FB_BA_LglPrev
This function block FB_BA_LglPrev is used for disinfection of the service water and for killing off Legionella. Disinfection mode is activated at input bEnLglPrev via a timer program. It is advisable to run the disinfection at least once per week (during the night). The temperature should be at least 70 °C. The activation interval at bEnLglPrev must be adequately long. The output bLd activates the storage tank charging.
For hot water tanks with several temperature sensors, a min selection of all sensors must be connected to fTMin.
If fTMin exceeds the value of fSp, a monitoring timer with a time of nTi_sec [s] is started. If the minimum tank temperature fTMin remains above fSp - fSpHys while the timer is active, the tank was heated adequately. If circulation is active, the output bLd must be linked to enabling of the circulation pump, to ensure that the water pipe within the service water system is included in the disinfection. If the temperature has fallen below fSp -fSpHys during the disinfection process, this process must be restarted and run until the time nTi has fully elapsed. If disinfection is successful, output bLd is reset.
If the disinfection process was incomplete during the function block activation (bEnLglPrev), this is indicated with the output bAlm. The output must be reset with bRst.
Explanation of the diagram:
t0 Start of the legionella program and switching of output bLd. Heating of the hot water tank.
t1 The tank has reached the temperature fSp. The timer for the heating time is started.
t2 The minimum tank temperature has fallen below fSp -fSpHys. The timer for the heating time is reset.
t3 The temperature exceeds fSp again, and the heating timer is started again.
t4 The minimum tank temperature was above the limit fSp - fSpHys over the period of nTi, disinfection was successful. bLd is reset and the hot water tank returns to normal operation.
bEnLglPrev : BOOL;
fTMin : REAL;
fSp : REAL;
fSpHys : REAL;
nTi : UDINT;
bRst : BOOL;
bEnLglPrev
| BOOL | Enabling of disinfection operation via a timer program. |
fTMin | REAL | Minimum tank temperature [°C]. Minimum selection of temperature sensors at the top and bottom. |
fSp | REAL | Setpoint for disinfection [°C]. |
fSpHys | REAL | Temperature difference [°K] lower limit; always calculated absolute. |
nTi | UDINT | Monitoring period [s]. |
bRst | BOOL | Resetting of the legionella alarm. |
Outputs
bLd : BOOL;
fSpOut : REAL;
nRTi : UDINT;
nSta : UDINT;
bAlm : BOOL;
bLd | BOOL | Anti-legionella mode active. |
fSpOut | REAL | Setpoint forwarding to charging circuit: |
nRTi | UDINT | Countdown timer disinfection mode. |
nSta
| UDINT | Disinfection program status:
bAlm | BOOL | The temperature setpoint was not reached consistently over the interval nTi, so that adequate disinfection is not guaranteed. |
TwinCAT from v3.1.4024.22 | Tc3_BA2 from v5.2.5.0 |