FB_BA_FdbAnalogExt
FB_BA_FdbAnalogExt 1:
The template is used to monitor analog values with dynamic switch values, e.g. for differential pressure monitoring of a fan.
FB_BA_FdbAnalogExt 2:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_FdbAnalogExt 3:
FUNCTION_BLOCK FB_BA_FdbAnalog EXTENDS FB_BA_View
  bEn                  : BOOL;
  bCommand             : BOOL;
  fIn                  : REAL;
  fOn                  : REAL := 10.0;
  fOff                 : REAL := 2.0;
  bDst                 : BOOL;
VAR_INPUT CONSTANT
  SwitchOnValue        : FB_BA_AV_Op;
  SwitchOffValue       : FB_BA_AV_Op;
  DelayFeedback        : FB_BA_AV_Op;
  DelayInterruption    : FB_BA_AV_Op;
  Dst                  : FB_BA_BV;
  FixedLimit           : FB_BA_Swi2P;
  FdbCtrl              : FB_BA_FdbCtrlBinary;
FB_BA_FdbAnalogExt 4: Inputs
Type
bEn
General enable of the template.
bCommand
The switching actuator output of the aggregate to be monitored is connected to the input.
fIn
REAL
The analog value to be monitored is connected to the input, e.g. a differential pressure sensor.
fOn
REAL
The switch-on value for FixedLimit is connected to the input.
In the case of differential pressure monitoring, a pressure value must be selected here which must not be undershot during the running process.
fOff
REAL
The switch-off value for FixedLimit is connected to the input.
This value must be just below the switch-on value fOn.
FB_BA_FdbAnalogExt 5: Outputs
Type
bDst
Binary object for displaying the fault.
FB_BA_FdbAnalogExt 6: Inputs CONSTANT
Type
SwitchOnValue
FB_BA_AV_Op
Analog value object for entering the switch-on value for fOn.
SwitchOffValue
FB_BA_AV_Op
Analog value object for entering the switch-off value for fOff.
DelayFeedback
FB_BA_AV_Op
Analog value object for entering the time delay of the "Aggregate ready for operation" information.
In the case of differential pressure monitoring, a time delay must be specified here after which it can be assumed that the system has built up the required differential pressure.
DelayInterruption
FB_BA_AV_Op
Analog value object for entering the delay time to trigger a fault message.
The message from the differential pressure sensor can be delayed, in order to buffer pressure fluctuations.
Dst
FB_BA_BV
Variables
Type
FixedLimit
FB_BA_Swi2P
Conversion of the analog value fIn into a binary switching signal for FdbCtrl.
FdbCtrl
FB_BA_FdbCtrlBinary
Monitoring of the binary feedback.