs CONSTANT
HighLimitValue | Analog value object for entering the upper limit value of the tolerance range. | |
LowLimitValue | Analog value object for entering the lower limit value of the tolerance range. | |
TiDly | Analog value object for entering the response delay of the outputs bHighLimit and bLowLimit. | |
HighLimitOn | The binary object is used to display bHighLimit and can be used as a fault message object by changing the parameterization. | |
LowLimitOn | The binary object is used to display bHighLimit and can be used as a fault message object by changing the parameterization. |