FB_BA_H_HtgCir01
Template FB_BA_H_HtgCir01 is used to program a static heating circuit.
The main components of the template are:
- Flow temperature control.
- Heating curve dependent on outside temperature with night setback.
- Operation mode selection.
- Control of the heating circuit pump.
- Control of an analog control valve.
![]() | The initialization of the template takes place within the method FB_Init. |
Fault shutdown
The plant switches off at:
- Fault in the heating circuit pump
- Fault in the flow temperature sensor
The following table lists the event-capable objects of the template that can trigger relevant PlantLock faults. The parameterization of the lock priority of these events can be found in FB_init.
Function block | eEnPlantLock | Function block | bPrioHigh | bPrioMedium |
TFl.MV | E_BA_LockPriority.eMedium |
PlantLock |
| X |
Pu.Dst | E_BA_LockPriority.eMedium |
| X |
Principle diagram
The principle diagram shows the intended use of the template with the plant elements involved.
Block diagram
FUNCTION_BLOCK FB_BA_H_HtgCir01 EXTENDS FB_BA_View
eOpMod : E_BA_EnergyLvl;
bRls : BOOL;
fSp : REAL;
bPu : BOOL;
fVlv : REAL;
VAR_INPUT CONSTANT
TFl : FB_BA_SensorAnalog_Raw;
TRt : FB_BA_SensorAnalog_Raw;
Vlv : FB_BA_Vlv;
Pu : FB_BA_Pu1st;
Sp : FB_BA_H_HtgCir_Sp;
OpMod : FB_BA_H_OpMod;
HtgLmt : FB_BA_HtgLmt;
TFlCtrl : FB_BA_PID;
PlantLock : FB_BA_PlantLock;
Outputs
Name | Type | Description |
eOpMod | Operation mode of the heating circuit. | |
bRls | BOOL | The variable indicates that the heating circuit is in operation. |
fSp | REAL | Calculated setpoint of the heating characteristic curve. |
bPu | BOOL | Heating circuit pump is active. |
fVlv | REAL | Calculated control value for the control valve. |
Inputs CONSTANT
TFl | The function block represents the flow temperature. | |
TRt | The function block represents the return temperature. | |
Vlv | Control valve | |
Pu | Heating circuit pump | |
Sp | The function block calculates the setpoint for the flow temperature based on the damped outside temperature and the frost protection setpoint. The damped outside temperature Site.stGeneralSettings.fTWthDamped and the frost protection setpoint Site.stGeneralSettings.fFrostProtectionSetpoint originate from the global variable list Site. | |
OpMod | FB_BA_H_OpMod | Operation mode selection of the heating circuit (Auto, Protection, Economy and Comfort). The variable Site.stGeneralSettings.bTWthLowLimit indicates that the outside temperature has fallen below the lower limit and the frost protection function is therefore active. |
HtgLmt | FB_BA_HtgLmt | The heating limit switch integrated in the function block enables automatic heating operation depending on the damped outside temperature. The damped outside temperature Site.stGeneralSettings.fTWthDamped originates from the global variable list Site. |
TFlCtrl | Flow temperature control of the heating circuit. | |
PlantLock | When the function block is called, the relevant faults of the event-enabled objects are collected and output at this and lower levels of the heating circuit. These relevant faults trigger the E_BA_EnergyLvl.eProtection operation mode in the OpMod operation mode program. As a result, the heating circuit is switched to the E_BA_EnergyLvl.eProtection operation mode. A list of the faults that shut down the plant can be found under Fault shutdowns. |