FB_BA_LightGroupPresence
FB_BA_LightGroupPresence 1:
One or more light actuators are combined in a light zone for simultaneous control, depending on local conditions.
This template represents a light zone (room) that is only switched via presence. Typical applications are sanitary areas or interior corridors.
Function
A rising edge at bPresence switches the light on via the internal light control block LightSwitch.
The output bAutomaticMode changes to TRUE and the light value is output via the function block LightEvent as the telegram ST_BA_Lighting.
On a falling edge at bPresence, the light is first dimmed to a minimum value via a ramp (if parameterized, see FB_BA_LightCtrl) and then switched off. The output bAutmaticMode changes to FALSE and the light telegram is deactivated on the function block LightEvent.
A rising edge at input bResetRoomFunction can be used to achieve premature switch-off and deactivation.
Input stReferenceFeedback
Information about the controlled light actuator or the reference actuator of a group is fed back into the light control function via this input.
The light value of the reference actuator is of particular importance here: If the light actuator is already controlled by another function of the same or lower priority and the template described here now "takes over" control, it must control the actuator based on its existing light value.
In addition, current values and states are transmitted and can be displayed via the HMI.
Data exchange HMI
The data exchange with the HMI is realized here in the base class FB_BA_Ext_LightBase (internal function block). The use of the following variables is visible in this template:
FB_BA_LightGroupPresence 2:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_LightGroupPresence 3:
FUNCTION_BLOCK FB_BA_LightGroupPresence EXTENDS FB_BA_Ext_LightBase
  bResetRoomFunction     : BOOL;
  bPresence              : BOOL;
  stAreaLighting         : ST_BA_Lighting;
  stScene                : ST_BA_Lighting;
  stReferenceFeedback    : ST_BA_LightActuatorFeedback;
  stLighting             : ST_BA_Lighting;
VAR_INPUT CONSTANT PERSISTENT
  nSwiTi                 : UDINT;
  nPreOffRampTi          : UDINT;
  fOnVal                 : REAL;
  fPreOffVal             : REAL;
  nPreOffDly             : UDINT;
  fLgtT                  : REAL;
  LightEvent             : FB_BA_LightingEvt :=( ePrio:= E_BA_LightingPrio.eSimple);
  LightSwitch            : FB_BA_LightCtrl;
  PrioSwi                : FB_BA_LightingTgmSel4;
FB_BA_LightGroupPresence 4: Inputs
Type
bResetRoomFunction
This input switches off the light function block LightSwitch - it is then no longer active (output bAutmaticMode/bManualMode = FALSE). Switch-off takes place via a ramp and dwell time on a basic light value, see parameters: fPreOffVal, nPreOffDly and nPreOffRampT.
bPresence
Presence signal input. A rising edge switches the light on and a falling edge switches it off. Switching on and off via presence is accompanied by activation and deactivation of the light function block.
stAreaLighting
ST_BA_Lighting
Resulting telegram from the higher levels (area, floor and building), which is formed in the FB_BA_AreaLighting function block.
stScene
ST_BA_Lighting
Reserved telegram input for scene control.
stReferenceFeedback
Feedback input of the controlled light actuator or the guide light of the controlled group.
FB_BA_LightGroupPresence 5: Outputs
Type
stLighting
ST_BA_Lighting
Resulting output program.
FB_BA_LightGroupPresence 6: Inputs CONSTANT PERSISTENT
Type
nSwiTi
UDINT
Ramp for the switching functions in seconds, related to a dimming from 0 to 100%. Pre-set to 2 s in FB_Init.
nPreOffRampTi
UDINT
Ramp used to drive to a base value fPreOffVal before switching off. Pre-set to 2 s in FB_Init.
fOnVal
REAL
Switch-on value. Pre-set to 100% in FB_Init.
fPreOffVal / nPreOffDly
REAL / UDINT
Base value and hold time at this value before switching off the overall function. If the current light value already falls below the base value, this function is not active and it is switched off immediately. Pre-set to 4% and 10 s in FB_Init.
fLgtT
REAL
Light temperature: Pre-set to 3000 K in FB_Init.
FB_BA_LightGroupPresence 7: Inputs CONSTANT
Type
LightEvent
FB_BA_LightingEvt
Telegram generator for the light values. The priority is pre-set to eManualActuator.
Type
LightSwitch
FB_BA_LightCtrl
Light control block.
PrioSwi
Telegram selection.