FB_BA_LglPrev
FB_BA_LglPrev 1:
This function block FB_BA_LglPrev is used for disinfection of the service water and for killing off Legionella. Disinfection mode is activated at input bEnLglPrev via a timer program. It is advisable to run the disinfection at least once per week (during the night). The temperature should be at least 70 °C. The activation interval at bEnLglPrev must be adequately long. The output bLd activates the storage tank charging.
For hot water tanks with several temperature sensors, a min selection of all sensors must be connected to fTMin.
If fTMin exceeds the value of fSp, a monitoring timer with a time of nTi_sec [s] is started. If the minimum tank temperature fTMin remains above fSp - fSpHys while the timer is active, the tank was heated adequately. If circulation is active, the output bLd must be linked to enabling of the circulation pump, to ensure that the water pipe within the service water system is included in the disinfection. If the temperature has fallen below fSp -fSpHys during the disinfection process, this process must be restarted and run until the time nTi has fully elapsed. If disinfection is successful, output bLd is reset.
If the disinfection process was incomplete during the function block activation (bEnLglPrev), this is indicated with the output bAlm. The output must be reset with bRst.
FB_BA_LglPrev 2:
Explanation of the diagram:
t0 Start of the legionella program and switching of output bLd. Heating of the hot water tank.
t1 The tank has reached the temperature fSp. The timer for the heating time is started.
t2 The minimum tank temperature has fallen below fSp -fSpHys. The timer for the heating time is reset.
t3 The temperature exceeds fSp again, and the heating timer is started again.
t4 The minimum tank temperature was above the limit fSp - fSpHys over the period of nTi, disinfection was successful. bLd is reset and the hot water tank returns to normal operation.
FB_BA_LglPrev 3: Inputs
  bEnLglPrev  : BOOL;
  fTMin       : REAL;
  fSp         : REAL;
  fSpHys      : REAL;
  nTi         : UDINT;
  bRst        : BOOL;
Type
bEnLglPrev
Enabling of disinfection operation via a timer program.
fTMin
REAL
Minimum tank temperature [°C]. Minimum selection of temperature sensors at the top and bottom.
fSp
REAL
Setpoint for disinfection [°C].
fSpHys
REAL
Temperature difference [°K] lower limit; always calculated absolute.
nTi
UDINT
Monitoring period [s].
bRst
Resetting of the legionella alarm.
FB_BA_LglPrev 4: Outputs
  bLd     : BOOL;
  fSpOut  : REAL;
  nRTi    : UDINT;
  nSta    : UDINT;
  bAlm    : BOOL;
Type
bLd
Anti-legionella mode active.
fSpOut
REAL
Setpoint forwarding to charging circuit:
fSp (input) if the function block is activated
0 if the function block is not activated.
nRTi
UDINT
Countdown timer disinfection mode.
nSta
UDINT
Disinfection program status:
  1. Disinfection operation was successful.
  2. Disinfection completed successfully. After the disinfection, and to reactivate legionella prevention, bEnLglPrev must be FALSE.
  3. Disinfection operation active.
  4. Disinfection not successfully. Alarm is pending.
  5. Disinfection not successfully, the alarm was acknowledged.
  6. Restart of the controller or no legionella mode has been requested yet.
bAlm
The temperature setpoint was not reached consistently over the interval nTi, so that adequate disinfection is not guaranteed.
Development environment
Required PLC library
TwinCAT from v3.1.4024.22
Tc3_BA2 from v5.2.5.0